ATC - M101 and M6 Modifications
Moderator: cnckeith
-
- Posts: 782
- Joined: Tue Oct 20, 2020 8:41 pm
- Acorn CNC Controller: Yes
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Arizona
ATC - M101 and M6 Modifications
I just completed a carousel style ATC that I have been designing to be CNC12 compatible with the least amount of custom programming possible. The attached schematic is a modified version of the Centroid supplied schematic for this kind of ATC. The main modification is that I removed the VFDZeroSpeed input.
Uwe mentioned that I can add M101 macro that contains the command /70014 ;Wait for Zero Speed. I understand that this will act as a virtual input and CNC12 will wait for the spindle to stop before moving ahead. I created the M101 macro (see attached).
I have no experience at all writing macros, but I believe that I have to change the M6 macro and add the M101 line most likely after M5 in the M6 macro.
I will be away for the next few weeks and hope to test this ATC for the first time using just after I upgrade from CNC12 v5.10 to CNC v5.40.
Can you please help with this minor macro implementation.
1. What is the correct file extension and file folder for the M101 macro. I believe it is supposed to be "C:\cncm\ncfiles\mfuncs\M6.cnc" but I don't see a mfuncs directory.
2. What is the correct file extension and file folder for the M6 macro? Does the Wizard change the name of the M6 macro if the ATC is being used. How do I modify the M6 macro properly?
Thanks... Richard
Uwe mentioned that I can add M101 macro that contains the command /70014 ;Wait for Zero Speed. I understand that this will act as a virtual input and CNC12 will wait for the spindle to stop before moving ahead. I created the M101 macro (see attached).
I have no experience at all writing macros, but I believe that I have to change the M6 macro and add the M101 line most likely after M5 in the M6 macro.
I will be away for the next few weeks and hope to test this ATC for the first time using just after I upgrade from CNC12 v5.10 to CNC v5.40.
Can you please help with this minor macro implementation.
1. What is the correct file extension and file folder for the M101 macro. I believe it is supposed to be "C:\cncm\ncfiles\mfuncs\M6.cnc" but I don't see a mfuncs directory.
2. What is the correct file extension and file folder for the M6 macro? Does the Wizard change the name of the M6 macro if the ATC is being used. How do I modify the M6 macro properly?
Thanks... Richard
- Attachments
-
- M101.cnc.txt
- (27 Bytes) Downloaded 5 times
-
- 15 s15119.r1 ATC ONLY (RJS) VALVE LATCHING RELAY.pdf
- (1.77 MiB) Downloaded 8 times
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Community Expert
- Posts: 3825
- Joined: Thu Sep 23, 2021 3:49 pm
- Acorn CNC Controller: Yes
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 6433DB0446C1-08115074
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Germany
Re: ATC - M101 and M6 Modifications
M101 is a build in function, M101 – Wait for PLC Bit (Closed, On, Set)
If you want to wait for zero spindle speed in a macro:
File Name for M6 = mfunc6.mac in the \cncm folder
Uwe
If you want to wait for zero spindle speed in a macro:
Code: Select all
IF #50001 ;Prevent lookahead from parsing past here
M101 /70014 ;Wait for Zero Speed
Uwe
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 586
- Joined: Wed Jan 23, 2019 4:19 pm
- Acorn CNC Controller: Yes
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 80F5B5B92C3A-0213236854
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Re: ATC - M101 and M6 Modifications
If you have zero speed signal going from your vfd to the acorn and it is working, you can also do
M101/50007 ;Wait for input 7
It can be wait for it to open or wait for it to close with M100 or M101
I use those for waiting on chuck to open or close, verify tool holder in spindle, ect....
Depending on the number of inputs you have, you can also just put a pause in the M5
M101/50007 ;Wait for input 7
It can be wait for it to open or wait for it to close with M100 or M101
I use those for waiting on chuck to open or close, verify tool holder in spindle, ect....
Depending on the number of inputs you have, you can also just put a pause in the M5
Ken
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Community Expert
- Posts: 3825
- Joined: Thu Sep 23, 2021 3:49 pm
- Acorn CNC Controller: Yes
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 6433DB0446C1-08115074
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Germany
Re: ATC - M101 and M6 Modifications
Since you have a spindle encoder, there is no need for wasting an input and doing extra wiring.
If there is no speed on the spindle the PLC will set Mem Bit 14
This can be tested with M101 /70014
The IF #50001 is to prevent further processing til 70014 is set.
Uwe
If there is no speed on the spindle the PLC will set Mem Bit 14
Code: Select all
SpindleZeroSpeedState_M IS MEM14
The IF #50001 is to prevent further processing til 70014 is set.
Uwe
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Community Expert
- Posts: 4666
- Joined: Wed Mar 24, 2010 5:48 pm
- Acorn CNC Controller: No
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
Re: ATC - M101 and M6 Modifications
Custom M functions are in the CNC12 installation directory. On a mill control that is c:\cncm.
If there is a custom M6, it is named "mfunc6.mac".
Yes, it would be appropriate to wait until the spindle is at zero speed, in the M6 macro, after calling M5, and before advancing the carousel.
There is no need for "IF #50001" ahead of "M101/70014".
An M101 command always runs in order, at run-time. That is different from "IF #70014", which would be evaluated at parse time. However, "IF #70014" does not need "IF #50001" ahead of it either, since "IF #70014" will by itself force parsing to wait for execution to catch up.
If there is a custom M6, it is named "mfunc6.mac".
Yes, it would be appropriate to wait until the spindle is at zero speed, in the M6 macro, after calling M5, and before advancing the carousel.
There is no need for "IF #50001" ahead of "M101/70014".
An M101 command always runs in order, at run-time. That is different from "IF #70014", which would be evaluated at parse time. However, "IF #70014" does not need "IF #50001" ahead of it either, since "IF #70014" will by itself force parsing to wait for execution to catch up.
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Community Expert
- Posts: 4666
- Joined: Wed Mar 24, 2010 5:48 pm
- Acorn CNC Controller: No
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
Re: ATC - M101 and M6 Modifications
As far as I can tell, a standard Acorn PLC program sets MEM14 "SpindleZeroSpeedState_M" based only on the "VFDZeroSpeed" input, if any.
I do not see any reference to the spindle encoder or SV_MEASURED_SPINDLE_SPEED.
You could, of course, replace:
with
But that will only work if you have a spindle encoder, have it properly configured, and have set bit 0 of Parameter 78.
I do not see any reference to the spindle encoder or SV_MEASURED_SPINDLE_SPEED.
You could, of course, replace:
Code: Select all
IF VFDZeroSpeed THEN (SpindleZeroSpeedState_M)
Code: Select all
IF ABS(SV_MEASURED_SPINDLE_SPEED) < 10 THEN (SpindleZeroSpeedState_M)
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Community Expert
- Posts: 3825
- Joined: Thu Sep 23, 2021 3:49 pm
- Acorn CNC Controller: Yes
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 6433DB0446C1-08115074
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Germany
Re: ATC - M101 and M6 Modifications
ok, so it is like belt and suspenders
This here is working with no VFD zero Speed input and encoder...
Uwe

This here is working with no VFD zero Speed input and encoder...
Code: Select all
IF #50001 ;Prevent lookahead from parsing past here
;IF #4201 || #4202 THEN GOTO 1000 ;Skip macro if graphing or searching
N100 ;Insert your code between N100 and N1000
G97 ;Turn off CSS
G98 ;Feed per Minute
M5 ;Turn off Spindle
M101 /70014 ;Wait for Zero Speed
IF ~#9078 and 1 THEN GOTO 200 ;Skip Spindle Encoder Speed Check if None Used
N110
G4 P0.1
IF #50001
IF #25009 > 10 THEN GOTO 110
N200
M94 /51 ;Request C-Axis Enable
M51 ;Perform Default M51 Actions
M151 ;Unwind C-Axis Position
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 782
- Joined: Tue Oct 20, 2020 8:41 pm
- Acorn CNC Controller: Yes
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Arizona
Re: ATC - M101 and M6 Modifications
Looking at my CNCM directory, I see "mfunc6" which I understand to be the standard M6 macro. I also see Mfunc6 customized for the probeApp as well as Mfunc6 customized for the ProbeApp and an ATC.
Why are there several versions of this file? When I viewed the M6 macro, "M101 /70014 was already included. What is the simplest way to get this working correctly.
Even though I am really waiting to test this with CNC12 v5.40, I did a bench test today. Something doesn't look quite right:
https://www.dropbox.com/scl/fi/ousoe44q ... 7jo9h&dl=0
Richard
Why are there several versions of this file? When I viewed the M6 macro, "M101 /70014 was already included. What is the simplest way to get this working correctly.
Even though I am really waiting to test this with CNC12 v5.40, I did a bench test today. Something doesn't look quite right:
https://www.dropbox.com/scl/fi/ousoe44q ... 7jo9h&dl=0
Richard
- Attachments
-
- mfunc6.mac
- (10.48 KiB) Downloaded 3 times
-
- M101.cnc.txt
- (27 Bytes) Downloaded 3 times
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Community Expert
- Posts: 4666
- Joined: Wed Mar 24, 2010 5:48 pm
- Acorn CNC Controller: No
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
Re: ATC - M101 and M6 Modifications
Your video looks pretty reasonable to me.
It advanced the carousel to remove T1 from the spindle; moved Z up; rotated four positions to get to T5; moved Z down; and retracted the carousel.
I could not hear it unclamping and clamping the drawbar, but I assume that is happening at the appointed times.
What is it that does not look right?
Note that after "ATC Init", the control does not assume T1 is in the carousel. It assumes T1 is in the spindle, and that the carousel is rotated to position 1. Therefore the first step in a tool change is to return T1 from the spindle to the carousel.
It advanced the carousel to remove T1 from the spindle; moved Z up; rotated four positions to get to T5; moved Z down; and retracted the carousel.
I could not hear it unclamping and clamping the drawbar, but I assume that is happening at the appointed times.
What is it that does not look right?
Note that after "ATC Init", the control does not assume T1 is in the carousel. It assumes T1 is in the spindle, and that the carousel is rotated to position 1. Therefore the first step in a tool change is to return T1 from the spindle to the carousel.
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Community Expert
- Posts: 3825
- Joined: Thu Sep 23, 2021 3:49 pm
- Acorn CNC Controller: Yes
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 6433DB0446C1-08115074
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Germany
Re: ATC - M101 and M6 Modifications
Of course you are right, I forgot the test with #25009 if no input is used for zero speed.cncsnw wrote: ↑Mon Sep 01, 2025 2:28 pm As far as I can tell, a standard Acorn PLC program sets MEM14 "SpindleZeroSpeedState_M" based only on the "VFDZeroSpeed" input, if any.
I do not see any reference to the spindle encoder or SV_MEASURED_SPINDLE_SPEED.
You could, of course, replace:withCode: Select all
IF VFDZeroSpeed THEN (SpindleZeroSpeedState_M)
But that will only work if you have a spindle encoder, have it properly configured, and have set bit 0 of Parameter 78.Code: Select all
IF ABS(SV_MEASURED_SPINDLE_SPEED) < 10 THEN (SpindleZeroSpeedState_M)
With your PLC change it is working also.
Uwe
(Note: Liking will "up vote" a post in the search results helping others find good information faster)