Quesions on HomeAll and LimitAll (Resolved)

All things related to the Centroid CNC Plasma systems, Hardware and Software.

Moderators: cnckeith, Joey

dovrosenberg
Posts: 81
Joined: Mon Nov 11, 2024 9:50 pm
Acorn CNC Controller: No
Plasma CNC Controller: Yes
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Quesions on HomeAll and LimitAll (Resolved)

Post by dovrosenberg »

Simple question: I have an X, 2 Y, 1Z axis on my plasma running Acorn. There are limit switches on each end of each access (8 total). If I want to use HomeAll and LimitAll configuration in S14954 drawing - will the switches wired as Home also act as limit switches and prevent over travel in that direction? If so, I would wire X+, Y+, Y1+, Z+ to be home switches going to input 1 and X-, Y-, Y1-, Z- to be limit switches going to Input 2??
Thanks in advance
Last edited by dovrosenberg on Mon May 19, 2025 8:53 am, edited 1 time in total.


Joey
Plasma/Laser Lead
Posts: 669
Joined: Tue Aug 17, 2021 10:51 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Quesions on HomeAll and LimitAll

Post by Joey »

You can run all axis to the same input and assign the input as home/ limit all

You will need to assign the slave of the gantry separately as the slave home input for auto squaring


ShawnM
Community Expert
Posts: 3037
Joined: Fri May 24, 2019 8:34 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 7804734C6498-0401191832
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Clearwater, FL

Re: Quesions on HomeAll and LimitAll

Post by ShawnM »

Save yourself a ton of headaches, wiring and wasted inputs and just use the negative switches. There's no need for all the extra switches and wiring when you could just use the "soft limits" built into Acorn.

As Joey mentioned wire X,Y and Z to one input set as "home all" and Y2 to it's own input labeled "slave input" if you are going to use auto squaring. This is the only way it works with auto squaring. If you are not auto squaring you don't even need the Y2 switch.


dovrosenberg
Posts: 81
Joined: Mon Nov 11, 2024 9:50 pm
Acorn CNC Controller: No
Plasma CNC Controller: Yes
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Quesions on HomeAll and LimitAll

Post by dovrosenberg »

Screenshot 2025-05-12 113742.png
So if I understand correctly -
OPTION 1:
wire X+, X-, Y+, Y-, Y1-(slave), Z+, Z- to HomeLimitAll maybe onto Input 1

Map Y1+ to SlaveHomeInput on Input 2

OR
OPTION 2:
Wire X+, Y+, Z+ to HomeALL on Input 1
Set soft travel limits to cover X-, Y-, Z- (no switches)
Wire Y1+ to SlaveHomeInput on Input 2

Someone suggested using limit switches AND soft travel limits. You are suggesting to just set the home switches and soft travel limits - is that correct?


ShawnM
Community Expert
Posts: 3037
Joined: Fri May 24, 2019 8:34 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 7804734C6498-0401191832
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Clearwater, FL

Re: Quesions on HomeAll and LimitAll

Post by ShawnM »

I'm suggesting wire X-, Y- and Z+ to input 1 labeled "home all" and Y2- to input 2 labeled "slave home input" and then setup your soft limits for the max table travel. You only need 4 switches to simplify this and make it work but you have to wire it per the manual if you want it to work correctly. All this is in the auto squaring manual.

Do you have mechanical switches or proximity switches? Are they NO or NC?


dovrosenberg
Posts: 81
Joined: Mon Nov 11, 2024 9:50 pm
Acorn CNC Controller: No
Plasma CNC Controller: Yes
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Quesions on HomeAll and LimitAll

Post by dovrosenberg »

I have NPN NC Proximity switches


dovrosenberg
Posts: 81
Joined: Mon Nov 11, 2024 9:50 pm
Acorn CNC Controller: No
Plasma CNC Controller: Yes
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Quesions on HomeAll and LimitAll

Post by dovrosenberg »

ShawnM wrote: Mon May 12, 2025 12:22 pm I'm suggesting wire X-, Y- and Z+ to input 1 labeled "home all" and Y2- to input 2 labeled "slave home input" and then setup your soft limits for the max table travel. You only need 4 switches to simplify this and make it work but you have to wire it per the manual if you want it to work correctly. All this is in the auto squaring manual.

Do you have mechanical switches or proximity switches? Are they NO or NC?

Based on your description, I would put a limit switches in the 3 red locations for X and Y and not worry about the other ends of X or Y gantries
CNC.png


ShawnM
Community Expert
Posts: 3037
Joined: Fri May 24, 2019 8:34 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 7804734C6498-0401191832
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Clearwater, FL

Re: Quesions on HomeAll and LimitAll

Post by ShawnM »

dovrosenberg wrote: Mon May 12, 2025 2:00 pm
ShawnM wrote: Mon May 12, 2025 12:22 pm I'm suggesting wire X-, Y- and Z+ to input 1 labeled "home all" and Y2- to input 2 labeled "slave home input" and then setup your soft limits for the max table travel. You only need 4 switches to simplify this and make it work but you have to wire it per the manual if you want it to work correctly. All this is in the auto squaring manual.

Do you have mechanical switches or proximity switches? Are they NO or NC?

Based on your description, I would put a limit switches in the 3 red locations for X and Y and not worry about the other ends of X or Y gantriesCNC.png
Correct, and then one of course at the top of the Z axis which is not shown.

X, Y and Z wired to input 1 which is HOME ALL and Y2 to input 2 as SLAVE HOME INPUT. Again, this is all in the auto squaring manual, do you have this manual downloaded? If you use auto squaring it can only be wired one way to work correctly.

What you label as Y on the left is actually Y1 and the slave on the right side is Y2 (it's the second Y axis drive)
Last edited by ShawnM on Mon May 12, 2025 3:14 pm, edited 2 times in total.


ShawnM
Community Expert
Posts: 3037
Joined: Fri May 24, 2019 8:34 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 7804734C6498-0401191832
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Clearwater, FL

Re: Quesions on HomeAll and LimitAll

Post by ShawnM »

dovrosenberg wrote: Mon May 12, 2025 12:52 pm I have NPN NC Proximity switches
You'll wire these in series and you should power them with 24 volts.


dovrosenberg
Posts: 81
Joined: Mon Nov 11, 2024 9:50 pm
Acorn CNC Controller: No
Plasma CNC Controller: Yes
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Quesions on HomeAll and LimitAll

Post by dovrosenberg »

ShawnM wrote: Mon May 12, 2025 2:44 pm
dovrosenberg wrote: Mon May 12, 2025 2:00 pm
ShawnM wrote: Mon May 12, 2025 12:22 pm I'm suggesting wire X-, Y- and Z+ to input 1 labeled "home all" and Y2- to input 2 labeled "slave home input" and then setup your soft limits for the max table travel. You only need 4 switches to simplify this and make it work but you have to wire it per the manual if you want it to work correctly. All this is in the auto squaring manual.

Do you have mechanical switches or proximity switches? Are they NO or NC?
So with the suggested configuration- is HOME located at 0,0,0 in my picture or the opposite corner at the end of the soft travel limit? I have the document downloaded and am reviewing it to make sure I understand it. I am planning on using software pairing and auto home. Hopefully the auto square will work as well


Based on your description, I would put a limit switches in the 3 red locations for X and Y and not worry about the other ends of X or Y gantriesCNC.png
Correct, and then one of course at the top of the Z axis which is not shown.

X, Y and Z wired to input 1 which is HOME ALL and Y2 to input 2 as SLAVE HOME INPUT. Again, this is all in the auto squaring manual, do you have this manual downloaded? If you use auto squaring it can only be wired one way to work correctly.

What you label as Y on the left is actually Y1 and the slave on the right side is Y2 (it's the second Y axis drive)


Post Reply