Allin1DC upgrade on Atrump mill- wiring and identifying 10537 DC servo motor transformer

All things related to Centroid Oak, Allin1DC, MPU11 and Legacy products

Moderator: cnckeith

Post Reply
PeteJ
Posts: 6
Joined: Fri Jan 05, 2024 3:12 pm
Acorn CNC Controller: No
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: Yes
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: A901347
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Allin1DC upgrade on Atrump mill- wiring and identifying 10537 DC servo motor transformer

Post by PeteJ »

20240104_114345.jpg
I purchased an Allin1DC along with a 10537 DC servo motor power supply .

I want to confirm that the transformer is correct so that I can cross reference it to the appropriate wiring schematic. There are no part numbers on the transformer anywhere. I have attached a picture to this thread.
It appears to be PN 1171, does that look correct?
Last edited by PeteJ on Mon Jan 08, 2024 10:05 am, edited 1 time in total.
cncsnw
Posts: 3854
Joined: Wed Mar 24, 2010 5:48 pm

Re: Identifying 10537 DC servo motor power supply transformer

Post by cncsnw »

Centroid only used/uses one transformer like that.

If you have a schematic that shows 120VAC primary-side connections going to BLK + BLK/WHT and ORG + ORG/WHT; and shows the 83VAC secondary on GRN wires; and shows the 24VAC secondary on BLU wires; then that schematic applies to your transformer.
PeteJ
Posts: 6
Joined: Fri Jan 05, 2024 3:12 pm
Acorn CNC Controller: No
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: Yes
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: A901347
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Identifying 10537 DC servo motor power supply transformer

Post by PeteJ »

Thank you for the reply. One more question on the power wiring. On the CAPBRDLOW the DC out + shows 605BLU going to CNT1/L4 +VM. Am I to interpret this as it should go to CNT1/L4 and to +VM or just to CNT1/L4?. Ibrliebe looking at the rest of the schematic it should just go to CNT1/L4 but want to make sure.
Screenshot_20240107_183944_Gallery.jpg
Screenshot_20240107_183912_Gallery.jpg
Screenshot_20240107_182129_Gallery.jpg
cncsnw
Posts: 3854
Joined: Wed Mar 24, 2010 5:48 pm

Re: Allin1DC upgrade on Atrump mill- wiring and identifying 10537 DC servo motor transformer

Post by cncsnw »

VM+ goes from the CAPBRDLO, through the E-stop contactor (in L4, out T4), to the Allin1DC.

In more recent schematics, the VM- leg runs through another main pole of the E-stop contactor (and the 542-543 VFD signal is moved to the N.O. auxiliary contacts 13 and 14).

It is good practice, when using a contactor like this for a large DC load, to interrupt both legs (plus and minus) so that the complete circuit is broken in more places. This reduces arcing.
PeteJ
Posts: 6
Joined: Fri Jan 05, 2024 3:12 pm
Acorn CNC Controller: No
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: Yes
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: A901347
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Allin1DC upgrade on Atrump mill- wiring and identifying 10537 DC servo motor transformer

Post by PeteJ »

Continuing the wiring questions I'm trying to map the wiring for the spindle on my old control to the new wiring.
Such as the VFD fault reset on connector h9 pins one and two but the remainder have me somewhat confused because the nomenclature is not identical.
I've attached images of the old schematic, pin wiring for the old H9 connector and the new schematic.


20240118_174547.jpg
20240118_174035.jpg
20240118_174230.jpg
Post Reply