You can do it. You need to fuse your router appropriately. Buy a pigtail with the correct plug on it, and a fusible air conditioning disconnect. Wire the pogtail to the line side of the disconnect. Put the correct size fuses for your machine in the disconnect. For discussions sake, let's say they are 15amp. From the disconnect to your machine control, you can run #14awg copper wire. If 20amp, #12, if 30amp, #10.Dan M wrote: ↑Fri Sep 07, 2018 11:08 pm Got a question for any one:
I want to wire the whole controller to 230/240v since the vfd needs it and I have a 50amp 230/240v nema 6-50 for my welder, bandsaw and compressor. Have you ever wired your power supplies and vfd to a single 230/240v nema 6-50 plug? I know my panel is more than enough being 50amps. I’m just curious if you have ever done it. All my meanwell power supplies are 100-240v so that shouldn’t be a problem. I’m just assuming I need to add a 20amp breaker inside the control box before the pig tail obviously. I have to use a nema 6-50 since those are the 240v outlets I have, it’s single phase no neutral just two hots and a ground for anyone that doesn’t know.
Thanks in advance!!!
Dan
In your control, you might want use smaller fuses for sub systems. If not you should wire all your power supplies with the same size wire used on the load side of the disconnect, dependent on the fuse size.
Home Depot sells fusible Air Conditioner disconnects for about $20.
You might want to look at Centroid's OAK/All in One DC schematics for more ideas.
Marty