not returning to machine zero
i apologise if this is in the wrong area it seemed like the right place, im not sure whta my controller is or model ,its a bridgeport retrofit 3 axis and its great,however,this morning i turned it on sent it to machine home and its going past the limit switches.it still zeros and is ready to work but i cant go into mdi unless i move it back inside ,all 3 axes are doing this, im not terribly elctronic savvy so...any ideas? i tried moving the limit switches in a little on the z but it hasnt changed anything,,,hope im explaining this right....heres another way of saying it... if i move x and y in to the middle of their travel,move z down ..go into mdi>g28zoxoyo it does everything expected and returns to machine zero,if i use the hand controller form inside the travel it goes and trips the limit switch but about .4'' further then g28 zero and mdi will be disabled until i move it off the limit switch... yesterday it was fine this morning its doing this.. nothing has changed or happened..
Re: not returning to machine zero
please post a fresh report.zip
Sounds like your soft limits where deleted. Post a report and we can see that.
Reported Generated: Fri Nov 11 14:09:44 2022
MPU12 serial number: 0008DC111213-0228222740
License: SERVO PRO
Version: CNC12-D Mill v4.20
Repo info: URL: /cnc11/trunk R12260 clean Mar 11 2021, 15:00:41
Machine Timers info
Power On : 000005.134
Job in Progress : 000000.010
Spindle Running : 000000.000
Since : 00/00/0
Operating System info:
Edition : Windows 10 Enterprise (10.0)
Version : 2009
OS Build : 22000.652
Memory info:
Total physical memory : 17076547584
Available physical memory : 14446444544
Processor info:
Intel(R) Core(TM) i5-8279U CPU @ 2.40GHz
Number of cores : 4
Number of logical processors : 8
Display Size: Width 1920 Height 1080
Installed Software:
Mill software installed
Mill Demo not installed
Lathe software not installed
Lathe Demo not installed
Configuration file
CNC12 Virtual v. 4.200 setup file for MPU11 serial number 0008DC111213-02282227
DRO display units: Inches
Machine units: Inches
Max spindle (high range): 4200.0
Min spindle (high range): 0.0
Machine home at pwrup: Home Switch
PLC type: Standard
Jog Panel type Virtual
Jog panel required: Yes
Remote Drive & Directory:
Fourth axis level offset 0
Fifth axis level offset 0
Axis Slow Jog Fast Jog (-) Fast Jog (+) Slow Jog Probe Fast Jog (-) Probe Fast Jog (+) Probe Max Rate Deadstart Delta Vmax
(in/min) (in/min) (in/min) (in/min) (in/min) (in/min) (in/min) (in/min) (in/min)
1 25.0000 75.0000 75.0000 25.0000 75.0000 75.0000 100.0000 3.0000 3.0000
2 25.0000 75.0000 75.0000 25.0000 75.0000 75.0000 100.0000 3.0000 3.0000
3 25.0000 75.0000 75.0000 25.0000 75.0000 75.0000 85.0000 3.0000 3.0000
4 25.0000 100.0000 100.0000 25.0000 100.0000 100.0000 300.0000 3.0000 3.0000
5 25.0000 100.0000 100.0000 25.0000 100.0000 100.0000 300.0000 3.0000 3.0000
6 25.0000 100.0000 100.0000 25.0000 100.0000 100.0000 300.0000 3.0000 3.0000
7 25.0000 100.0000 100.0000 25.0000 100.0000 100.0000 300.0000 3.0000 3.0000
8 25.0000 100.0000 100.0000 25.0000 100.0000 100.0000 300.0000 3.0000 3.0000
Axis Label Motor Encoder Lash Comp. Limit Home Dir Screw
revs/in counts/rev. (inches) - + - + Rev Comp
1 X 5.0000000000000000 20000 0.0000 1 2 1 2 N N
2 Y 5.0000000000000000 20000 0.0060 3 4 3 4 N N
3 Z 5.0000000000000000 8000 0.0008 5 6 5 6 N N
4 N 5.0000000000000000 8000 0.0000 0 0 30 30 N N
5 N 5.0000000000000000 8000 0.0000 0 0 0 0 N N
6 N 5.0000000000000000 8000 0.0000 0 0 0 0 N N
7 N 5.0000000000000000 8000 0.0000 0 0 0 0 N N
8 N 5.0000000000000000 8000 0.0000 0 0 0 0 N N
Axis Kp Ki Kd Limit Kg Kv1 Ka Accel
X 1.0000 0.004000 3.0000 32000 -0.4466 5.0854 13.6646 0.1930
Y 1.0000 0.004000 3.0000 32000 -0.1930 5.2976 9.7609 0.1130
Z 1.0000 0.004000 3.0000 32000 -2.4500 0.1385 5.1436 0.1000
N 1.0000 0.004000 3.0000 32000 0.0000 0.0000 0.0000 0.5000
Job file
Last job file: C:\cncm\ncfiles\1001.nc
Part count: 1 Edge Finder Diameter: 0.0000
PID Collection Axis: 1 Density: 1 Extension:
Move Commands: 1
2
3
4
5
WCS: #1 X axis Y axis Z axis N axis N axis N axis N axis N axis
G52 Shift Distance: 0.0000 0.0000 0.0000 0.0000 0.0000 0.0000 0.0000 0.0000
Home State: Set Set Set Not set Not set Not set Not set Not set
Tool Reference: Not set Not set -4.0000 Not set Not set Not set Not set Not set
Digitize Grid Radial Grid Radial
Filename: Multi Patch: No
Replay Feedrate: 3.0000 3.0000 Pattern: Zig Zag Zig Zag
Envelope: X 1.0000 S 0.00 Step: X 0.0100 0.0100
Y 1.0000 E 90.00 Y 0.0100
R 1.0000
Z Depth: 1.0000 1.0000 Z Step: 0.1000 0.0100
Grid First Axis: 0 Radial containment: Full Clearance Ht: 0.0100
Job Progress Recorded. Program Stack Level (PSL) = 0
Prog Line Repeat File Date/Time
PSL Num Number Countdn YYYYMMDDHHMMSS File Path
00 20000 00000018 00001 20221010110930 C:\cncm\ncfiles\1001.nc
Canned Cycle Repeat Countdown = 0, Canned Cycle Progress = 0
Perform 'Forced' Tool Change: Yes
Tool in spindle: 5
ATC Error code: 0
Saved user variable values:
#150 = 0.0000
#151 = 0.0000
#152 = 0.0000
#153 = 0.0000
#154 = 0.0000
#155 = 0.0000
#156 = 0.0000
#157 = 0.0000
#158 = 0.0000
#159 = 0.0000
Machine Parameters
00 -11.00000| 20 72.00000| 40 0.00010| 60 0.00000| 80 0.00000
01 0.00000| 21 0.02000| 41 0.00010| 61 0.50000| 81 -1.00000
02 0.00000| 22 0.02000| 42 0.00000| 62 90.00000| 82 0.00000
03 0.00000| 23 0.02000| 43 0.00000| 63 1.50000| 83 0.05000
04 5.00000| 24 0.02000| 44 0.00000| 64 0.00000| 84 3.00000
05 0.00000| 25 0.68000| 45 0.00000| 65 1.00000| 85 0.00000
06 0.00000| 26 0.68000| 46 0.00000| 66 1.00000| 86 0.00000
07 0.00000| 27 0.68000| 47 0.00000| 67 1.00000| 87 18.75000
08 2.00000| 28 0.68000| 48 0.10000| 68 0.00000| 88 18.75000
09 0.00000| 29 150.00000| 49 0.00000| 69 1.00000| 89 18.75000
10 0.00000| 30 180.00000| 50 0.00000| 70 0.00100| 90 18.75000
11 50769.00000| 31 0.00000| 51 0.00000| 71 0.00000| 91 0.00000
12 0.00000| 32 26.00000| 52 0.00000| 72 0.00000| 92 0.00000
13 0.05000| 33 1.00000| 53 0.00000| 73 0.05000| 93 0.00000
14 10.00000| 34 8000.00000| 54 0.00000| 74 4.00000| 94 0.00000
15 1.00000| 35 5.00000| 55 0.00000| 75 0.00000| 95 2.00000
16 10.00000| 36 0.00000| 56 4.00000| 76 0.00000| 96 2.00000
17 0.00000| 37 10.00000| 57 0.00000| 77 0.00000| 97 1.00000
18 50771.00000| 38 0.00000| 58 0.00000| 78 0.00000| 98 2.00000
19 2.00000| 39 200.00000| 59 0.00000| 79 70.00000| 99 10.00000
100 1.00000| 120 0.10000| 140 4.00000| 160 0.00000| 180 0.00000
101 0.10000| 121 0.00200| 141 10000.00000| 161 0.00000| 181 19.20000
102 3.00000| 122 0.00020| 142 1000.00000| 162 0.00000| 182 801.00000
103 75.00000| 123 0.00000| 143 11.00000| 163 0.00000| 183 0.00000
104 0.00000| 124 0.00000| 144 0.00000| 164 0.00000| 184 10.00000
105 0.00000| 125 0.00000| 145 0.00000| 165 0.00000| 185 0.00000
106 1.00000| 126 0.00000| 146 0.00000| 166 0.00000| 186 0.00000
107 0.00000| 127 0.00000| 147 10.00000| 167 0.00000| 187 16000.00000
108 1.00000| 128 0.00000| 148 0.00000| 168 0.00000| 188 7.00000
109 1.00000| 129 0.00000| 149 1.00000| 169 0.00000| 189 8.00000
110 0.00000| 130 0.00000| 150 0.00000| 170 1.00000| 190 7.00000
111 0.00000| 131 0.00000| 151 0.00000| 171 0.00000| 191 0.00000
112 0.00000| 132 0.02000| 152 0.00000| 172 0.00000| 192 0.00000
113 0.00000| 133 0.02000| 153 0.00000| 173 0.00000| 193 0.00000
114 0.00000| 134 0.02000| 154 0.00000| 174 0.00000| 194 0.00000
115 0.00000| 135 0.02000| 155 0.00000| 175 0.00000| 195 0.00000
116 0.00000| 136 0.00000| 156 2.00000| 176 0.00000| 196 0.00000
117 0.00000| 137 0.00000| 157 2.00000| 177 0.00000| 197 0.00000
118 0.00000| 138 0.00000| 158 2.00000| 178 0.00000| 198 0.00000
119 0.00000| 139 0.00000| 159 2.00000| 179 0.00000| 199 0.00000
200 0.00000| 220 1.00000| 240 0.10000| 260 1.00000| 280 0.00000
201 0.00000| 221 1.00000| 241 20.00000| 261 0.00000| 281 0.00000
202 0.00000| 222 0.00100| 242 0.00000| 262 0.00000| 282 0.00000
203 0.00000| 223 800.00000| 243 0.00000| 263 0.00000| 283 0.00000
204 0.00000| 224 0.00000| 244 0.00000| 264 0.00000| 284 50.00000
205 0.00000| 225 4.00000| 245 0.00000| 265 0.00000| 285 50.00000
206 0.00000| 226 10.00000| 246 0.00000| 266 0.00000| 286 50.00000
207 0.00000| 227 73.00000| 247 0.00000| 267 0.00000| 287 50.00000
208 0.12500| 228 0.00000| 248 0.00000| 268 0.00000| 288 50.00000
209 0.12500| 229 0.00000| 249 0.00000| 269 0.00000| 289 50.00000
210 0.12500| 230 1.25150| 250 0.00000| 270 0.00000| 290 50.00000
211 0.12500| 231 0.17350| 251 0.00000| 271 0.00000| 291 50.00000
212 0.12500| 232 0.00000| 252 18.75000| 272 0.00000| 292 0.00000
213 0.12500| 233 0.00000| 253 18.75000| 273 0.00000| 293 0.00000
214 0.12500| 234 0.00000| 254 18.75000| 274 0.00000| 294 0.00000
215 0.12500| 235 0.00000| 255 18.75000| 275 0.00000| 295 0.00000
216 0.00000| 236 0.68000| 256 0.00000| 276 0.00000| 296 0.00000
217 0.00000| 237 0.68000| 257 0.00000| 277 0.00000| 297 0.00000
218 0.00000| 238 0.68000| 258 0.00000| 278 0.00000| 298 0.00000
219 1.00000| 239 0.68000| 259 0.00000| 279 0.00000| 299 0.00000
300 1.00000| 320 0.00000| 340 0.00000| 360 0.00000| 380 0.00000
301 2.00000| 321 0.00000| 341 0.00000| 361 0.00000| 381 54.00000
302 3.00000| 322 0.00000| 342 0.00000| 362 0.00000| 382 55.00000
303 0.00000| 323 0.00000| 343 0.00000| 363 0.00000| 383 0.00000
304 0.00000| 324 0.00000| 344 0.00000| 364 0.00000| 384 0.00000
305 0.00000| 325 0.00000| 345 0.00000| 365 0.00000| 385 0.00000
306 0.00000| 326 0.00000| 346 0.00000| 366 2.00000| 386 0.00000
307 0.00000| 327 0.00000| 347 0.00000| 367 2.00000| 387 0.00000
308 1.00000| 328 0.00000| 348 0.00000| 368 4.00000| 388 0.00000
309 2.00000| 329 0.00000| 349 100.00000| 369 75.00000| 389 0.00000
310 3.00000| 330 0.00000| 350 400.00000| 370 0.00000| 390 0.00000
311 0.00000| 331 0.00000| 351 0.00000| 371 0.00000| 391 1000.00000
312 0.00000| 332 0.00000| 352 100.00000| 372 0.00000| 392 0.00000
313 6.00000| 333 0.00000| 353 400.00000| 373 0.00000| 393 0.10000
314 0.00000| 334 0.00000| 354 0.00000| 374 0.00000| 394 0.10000
315 0.00000| 335 0.00000| 355 100.00000| 375 0.00000| 395 30.00000
316 0.00000| 336 0.00000| 356 400.00000| 376 0.00000| 396 30.00000
317 0.00000| 337 0.00000| 357 0.00000| 377 0.00000| 397 0.25000
318 0.00000| 338 0.00000| 358 0.00000| 378 0.00000| 398 1.00000
319 0.00000| 339 0.00000| 359 0.00000| 379 0.00000| 399 0.50000
400 0.00000| 420 0.00000| 440 0.00000| 460 0.00000| 480 0.00000
401 0.00000| 421 0.00000| 441 0.00000| 461 0.00000| 481 0.00000
402 0.00000| 422 0.00000| 442 0.00000| 462 0.00000| 482 0.00000
403 0.00000| 423 0.00000| 443 0.00000| 463 0.00000| 483 0.00000
404 0.00000| 424 0.00000| 444 0.00000| 464 0.00000| 484 0.00000
405 0.00000| 425 0.00000| 445 0.00000| 465 0.00000| 485 0.00000
406 0.00000| 426 0.00000| 446 0.00000| 466 0.00000| 486 0.00000
407 0.00000| 427 0.00000| 447 0.00000| 467 0.00000| 487 0.00000
408 0.00000| 428 0.00000| 448 0.00000| 468 0.00000| 488 0.00000
409 0.00000| 429 0.00000| 449 0.00000| 469 0.00000| 489 0.00000
410 0.00000| 430 0.00000| 450 0.00000| 470 0.00000| 490 0.00000
411 0.00000| 431 0.00000| 451 0.00000| 471 0.00000| 491 0.00000
412 0.00000| 432 0.00000| 452 0.00000| 472 0.00000| 492 0.00000
413 0.00000| 433 0.00000| 453 0.00000| 473 0.00000| 493 0.00000
414 0.00000| 434 0.00000| 454 0.00000| 474 0.00000| 494 0.00000
415 0.00000| 435 0.00000| 455 0.00000| 475 0.00000| 495 0.00000
416 0.00000| 436 0.00000| 456 0.00000| 476 0.00000| 496 0.00000
417 0.00000| 437 0.00000| 457 0.00000| 477 0.00000| 497 0.00000
418 0.00000| 438 0.00000| 458 0.00000| 478 0.00000| 498 0.00000
419 0.00000| 439 0.00000| 459 0.00000| 479 0.00000| 499 0.00000
500 0.00000| 520 0.00000| 540 0.00000| 560 0.00000| 580 0.00000
501 0.00000| 521 0.00000| 541 0.00000| 561 0.00000| 581 0.00000
502 0.00000| 522 0.00000| 542 0.00000| 562 0.00000| 582 0.00000
503 0.00000| 523 0.00000| 543 0.00000| 563 0.00000| 583 0.00000
504 0.00000| 524 0.00000| 544 0.00000| 564 0.00000| 584 0.00000
505 0.00000| 525 0.00000| 545 0.00000| 565 0.00000| 585 0.00000
506 0.00000| 526 0.00000| 546 0.00000| 566 0.00000| 586 0.00000
507 0.00000| 527 0.00000| 547 0.00000| 567 0.00000| 587 0.00000
508 0.00000| 528 0.00000| 548 0.00000| 568 0.00000| 588 0.00000
509 0.00000| 529 0.00000| 549 0.00000| 569 0.00000| 589 0.00000
510 0.00000| 530 0.00000| 550 0.00000| 570 0.00000| 590 0.00000
511 0.00000| 531 0.00000| 551 0.00000| 571 0.00000| 591 0.00000
512 0.00000| 532 0.00000| 552 0.00000| 572 0.00000| 592 0.00000
513 0.00000| 533 0.00000| 553 0.00000| 573 0.00000| 593 0.00000
514 0.00000| 534 0.00000| 554 0.00000| 574 0.00000| 594 0.00000
515 0.00000| 535 0.00000| 555 0.00000| 575 0.00000| 595 0.00000
516 0.00000| 536 0.00000| 556 0.00000| 576 0.00000| 596 0.00000
517 0.00000| 537 0.00000| 557 0.00000| 577 0.00000| 597 0.00000
518 0.00000| 538 0.00000| 558 0.00000| 578 0.00000| 598 0.00000
519 0.00000| 539 0.00000| 559 0.00000| 579 0.00000| 599 0.00000
600 0.00000| 620 0.00000| 640 0.00000| 660 0.00000| 680 0.00000
601 0.00000| 621 0.00000| 641 0.00000| 661 0.00000| 681 0.00000
602 0.00000| 622 0.00000| 642 0.00000| 662 0.00000| 682 0.00000
603 0.00000| 623 0.00000| 643 0.00000| 663 0.00000| 683 0.00000
604 0.00000| 624 0.00000| 644 0.00000| 664 0.00000| 684 0.00000
605 0.00000| 625 0.00000| 645 0.00000| 665 0.00000| 685 0.00000
606 0.00000| 626 0.00000| 646 0.00000| 666 0.00000| 686 0.00000
607 0.00000| 627 0.00000| 647 0.00000| 667 0.00000| 687 0.00000
608 0.00000| 628 0.00000| 648 0.00000| 668 0.00000| 688 0.00000
609 0.00000| 629 0.00000| 649 0.00000| 669 0.00000| 689 0.00000
610 0.00000| 630 0.00000| 650 0.00000| 670 0.00000| 690 0.00000
611 0.00000| 631 0.00000| 651 0.00000| 671 0.00000| 691 0.00000
612 0.00000| 632 0.00000| 652 0.00000| 672 0.00000| 692 0.00000
613 0.00000| 633 0.00000| 653 0.00000| 673 0.00000| 693 0.00000
614 0.00000| 634 0.00000| 654 0.00000| 674 0.00000| 694 0.00000
615 0.00000| 635 0.00000| 655 0.00000| 675 0.00000| 695 0.00000
616 0.00000| 636 0.00000| 656 0.00000| 676 0.00000| 696 0.00000
617 0.00000| 637 0.00000| 657 0.00000| 677 0.00000| 697 0.00000
618 0.00000| 638 0.00000| 658 0.00000| 678 0.00000| 698 0.00000
619 0.00000| 639 0.00000| 659 0.00000| 679 0.00000| 699 0.00000
700 0.00000| 720 0.00000| 740 0.00000| 760 0.00000| 780 0.00000
701 0.00000| 721 0.00000| 741 0.00000| 761 0.00000| 781 0.00000
702 0.00000| 722 0.00000| 742 0.00000| 762 0.00000| 782 0.00000
703 0.00000| 723 0.00000| 743 0.00000| 763 0.00000| 783 0.00000
704 0.00000| 724 0.00000| 744 0.00000| 764 0.00000| 784 0.00000
705 0.00000| 725 0.00000| 745 0.00000| 765 0.00000| 785 0.00000
706 0.00000| 726 0.00000| 746 0.00000| 766 0.00000| 786 0.00000
707 0.00000| 727 0.00000| 747 0.00000| 767 0.00000| 787 0.00000
708 0.00000| 728 0.00000| 748 0.00000| 768 0.00000| 788 0.00000
709 0.00000| 729 0.00000| 749 0.00000| 769 0.00000| 789 0.00000
710 0.00000| 730 0.00000| 750 0.00000| 770 0.00000| 790 0.00000
711 0.00000| 731 0.00000| 751 0.00000| 771 0.00000| 791 0.00000
712 0.00000| 732 0.00000| 752 0.00000| 772 0.00000| 792 0.00000
713 0.00000| 733 0.00000| 753 0.00000| 773 0.00000| 793 0.00000
714 0.00000| 734 0.00000| 754 0.00000| 774 0.00000| 794 0.00000
715 0.00000| 735 0.00000| 755 0.00000| 775 0.00000| 795 0.00000
716 0.00000| 736 0.00000| 756 0.00000| 776 0.00000| 796 0.00000
717 0.00000| 737 0.00000| 757 0.00000| 777 0.00000| 797 0.00000
718 0.00000| 738 0.00000| 758 0.00000| 778 0.00000| 798 0.00000
719 0.00000| 739 0.00000| 759 0.00000| 779 0.00000| 799 0.00000
800 0.00000| 820 0.00000| 840 0.00000| 860 0.00000| 880 0.00000
801 0.00000| 821 0.00000| 841 0.00000| 861 0.00000| 881 0.00000
802 0.00000| 822 0.00000| 842 0.00000| 862 0.00000| 882 0.00000
803 0.00000| 823 0.00000| 843 0.00000| 863 0.00000| 883 0.00000
804 0.00000| 824 0.00000| 844 0.00000| 864 0.00000| 884 0.00000
805 0.00000| 825 0.00000| 845 0.00000| 865 0.00000| 885 0.00000
806 0.00000| 826 0.00000| 846 0.00000| 866 0.00000| 886 0.00000
807 0.00000| 827 0.00000| 847 0.00000| 867 0.00000| 887 0.00000
808 0.00000| 828 0.00000| 848 0.00000| 868 0.00000| 888 0.00000
809 0.00000| 829 0.00000| 849 0.00000| 869 0.00000| 889 0.00000
810 0.00000| 830 0.00000| 850 0.00000| 870 0.00000| 890 0.00000
811 0.00000| 831 0.00000| 851 0.00000| 871 0.00000| 891 0.00000
812 0.00000| 832 0.00000| 852 0.00000| 872 0.00000| 892 0.00000
813 0.00000| 833 0.00000| 853 0.00000| 873 0.00000| 893 0.00000
814 0.00000| 834 0.00000| 854 0.00000| 874 0.00000| 894 0.00000
815 0.00000| 835 0.00000| 855 0.00000| 875 0.00000| 895 0.00000
816 0.00000| 836 0.00000| 856 0.00000| 876 0.00000| 896 0.00000
817 0.00000| 837 0.00000| 857 0.00000| 877 0.00000| 897 0.00000
818 0.00000| 838 0.00000| 858 0.00000| 878 0.00000| 898 0.00000
819 0.00000| 839 0.00000| 859 0.00000| 879 0.00000| 899 0.00000
900 0.00000| 920 0.00000| 940 0.00000| 960 0.00000| 980 0.00000
901 0.00000| 921 0.00000| 941 0.00000| 961 0.00000| 981 0.00000
902 0.00000| 922 0.00000| 942 0.00000| 962 0.00000| 982 0.00000
903 0.00000| 923 0.00000| 943 0.00000| 963 0.00000| 983 0.00000
904 0.00000| 924 0.00000| 944 0.00000| 964 0.00000| 984 0.00000
905 0.00000| 925 0.00000| 945 0.00000| 965 0.00000| 985 0.00000
906 0.00000| 926 0.00000| 946 0.00000| 966 0.00000| 986 0.00000
907 0.00000| 927 0.00000| 947 0.00000| 967 0.00000| 987 0.00000
908 0.00000| 928 0.00000| 948 0.00000| 968 0.00000| 988 0.00000
909 0.00000| 929 0.00000| 949 0.00000| 969 0.00000| 989 0.00000
910 0.00000| 930 0.00000| 950 0.00000| 970 0.00000| 990 0.00000
911 0.00000| 931 0.00000| 951 0.00000| 971 0.00000| 991 0.00000
912 0.00000| 932 0.00000| 952 0.00000| 972 0.00000| 992 0.00000
913 0.00000| 933 0.00000| 953 0.00000| 973 0.00000| 993 0.00000
914 0.00000| 934 0.00000| 954 0.00000| 974 0.00000| 994 0.00000
915 0.00000| 935 0.00000| 955 0.00000| 975 0.00000| 995 0.00000
916 0.00000| 936 0.00000| 956 0.00000| 976 0.00000| 996 0.00000
917 0.00000| 937 0.00000| 957 0.00000| 977 0.00000| 997 0.00000
918 0.00000| 938 0.00000| 958 0.00000| 978 0.00000| 998 0.00000
919 0.00000| 939 0.00000| 959 0.00000| 979 0.00000| 999 0.00000
License: SERVO PRO
Machine Timers info
Since : 00/00/0
Version : 2009
Memory info:
Processor info:
Number of cores : 4
Installed Software:
Configuration file
PLC type: Standard
Job file
Move Commands: 1
2
3
4
5
R 1.0000
Tool in spindle: 5
ATC Error code: 0
#150 = 0.0000
#151 = 0.0000
#152 = 0.0000
#153 = 0.0000
#154 = 0.0000
#155 = 0.0000
#156 = 0.0000
#157 = 0.0000
#158 = 0.0000
#159 = 0.0000
Machine Parameters
License: SERVO PRO
Machine Timers info
Since : 00/00/0
Version : 2009
Memory info:
Processor info:
Number of cores : 4
Installed Software:
Configuration file
PLC type: Standard
Job file
Move Commands: 1
2
3
4
5
R 1.0000
Tool in spindle: 5
ATC Error code: 0
#150 = 0.0000
#151 = 0.0000
#152 = 0.0000
#153 = 0.0000
#154 = 0.0000
#155 = 0.0000
#156 = 0.0000
#157 = 0.0000
#158 = 0.0000
#159 = 0.0000
Machine Parameters
License: SERVO PRO
Machine Timers info
Since : 00/00/0
Version : 2009
Memory info:
Processor info:
Number of cores : 4
Installed Software:
Configuration file
PLC type: Standard
Job file
Move Commands: 1
2
3
4
5
R 1.0000
Tool in spindle: 5
ATC Error code: 0
#150 = 0.0000
#151 = 0.0000
#152 = 0.0000
#153 = 0.0000
#154 = 0.0000
#155 = 0.0000
#156 = 0.0000
#157 = 0.0000
#158 = 0.0000
#159 = 0.0000
Machine Parameters
hope thats what youre referring to ,,learning as i go
That's the report but it's best to just upload the zip file created by CNC12. This way it can be restored to a test machine to see what is happening.
You should be attaching the full zip report to upload.
When you start the machine and the homing cycle runs, what happens? What type of homing switches are we talking about?
If there is an error in the homing process, soft limits are lost.
Keep in mind, home switches are used to home the machine, limit switch are to limit travel, not necessarily the same, and not setup the same.
i moved this thread to the 'servo' side of the forum out of the Acorn Forum.
Some clarifications:
On an Allin1DC installation like yours, the limit switches are the home switches. Axes home to their limits: typically X minus, Y plus, Z plus.
You should set software travel limits, on the Machine Configuration -> Jog Parameters table, to tell the control how far each axis can move from its home position, before it reaches the opposite limit of travel.
An Allin1DC system like yours typically does *not* lose its software travel limits if an error occurs during homing. That unfortunate feature is limited to the auto-squaring macros for certain Acorn gantry router installations.
The partial "report.txt" file that you pasted in above was truncated prior to where the travel limits would be shown. If you were to post (as an attachment, in the "Full Editor" interface) your report.zip file, then we would be able to see your software travel limit values.