Making progress but have run into a question. Working on getting the E-stop buttons wired up.
The front panel on the Acer, one used for Spindle speed and direction. I assume that it can go away, and the wiring can be removed.
There is an E-Stop located up there. Should I leave it or remove and put one near the operator display? EDIT: I found another post discussing similar setup. Sounds like I can keep that E-stop. (There is a separate on/off switch for the cabinet with the VFD. My guess is it is the reason there is a second Contactor...see below)
Looking at this also began a rabbit hole research into the VFD and getting it wired up.
This mill uses a Toshiba VFS7-2037P Input source is listed as 3PH -200~230V-50/60Hz.
I have been running the mill using just 220V 1PH. Not sure how or why that was working....EDIT: I will be connecting it with 3PH now that I know it is needed by the VFD, unless someone tell me not to.
Anyone familiar with this particular model and converting it to Allin1DC?
Looking at the documentation/print for Allin1DC I do not see a second Contactor, like this mill had. Can that also be omitted?
Acer e-Mill Anilam to AllIn1DC conversion build
Moderator: cnckeith
-
- Posts: 65
- Joined: Fri Mar 03, 2023 6:56 pm
- Acorn CNC Controller: No
- Allin1DC CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: 0008dc111213-1223222881
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Re: Acer e-Mill Anilam to AllIn1DC conversion build
centroid467 wrote: ↑Tue Mar 07, 2023 10:29 am Several things:
3. It is likely that you will need a step down transformer to go from whatever you plan on powering the mill with (120VAC, 220VAC etc) down to a safe level. The ALLIN1DC is specified for motor voltages from 20 to 180 VDC. 83 VAC is a good choice because it rectifies to 120 VDC. The Anilam motors should be alright as long as you are rectifying less than 99 VAC.
Just now realized that I DO need a transformer.
What kind of current output am I looking for when sizing the transformer?
1A, 2A or 4A?
Figure on going from 110vac to 80vac
What I find more confusing is the transformer listed for sale by Centroid is 110 to 120/ VAC Input and Output is 117 DC. The picture attached even shows it being connected to the CAPBRD where the print shows AC current being connected.
Re: Acer e-Mill Anilam to AllIn1DC conversion build
Transformers do not output DC.
The text in the description is for the power supply as a whole: you put ca. 120VAC into the transformer, and you get ca. 120VDC out of the connected rectifier (CAPBRDLO and capacitor).
There is also a typo in that description, "motors with voltage ratings higher than 117VAC". DC brushed servo motors are rated for a maximum VDC, not VAC.
Assuming you are planning to power three servo motors, you would ideally want a transformer capable of supplying at least 15A at ca. 80VAC; but 10A would probably be sufficient. 4A would be woefully inadequate for anything more than bench testing.
The text in the description is for the power supply as a whole: you put ca. 120VAC into the transformer, and you get ca. 120VDC out of the connected rectifier (CAPBRDLO and capacitor).
There is also a typo in that description, "motors with voltage ratings higher than 117VAC". DC brushed servo motors are rated for a maximum VDC, not VAC.
Assuming you are planning to power three servo motors, you would ideally want a transformer capable of supplying at least 15A at ca. 80VAC; but 10A would probably be sufficient. 4A would be woefully inadequate for anything more than bench testing.
-
- Posts: 7292
- Joined: Wed Mar 03, 2010 4:23 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: Yes
- CNC Control System Serial Number: none
- DC3IOB: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Contact:
Re: Acer e-Mill Anilam to AllIn1DC conversion build
please tell me the location of that image, the price is wrong as well.Skunk wrote: ↑Tue Mar 14, 2023 11:46 amcentroid467 wrote: ↑Tue Mar 07, 2023 10:29 am Several things:
3. It is likely that you will need a step down transformer to go from whatever you plan on powering the mill with (120VAC, 220VAC etc) down to a safe level. The ALLIN1DC is specified for motor voltages from 20 to 180 VDC. 83 VAC is a good choice because it rectifies to 120 VDC. The Anilam motors should be alright as long as you are rectifying less than 99 VAC.
Just now realized that I DO need a transformer.
What kind of current output am I looking for when sizing the transformer?
1A, 2A or 4A?
Figure on going from 110vac to 80vac
What I find more confusing is the transformer listed for sale by Centroid is 110 to 120/ VAC Input and Output is 117 DC. The picture attached even shows it being connected to the CAPBRD where the print shows AC current being connected.
Transformer.png
Need support? READ THIS POST first. http://centroidcncforum.com/viewtopic.php?f=60&t=1043
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
-
- Posts: 3095
- Joined: Tue Mar 22, 2016 10:03 am
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: Yes
- CNC Control System Serial Number: 100505
100327
102696
103432
7804732B977B-0624192192 - DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Boston, MA
- Contact:
Re: Acer e-Mill Anilam to AllIn1DC conversion build
Actually, the photos shows the capboard being screwed to the two terminals on top of the capacitor. The transformer in the background is confusing, but the transformer leads are just coiled in front of the transformer.
Cheers,
Tom
Confidence is the feeling you have before you fully understand the situation.
I have CDO. It's like OCD, but the letters are where they should be.
Tom
Confidence is the feeling you have before you fully understand the situation.
I have CDO. It's like OCD, but the letters are where they should be.
-
- Posts: 65
- Joined: Fri Mar 03, 2023 6:56 pm
- Acorn CNC Controller: No
- Allin1DC CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: 0008dc111213-1223222881
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Re: Acer e-Mill Anilam to AllIn1DC conversion build
please tell me the location of that image, the price is wrong as well.
[/quote]
Looks like you must have found it. It was on this page ...'https://www.centroidcnc.com/centroid_di ... oller.html'
-
- Posts: 65
- Joined: Fri Mar 03, 2023 6:56 pm
- Acorn CNC Controller: No
- Allin1DC CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: 0008dc111213-1223222881
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Re: Acer e-Mill Anilam to AllIn1DC conversion build
Thanks Tom. I think my confusion was not seeing this as a power supply system, instead I was seeing two separate/independent devices.
-
- Posts: 7292
- Joined: Wed Mar 03, 2010 4:23 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: Yes
- CNC Control System Serial Number: none
- DC3IOB: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Contact:
Re: Acer e-Mill Anilam to AllIn1DC conversion build
Looks like you must have found it. It was on this page ...'https://www.centroidcnc.com/centroid_di ... oller.html'
[/quote]
yep, found and fixed. thanks, k
Need support? READ THIS POST first. http://centroidcncforum.com/viewtopic.php?f=60&t=1043
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
-
- Posts: 7292
- Joined: Wed Mar 03, 2010 4:23 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: Yes
- CNC Control System Serial Number: none
- DC3IOB: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Contact:
Re: Acer e-Mill Anilam to AllIn1DC conversion build
this subject is covered in detail starting here.Skunk wrote: ↑Tue Mar 14, 2023 11:46 amcentroid467 wrote: ↑Tue Mar 07, 2023 10:29 am Several things:
3. It is likely that you will need a step down transformer to go from whatever you plan on powering the mill with (120VAC, 220VAC etc) down to a safe level. The ALLIN1DC is specified for motor voltages from 20 to 180 VDC. 83 VAC is a good choice because it rectifies to 120 VDC. The Anilam motors should be alright as long as you are rectifying less than 99 VAC.
Just now realized that I DO need a transformer.
What kind of current output am I looking for when sizing the transformer?
1A, 2A or 4A?
Figure on going from 110vac to 80vac
What I find more confusing is the transformer listed for sale by Centroid is 110 to 120/ VAC Input and Output is 117 DC. The picture attached even shows it being connected to the CAPBRD where the print shows AC current being connected.
Transformer.png
Need support? READ THIS POST first. http://centroidcncforum.com/viewtopic.php?f=60&t=1043
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
-
- Posts: 65
- Joined: Fri Mar 03, 2023 6:56 pm
- Acorn CNC Controller: No
- Allin1DC CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: 0008dc111213-1223222881
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Re: Acer e-Mill Anilam to AllIn1DC conversion build
ok I am to the point of getting the spindle working. Fairly certain, by looking at the included manual page from the Toshiba VFD, that I can go from the VFD to the Allin1DC by passing the reversing contactors that were present in the Anilam system. I'd like to hear different if you think I should do differently.