no Motion after tripping limit switches <resolved>

Post by warnerr »

Revised my limit switches for my allinonedc so i have seperate mechanical switches - two for each axis now. (anilam only had one per) all servers move correct, jog and count. hitting seitches triggers stop and displays correct switch. It should be noted these are old allenbradly mechanicals- they take about a quarter inch of travel in opposite direction to reset. The software sees this as no motion and trips. reversing switches software position does not solve. Was hoping to use limit switch homing....What do you recommend?
refuses to move out of trip zone
refuses to move out of trip zone


cnckeith
Site Admin
Posts: 8932
Joined: Wed Mar 03, 2010 4:23 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: Yes
CNC Control System Serial Number: none
DC3IOB: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Contact:

Re: no Motion after tripping limit switches

Post by cnckeith »

please post a fresh.report.zip so we can see your settings. here is how..
viewtopic.php?f=60&t=1043
Need support? READ THIS POST first. http://centroidcncforum.com/viewtopic.php?f=60&t=1043
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html


warnerr
Posts: 21
Joined: Fri Jun 14, 2019 10:10 pm
Acorn CNC Controller: No
Allin1DC CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: a900749
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: no Motion after tripping limit switches

Post by warnerr »

report attached.
report_0501192210_2019-10-10_12-52-45.zip
newly built machine homing
(196.59 KiB) Downloaded 146 times


cncsnw
Community Expert
Posts: 4576
Joined: Wed Mar 24, 2010 5:48 pm

Re: no Motion after tripping limit switches

Post by cncsnw »

CNC12 is unnecessarily restrictive about switch hysteresis. It will only back away from the tripped switch by one turn of the motor, or 1/4", whichever is greater. I understand the next release is at least going to increase the distance limit from 1/4" to 1/2".

A better long-term solution would be to permit the axis to back off either one turn of the motor, or back to where it was sitting when you started the homing move (whichever is farther). But that will have to wait for some more distant future release.

In the mean time you can work around the restriction by lying about your turns ratio and encoder count. E.g. if you change your Z axis revs/inch from 6.67330 to 3.33665, and change encoder counts/rev from 8000 to 16000, then CNC12 would at least be willing to back off by 0.2997" (what the control would then think is one turn). For X and Y you would have to do at least 4x adjustment, to get the apparent distance of one motor turn over 1/4".


martyscncgarage
Community Expert
Posts: 9953
Joined: Tue Mar 28, 2017 12:01 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Mesa, AZ

Re: no Motion after tripping limit switches

Post by martyscncgarage »

You have an All in One DC
I noted in your report you have two axis reversals Axis 1 X, an Axis 3 Z):
Axis Label Motor Encoder Lash Comp. Limit Home Dir Screw
revs/in counts/rev. (inches) - + - + Rev Comp
1 X 13.2247676999999992 8000 0.0000 1 2 1 2 Y N
2 Y 13.2943574000000009 8000 0.0000 3 4 3 4 N N
3 Z 6.6733018299999998 8000 0.0000 5 6 5 6 Y N

Besides just clicking Y you have to go switch the limit switch inputs and change the screen above.
Follow this tech bulletin: https://www.centroidcnc.com/dealersuppo ... ds/137.pdf

You need to do this for X and Z Y is OK. Once you physically swap the X+ and X- limit switch inputs and the Z+ and Z- limit switch inputs on All in One DC you go into the screen above and change from 1 2 for limit and 1 2 for home to 2 1 for limit and 2 1 for home for X axis
And from 5 6 for limit and 5 6 for Home to 6 5 for Limt and 6 5 for Home

Read the tech bulletin, hopefully it makes sense. But it has to be done.

Marty
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ


warnerr
Posts: 21
Joined: Fri Jun 14, 2019 10:10 pm
Acorn CNC Controller: No
Allin1DC CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: a900749
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: no Motion after tripping limit switches

Post by warnerr »

you are correct. i spent some time and did some reconfiguring before i got your information so i should post an updated report. System sets fine if i use ‘ jog’ and place everything centered- even the soft stops trigger properly and i can back off.


warnerr
Posts: 21
Joined: Fri Jun 14, 2019 10:10 pm
Acorn CNC Controller: No
Allin1DC CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: a900749
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: no Motion after tripping limit switches

Post by warnerr »

THANK YOU! THANK YOU! martyscncgarage - I had software flipped switches but had not moved wires- THAT IS THE SOLUTION! Might be nice to add to manual. Your a genius!