How do I troubleshoot bad threads? <Resolved>

All things related to the Centroid Acorn CNC Controller

Moderator: cnckeith

fusion
Posts: 91
Joined: Wed May 09, 2018 7:54 am
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 0479B7ADF2F3-1127192707
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Greensboro, NC

How do I troubleshoot bad threads? <Resolved>

Post by fusion »

I'm trying to thread 1/4-20 using Intercon.
The threads look bad. How do you test the encoder?
Pic of threads and report are attached.
Mike
Attachments
IMG_4459.jpg
report_98038A53EB0B-0203259072_2025-05-28_21-23-14.zip
(1.07 MiB) Downloaded 3 times


suntravel
Community Expert
Posts: 3522
Joined: Thu Sep 23, 2021 3:49 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 6433DB0446C1-08115074
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Germany

Re: How do I troubleshoot bad threads?

Post by suntravel »

G-code file and picture of the tool pls.

Uwe


lavrgs
Posts: 646
Joined: Sat Aug 11, 2018 11:22 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: Yes
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Oregon

Re: How do I troubleshoot bad threads?

Post by lavrgs »

Do you have a thread gage? Are you cutting acme threads 8-)? Intercon may require some tweaks to Minor Diameter depending on the type of tool you are using
Attachments
Thread gage.jpg


cncsnw
Community Expert
Posts: 4535
Joined: Wed Mar 24, 2010 5:48 pm

Re: How do I troubleshoot bad threads?

Post by cncsnw »

That looks like unsynchronized starts, due to false index pulse signals. Likely VFD-generated noise on your spindle encoder cable.

On the PID Configuration screen, watch for the asterisk "*" next to the N on the 5th line (which represents your spindle encoder). The asterisk indicates when the index pulse is on.

If you turn the spindle by hand, the asterisk should flash just once per turn, always in the same location.

Assuming that checks out, then start the spindle running at about 60 RPM, and again watch for the asterisk. It should still flash, just briefly, just once per turn. If the asterisk is visible more often than that, it is is because Acorn is seeing false triggers due to noise.


fusion
Posts: 91
Joined: Wed May 09, 2018 7:54 am
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 0479B7ADF2F3-1127192707
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Greensboro, NC

Re: How do I troubleshoot bad threads?

Post by fusion »

cncsnw, that was my thought just without as much detail. It looked like bad threads Mach3 made when the index pulse wasn’t working properly. That’s why I asked for a way to troubleshoot the encoder. It is an eBay sourced encoder, so the quality it questionable.
I’ll do those checks and get back to you.
My VFD is located in the steel base of the lathe. The control enclosure is sitting next to that. I thought the steel base would be enough to shield the sensitive components from noise.
Also the VFD is 1 hp single phase in 3 out Automaion Direct GS2.
What steps should I take to eliminate the noise if that is what we determine is the issue?
I was hoping I miswired the encoder and was missing the index pulse.
Thanks for the help
Mike


richardb15
Posts: 159
Joined: Fri Jan 17, 2025 4:01 am
Acorn CNC Controller: No
Plasma CNC Controller: No
AcornSix CNC Controller: Yes
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 0008DC111213-0701240191
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Victoria, Australia

Re: How do I troubleshoot bad threads?

Post by richardb15 »

I mentioned on your comms issued thread that it looked like all the signal cable screens were not connected to anything, and you have mains and signal wires crossing and almost touching, plus your earthing is not best practice. I'd start there, the encoder might be okay, but unless you sort all the potential points of interference you'll be chasing interference issues forever.


tblough
Community Expert
Posts: 3520
Joined: Tue Mar 22, 2016 10:03 am
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: Yes
CNC Control System Serial Number: 100505
100327
102696
103432
7804732B977B-0624192192
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Boston, MA
Contact:

Re: How do I troubleshoot bad threads?

Post by tblough »

Is the cable between your motor and VFD shielded and properly grounded? If you have an oscilloscope, you can look at the A, B, and Z differential pairs coming from your encoder to see if there is noise on those 6 signal lines.

Is this a stepper or servo driven lathe?
Cheers,

Tom
Confidence is the feeling you have before you fully understand the situation.
I have CDO. It's like OCD, but the letters are where they should be.


fusion
Posts: 91
Joined: Wed May 09, 2018 7:54 am
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 0479B7ADF2F3-1127192707
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Greensboro, NC

Re: How do I troubleshoot bad threads?

Post by fusion »

Hi!
Uwe, I have attached the files you requested.
tblough, I don't recall a shield in that wire. I will check. My electrical skills are very lacking. I remember 4 wires but not a shield. Where should the shield wire be attached? The ground pin on the DB9 BOB? What pin number is that? Its a stepper driven lathe. I have no oscilloscope.
richardb15, I do remember that. I moved the ethernet wire away from the power wires. I also moved the grounds to the common lug on the back panel. I will spend the weekend try to tidy up and move wires as you suggested.
The lathe is an old Atlas. It seems mechanically sound. My backlash is about .0015 on both axis.

Thanks for all your help!
Mike
Attachments
encoder 1.JPG
IMG_4461.jpg
IMG_4460.jpg
test2.cnc
(1016 Bytes) Downloaded 1 time


tblough
Community Expert
Posts: 3520
Joined: Tue Mar 22, 2016 10:03 am
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: Yes
CNC Control System Serial Number: 100505
100327
102696
103432
7804732B977B-0624192192
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Boston, MA
Contact:

Re: How do I troubleshoot bad threads?

Post by tblough »

If your lathe is stepper driven, then one other possibility is that your Z stepper cannot handle the acceleration on the thread return and is loosing steps. Turn your feedrate and rapid rates down to 10% and try again.

Your VFD manual will show the proper way to ground the motor cable shield.
Cheers,

Tom
Confidence is the feeling you have before you fully understand the situation.
I have CDO. It's like OCD, but the letters are where they should be.


fusion
Posts: 91
Joined: Wed May 09, 2018 7:54 am
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 0479B7ADF2F3-1127192707
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Greensboro, NC

Re: How do I troubleshoot bad threads?

Post by fusion »

I think I have a bad encoder or bought the wrong kind.
I think I have it wired correctly, but see what you think. When the orange lead is connected to pin 6 my asterisk "*" next to the N on the 5th line is always ON.
If I move that lead to pin 3, the asterisk "*" next to the N on the 5th line is ON all the time except for one spot where it will turn OFF.
It seems like if I could invert the Z signal with it wire on pin 3 it would work. Is that possible?
If I need a different encoder, could you make a recommendation that isn't too expensive? This one is a Chinese eBay special. I thought I ordered the same one I used on my mill project, and it seems to work just fine.

Thanks for your help!
Mike
Attachments
encoder.PNG
IMG_4469.jpg
IMG_4467.jpg
IMG_4470.jpg


Post Reply