Error Code 916 while auto squaring <beta software>

Posted: Mon Dec 05, 2022 7:54 pm
by bleiler60
While trying to run auto square when the K3 probe is unplugged the auto squaring routine stops and displays the 916 error code. Plug in the probe and auto square works. I'm using the Acorn Six board with the K3 Probe & TT-4 wired using the wiring diagram for the board. Using the PLC diagnostic screen everything seems be be working as it should.

Re: Error Code 916 while auto squaring

Posted: Mon Dec 05, 2022 11:08 pm
by suntravel
916 Unexpected probe contact

probed tripped when a cycle did not ex-
pected contact

Check the wiring/setup of the probe, it is tripped when unplugged

Uwe

Re: Error Code 916 while auto squaring

Posted: Tue Dec 06, 2022 1:11 am
by bleiler60
Here are the screenshots from the PLC diagnostics. The wiring to the board is correct, White to input 9 (Probe Signal); Red to input 10 (Probe Detect).

Probe unplugged
Probe unplugged
Probe plugged in
Probe plugged in
Capture14.PNG
plugged in while Auto square/homing
plugged in while Auto square/homing
unplugged while Auto square/Homing
unplugged while Auto square/Homing
Configuration screen
Configuration screen

Re: Error Code 916 while auto squaring

Posted: Tue Dec 06, 2022 3:24 am
by suntravel
Input 9 should not change when plugged in or not, only if the probe triggers.

You wired Probe Tripped cable to Probe Detect input and Probe Detect cable to Probe Tripped input.

Uwe

Re: Error Code 916 while auto squaring

Posted: Tue Dec 06, 2022 6:37 am
by bleiler60
Thanks, I'll try swapping out the wiring.

This is the wiring diagram that I used
Probe wiring
Probe wiring

Re: Error Code 916 while auto squaring

Posted: Tue Dec 06, 2022 6:48 am
by suntravel
You can also try first to swap the inputs in the Wizard...

Uwe

Re: Error Code 916 while auto squaring

Posted: Tue Dec 06, 2022 8:29 am
by bleiler60
Tried swapping out the wiring, didn't work. Changed the inputs in the wizard same results.
Tried different inputs on the board, no luck. I think the Probe might be defective.

Re: Error Code 916 while auto squaring

Posted: Tue Dec 06, 2022 9:19 am
by bleiler60
Tried using the cable that came with the TT-4, nothing changed, still can't run auto square/homing when the Probe is unplugged.

Re: Error Code 916 while auto squaring

Posted: Tue Dec 06, 2022 1:01 pm
by suntravel
sorry for the confusion, probe is connected ok. Looks like on my mill with NC probe.

But I can not test autosquare, because I have no router.

Uwe

Re: Error Code 916 while auto squaring

Posted: Tue Dec 06, 2022 1:45 pm
by bleiler60
No problem ;)
I appreciate that you tried to solve this issue.
I'm probably going to contact Centroid tech to determine if the probe maybe defective, unless someone else can offer any advice as to why this isn't working.

Thanks