I have this repetitive issue. I go to my shop, start my American Rotary Phase converter up, turn on 240vac to my router table. I then power up 120vac to my M400 panel, and everything works fine for about an hour or so. I am still setting up the controller, thus requiring quite a few power down/ power up of both the 240vac and the M400. After an hour or so I start getting a fault I cannot get to reset (usually SpindleError Fault). After I reboot, re-power, everything looks fine. I then hit cycle start to Home the machine, and I get another Spindle Fault error. If I power down repetitive times, and re-power same thing. I get frustrated, give up, and go to house, next day turn on phase converter power up, every thing works fine. It does this everyday.
notes,
1- If I goto to the diag screen, and Cntrl ALT "I" on SpindleInverterOk_I and toggle it, then I get a Panel Comm Fault in the message window.
2- I search forum, and added the timer for Inverter code
Annoying issue (Resolved)
Moderator: cnckeith
-
- Posts: 156
- Joined: Thu Jul 09, 2020 9:50 pm
- Acorn CNC Controller: No
- Allin1DC CNC Controller: No
- Oak CNC controller: Yes
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Annoying issue (Resolved)
- Attachments
-
- report_0610200966_2021-12-12_14-13-01.zip
- (3.51 MiB) Downloaded 51 times
Last edited by repauli1 on Sat Dec 18, 2021 5:52 pm, edited 1 time in total.
Re: Annoying issue
Part of the problem, at least, is that your message file "plcmsg.txt" does not match up with your PLC program source file.
For example, your message file includes:
While your PLC source file includes:
So, when your PLC program wants to report a fault on your #4 axis drive, it requests message #28, and CNC12 displays a spindle drive fault message.
When your PLC program wants to report a spindle drive fault, it requests message #30, and CNC12 displays a jog panel outbound communication fault message.
You should search for -- or ask Centroid for -- a message file that matches the PLC program you are using.
For example, your message file includes:
Code: Select all
28 9028 SPINDLE FAULT!
29 9029 Jog Panel Communication In Fault
30 9030 Jog Panel Communication Out Fault
Code: Select all
AXIS4_DRIVE_FAULT_C IS 7169;(1+256*28)
AXIS5_DRIVE_FAULT_C IS 7425;(1+256*29)
SPINDLE_FAULT_MSG_C IS 7681;(1+256*30)
JOGBOARD_INFLT_C IS 7937;(1+256*31)
JOGBOARD_OUTFLT_C IS 8193;(1+256*32)
When your PLC program wants to report a spindle drive fault, it requests message #30, and CNC12 displays a jog panel outbound communication fault message.
You should search for -- or ask Centroid for -- a message file that matches the PLC program you are using.
-
- Posts: 156
- Joined: Thu Jul 09, 2020 9:50 pm
- Acorn CNC Controller: No
- Allin1DC CNC Controller: No
- Oak CNC controller: Yes
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Re: Annoying issue
That will help me quite a bit, I will check the fault msg file. Thanks!
-
- Posts: 156
- Joined: Thu Jul 09, 2020 9:50 pm
- Acorn CNC Controller: No
- Allin1DC CNC Controller: No
- Oak CNC controller: Yes
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Re: Annoying issue
This reply by cncsw was the fix, found out my slaved axes was the issue, not the spindle!
Like always thank you everyone!