Page 2 of 3
Re: Torch sensor hookup
Posted: Tue Dec 05, 2023 3:00 pm
by ShawnM
You have to run 24 volts into H1 or H4 for the inputs to work, look at the diagram closer.
Posted: Tue Dec 05, 2023 3:39 pm
by _Duke_
Aha, well spotted Shawn!
I guess I assumed that since the leds on the torch prox sensors themselves worked, they were getting juice.
I just powered everything down and hooked up a 24v feed to the H4 terminal, but it makes no difference. The lights on the sensors go off and back on when I lift the round mount, but the lights on the Acorn board stay lit red.
Posted: Tue Dec 05, 2023 4:25 pm
by _Duke_
Ok, I'm a little confused.
What triggers these inputs? Pulling them high or pulling them low?
The way I've got it wired per the diagram, my NPN prox sensors are sending +24vdc along the signal wire to the THC_TX board. But it seems like the Acorn board input pins only register when they get pulled to COM.
Have I got something backwards here?
Posted: Tue Dec 05, 2023 6:06 pm
by centroid467
You want to pull these inputs down to COM/GND for the 24VDC source. The ACORN and THC_TX inputs have their own pull up resistors built in. As you found out, ACORN requires wiring 24V to the inputs while the THC_TX inputs are internally connected to its +24VDC input pin.
It seems your sensor wire colors might be different so it will definitely be worth doublechecking the pinout there.
Posted: Tue Dec 05, 2023 6:36 pm
by _Duke_
The sensor wires are brown blue black just like I'd expect. I wonder if they are mis-labeled as NPN when they're in fact PNP...
Posted: Tue Dec 05, 2023 6:38 pm
by ShawnM
Are they normally open or normally closed prox sensors? Do you have that set correctly in the wizard?
Posted: Tue Dec 05, 2023 7:16 pm
by _Duke_
ShawnM wrote: ↑Tue Dec 05, 2023 6:38 pm
They're NO, but act as NC since the round mount holds them closed until it's bumped. That's not the issue though, I've set it both ways in the software. It's sending +24v through the signal wire when triggered, instead of trying the signal wire to ground
Posted: Tue Dec 05, 2023 7:50 pm
by Joey
Looks like your GND's on the TX board are switched.
[attachment=1]Screenshot_20231205-184318.png[/attachment
Posted: Tue Dec 05, 2023 8:51 pm
by _Duke_
I switched the grounds around on the TX board, made no difference.
Is there a way to test communication between TX and RX boards?
I put a jumper straight from GND to IN1 on the TX board, and the IN1 led on the Acorn board still stays red
Posted: Tue Dec 05, 2023 9:03 pm
by Joey
Can you put more pictures up of everything in the cabinet and power supplies please.
The T in would not work if the TX was not communicating and there would be encoder errors popping up in CNC12.