wired mpg E-Stop integrate into plc
I connected a wired handwheel to the Oak. Now the E-Stop button still needs to be programmed in the PLC.
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
Re: wired mpg E-Stop integrate into plc
There are several ways to do it.
The simplest is to just locate every place where the PLC program tests "EStopOk_I" and expand that to read "(EStopOk_I && MPG_AUX_1_I)" (assuming, of course, that your MPG E-Stop button is normally-closed).
The simplest is to just locate every place where the PLC program tests "EStopOk_I" and expand that to read "(EStopOk_I && MPG_AUX_1_I)" (assuming, of course, that your MPG E-Stop button is normally-closed).
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 158
- Joined: Sun Nov 12, 2023 1:33 pm
- Acorn CNC Controller: No
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: Yes
- CNC Control System Serial Number: A901313
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Switzerland
Re: wired mpg E-Stop integrate into plc
thanks
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 13
- Joined: Wed Sep 07, 2022 9:39 am
- Acorn CNC Controller: No
- Allin1DC CNC Controller: No
- Oak CNC controller: Yes
- CNC Control System Serial Number: various
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Milano - Italy
- Contact:
Re: wired mpg E-Stop integrate into plc
Buongiorno Houseman303,
Did you connect a handweel with an integrated emergency button?
How did you connect him to Oak?
Thank you in advance.
Did you connect a handweel with an integrated emergency button?
How did you connect him to Oak?
Thank you in advance.
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 158
- Joined: Sun Nov 12, 2023 1:33 pm
- Acorn CNC Controller: No
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: Yes
- CNC Control System Serial Number: A901313
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Switzerland
Re: wired mpg E-Stop integrate into plc
Emergency stop at MpgAux In1 and +5v. NC switching of the emergency stop. PLC programming is above.
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 13
- Joined: Wed Sep 07, 2022 9:39 am
- Acorn CNC Controller: No
- Allin1DC CNC Controller: No
- Oak CNC controller: Yes
- CNC Control System Serial Number: various
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Milano - Italy
- Contact:
Re: wired mpg E-Stop integrate into plc
Grazie,
In Europe it is necessary to have this emergency button.
Until now I have solved it in other ways, but this is much better.
Thanks again.
Emanuele
In Europe it is necessary to have this emergency button.
Until now I have solved it in other ways, but this is much better.
Thanks again.
Emanuele
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 158
- Joined: Sun Nov 12, 2023 1:33 pm
- Acorn CNC Controller: No
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: Yes
- CNC Control System Serial Number: A901313
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Switzerland
Re: wired mpg E-Stop integrate into plc
That's why I also have a wired handwheel. Wireless handwheel is not safety compliant. I could still imagine it with a Linux system, but definitely not with Windows 10/11!
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Site Admin
- Posts: 8841
- Joined: Wed Mar 03, 2010 4:23 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: Yes
- CNC Control System Serial Number: none
- DC3IOB: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Contact:
Re: wired mpg E-Stop integrate into plc
i've been using it for about 5 years now, not one issue if you have windows configured properly for CNC use.Houseman303 wrote: ↑Thu Jan 18, 2024 4:05 am That's why I also have a wired handwheel. Wireless handwheel is not safety compliant. I could still imagine it with a Linux system, but definitely not with Windows 10/11!
Need support? READ THIS POST first. http://centroidcncforum.com/viewtopic.php?f=60&t=1043
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 13
- Joined: Wed Sep 07, 2022 9:39 am
- Acorn CNC Controller: No
- Allin1DC CNC Controller: No
- Oak CNC controller: Yes
- CNC Control System Serial Number: various
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Milano - Italy
- Contact:
Re: wired mpg E-Stop integrate into plc
We also use it without problems, but in Europe, the handweel MUST have a hardware emergency button to the current regulations.
(Note: Liking will "up vote" a post in the search results helping others find good information faster)