Yesterday I tried to "calibrate" my spindle speed and when all was said and done I started getting Drive Faults. I have a Hitachi SJ-100 VFD -see attached. I was reducing A04, which was set to 60 to get the actual speed of 560 down to the commanded speed of 500. I started getting intermittent speed changes, as if I was losing power, and then drive faults. I set the A04 back to 60 and the problem continued. I had also made some changes to various Centroid parameters that I don't think would affect the spindle...see report.
I used Winmerge to compare 2-14 to the 2-10 report files and there were some changes to parameters I did not directly change - I did change skins and went back to the original but Parameters in the 900 range were not changed by me...
I will go out in a bit to restore the 2-10 report and see if my issues are fixed.
I also include a file for the suggested parameter settings for the Hitachi SJ-100
Tweaking VFD and Centroid Parameters
Moderator: cnckeith
-
- Posts: 530
- Joined: Sat Aug 11, 2018 11:22 pm
- Acorn CNC Controller: Yes
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: Yes
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Oregon
Tweaking VFD and Centroid Parameters
- Attachments
-
- HITACHI SJ100.pdf
- Hitachi settings
- (6.51 KiB) Downloaded 8 times
-
- report_0008DC111213-0821233001_2024-02-14_15-04-23.zip
- (828.51 KiB) Downloaded 19 times
-
- hitachi-sj100-manual.pdf
- Hitachi Manual
- (5.03 MiB) Downloaded 6 times
My Tree J325 & Projectshttps://photos.app.goo.gl/LLHf8M84eQYwP3ph6
MAKING PARTS https://www.youtube.com/shorts/MSQ4TyTzFkk
Hardinge CHNC4 Retrofithttps://photos.app.goo.gl/244YnF9ykyUf7mfq7
MAKING PARTS https://www.youtube.com/shorts/MSQ4TyTzFkk
Hardinge CHNC4 Retrofithttps://photos.app.goo.gl/244YnF9ykyUf7mfq7
Re: Tweaking VFD and Centroid Parameters
Parameters 911 through 940 reflect the inversion and forcing selections you have made on the Alt-i PLC Diagnostic display.
You should be particularly wary of any non-zero values in Parameters 916-940. Those indicate "forcing" of inputs, outputs, or memory bits. While forcing bits can be useful for short-term diagnostics, there is rarely an appropriate use for permanent forcing.
For INP1 - INP6 on an Allin1DC, if you have no limit switches to connect, you need to use the hardware DIP switches, not software forcing or even inversion.
You should be particularly wary of any non-zero values in Parameters 916-940. Those indicate "forcing" of inputs, outputs, or memory bits. While forcing bits can be useful for short-term diagnostics, there is rarely an appropriate use for permanent forcing.
For INP1 - INP6 on an Allin1DC, if you have no limit switches to connect, you need to use the hardware DIP switches, not software forcing or even inversion.
-
- Posts: 530
- Joined: Sat Aug 11, 2018 11:22 pm
- Acorn CNC Controller: Yes
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: Yes
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Oregon
Re: Tweaking VFD and Centroid Parameters
What about OUTPUT1 I have it forced to get the spindle to run - what is the correct solution?
My Tree J325 & Projectshttps://photos.app.goo.gl/LLHf8M84eQYwP3ph6
MAKING PARTS https://www.youtube.com/shorts/MSQ4TyTzFkk
Hardinge CHNC4 Retrofithttps://photos.app.goo.gl/244YnF9ykyUf7mfq7
MAKING PARTS https://www.youtube.com/shorts/MSQ4TyTzFkk
Hardinge CHNC4 Retrofithttps://photos.app.goo.gl/244YnF9ykyUf7mfq7
-
- Posts: 530
- Joined: Sat Aug 11, 2018 11:22 pm
- Acorn CNC Controller: Yes
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: Yes
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Oregon
Re: Tweaking VFD and Centroid Parameters
I set the VFD to be controlled by the front panel and set the parameters back to what they were prior to calibration and all is good. Then set the VFD To be controlled by Centroid ...still good.
My Tree J325 & Projectshttps://photos.app.goo.gl/LLHf8M84eQYwP3ph6
MAKING PARTS https://www.youtube.com/shorts/MSQ4TyTzFkk
Hardinge CHNC4 Retrofithttps://photos.app.goo.gl/244YnF9ykyUf7mfq7
MAKING PARTS https://www.youtube.com/shorts/MSQ4TyTzFkk
Hardinge CHNC4 Retrofithttps://photos.app.goo.gl/244YnF9ykyUf7mfq7
-
- Posts: 7334
- Joined: Wed Mar 03, 2010 4:23 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: Yes
- CNC Control System Serial Number: none
- DC3IOB: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Contact:
Re: Tweaking VFD and Centroid Parameters
i have some vfd parameters need a power cycle to take effect. most manuals will show this in the parameter list with some indication (like an asterisk) beside it to let you know if you change that parameter then the vfd needs a power cycle and wait for power LED to go out!~
control by VFD panel vs. control by input (the cnc control) is often one of those.
when in doubt/stuck power cycle the vfd.
control by VFD panel vs. control by input (the cnc control) is often one of those.
when in doubt/stuck power cycle the vfd.
Need support? READ THIS POST first. http://centroidcncforum.com/viewtopic.php?f=60&t=1043
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
Re: Tweaking VFD and Centroid Parameters
If OUT1 does not close, and stay closed, when you release emergency stop, then the control is detecting, and hopefully reporting, a fault condition.What about OUTPUT1 I have it forced to get the spindle to run - what is the correct solution?
The correct solution is to find out what that fault condition is, and resolve it. In the short term, that might involve a more surgical workaround (e.g. inverting an input or installing a jumper wire to defeat a specific fault condition that you know does not matter right now).
Some fault conditions are notoriously hard to identify, because CNC12 does not reliably report them if they are present at power-up. If there is no meaningful message in the message box (not even scrolled up out of sight), then check a few common things:
1) On the PID encoder screen, are all of your servo axis encoder, plus your spindle encoder, showing "000-" in the "DQOA" columns?
2) Is your emergency stop input working, and do you have that input number entered, as a negative number, in Parameter 0?
It looks like your particular PLC program will trigger a fault, and open OUT1, if you try to run the spindle while the collet-closed input (INP28) is open.
Since the collet-closed input is a pressure switch in the air line to the "close" side of the collet closer actuator, you can expect this fault if you simply do not have air connected. You will probably need to jumper or invert INP28, and also INP12 "AirPressureOk_I", if you do not yet have air connected or do not have the pressure switches working.
-
- Posts: 530
- Joined: Sat Aug 11, 2018 11:22 pm
- Acorn CNC Controller: Yes
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: Yes
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Oregon
Re: Tweaking VFD and Centroid Parameters
It is the air that's the problem along with a message about the tool being wrong - I removed the ATC and can get by... My current road block is the air, I'm shopping for a larger compressor but I am not certain the one I'm looking at will ever keep up. I've looked for air consumption for the CHNC 4 and the number seem low for what everyone describes as an AIRHOG. The compressor I'm looking at is an Ingersoll Rand SS3L3 3HP 230V unit that produces 11.5 CFM @ 90 PSI.
Are you certain about P28 it is set to 0.68 and is for the servo motors?…sorry IN28
Are you certain about P28 it is set to 0.68 and is for the servo motors?…sorry IN28
My Tree J325 & Projectshttps://photos.app.goo.gl/LLHf8M84eQYwP3ph6
MAKING PARTS https://www.youtube.com/shorts/MSQ4TyTzFkk
Hardinge CHNC4 Retrofithttps://photos.app.goo.gl/244YnF9ykyUf7mfq7
MAKING PARTS https://www.youtube.com/shorts/MSQ4TyTzFkk
Hardinge CHNC4 Retrofithttps://photos.app.goo.gl/244YnF9ykyUf7mfq7