Post by tblough »

I'm working on getting clamping feedback working in my PLC. This is what I have at this point. Is there a better way to verify the rotary table clamp feedback?

Code: Select all

IN PLCMSG.TXT
...
41  5041 Warning: Rotary Table Not Clamped
...



IN PLC PROGRAM
...
ROTARY_NOT_CLAMPED_MSG                                                 IS 10498;(2+256*41)
...
RotaryTableClamped            IS INP13
...
RotaryTableClamp              IS OUT9
...
ClampTimer             IS T20 ; Timer to check clamp feedback signal
...
;==============================================================================
                              FourthAxisStage
;==============================================================================
IF SV_MACHINE_PARAMETER_800 == 1 THEN SET ClampEnabled_M, ClampTimer = 1000
IF SV_MACHINE_PARAMETER_800 != 1 THEN RST ClampEnabled_M 

; Rotary Table Clamp on/off
; RTB 1/14
IF ClampEnabled_M && M10 THEN (RotaryTableClamp), SET ClampTimer ; turn on clamp and wait 1 second to check it is on
IF !RotaryTableClamp THEN RST ClampTimer
IF ClampTimer && !RotaryTableClamped THEN InfoMsg_W = Rotary_Not_Clamped_MSG, RST ClampTimer

...
Last edited by tblough on Wed Jan 16, 2019 10:42 am, edited 1 time in total.
Cheers,

Tom
Confidence is the feeling you have before you fully understand the situation.
I have CDO. It's like OCD, but the letters are where they should be.


cncsnw
Community Expert
Posts: 4596
Joined: Wed Mar 24, 2010 5:48 pm
Acorn CNC Controller: No
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No

Re: Rotary Table Clamp and Clamp Feedback in PLC

Post by cncsnw »

That looks reasonable.