I have a mill that some times I use a 4th axis with.
Anyone know how to setup the home file to detect an input to enable or disable B axis?
I have a jumper in my 4th axis plug that turns on the 4th axis drive if it’s plugged in. It also is wired to input #8.
In #8 true = enable “B” and home “B”
In #8 false = disable “B” don’t home “B”
Home file 4th axis select
Re: Home file 4th axis select
Here's my home file (part you want is the IF at the end):
; For the following tests:
; #20103 = third axis label: 90 = Z (enabled), anything else = disabled
; #50007 = quill clamped switch [INP7] state: 1 = clamped 0 = not clamped
IF [#20103 == 90 && #50007==0] THEN GOTO 20 ; 3-axis mode, but failed to clamp
IF [#20103 != 90 && #50007==1] THEN GOTO 30 ; 2-axis mode, but quill is clamped
IF [#20103 == 90 && #50007==1] THEN GOTO 40 ; normal 3-axis mode
IF [#20103 != 90 && #50007==0] THEN GOTO 50 ; normal 2-axis mode
GOTO 1000 ; should never get here, but if we do, skip everything else
N20
; we will never run this case as ballnut unclamped is handled in the PLC
M93/Z
M200 "Clamp quill ballnut and retry home"
GOTO 1000
N30
M200 "Enable Z axis [F1/F5] and retry home."
GOTO 1000
N40
; if Z homing backoff distance (in G91 line) is altered,
; must change \cncm\system\plcmacro9.mac to match
M92/Z
G91 G1 G20 Z0.110 F[#20203]
M26/Z
N50
M91/X
G91 G1 G20 X-0.060 F[#20201]
M26/X
M92/Y
G91 G1 G20 Y0.100 F[#20202]
M26/Y
IF [#20104 == 77 || #20104 == 78] GOTO 1000 ; "M" or "N" - no fourth axis control
M92/$[#20104] ; use whatever the 4th axis label is
G91 G20 G1 $[#20104]30.596 F[#20204]
M26/$[#20104]
N1000
If you set Parameter 131 appropriately (e.g. to 21, for a fourth axis labeled 'B') then you can just leave unconditional B axis commands in your homing macro.
There is then no need for a detection input. You do have to press the F6 key on the Setup menu when you want to turn the axis on and off.
The reason Tom's file needs the IF/GOTO using variable #20104, is the G1 move in between the M92 and the M26. If it just had "M92/B" followed by "M26/B", then the IF/GOTO would not be necessary.
Marc is correct. I have the G1 move so the rotary home is set with the t-slot horizontal as B=0°(it's the CDO I have).
Ok.
I’ll have to look up these # variables to see what they are for it to make any sense.
Thanks guy’s
Thanks guy’s
Does B then get homed after the axis is selected via the F6 key?cncsnw wrote: ↑Mon Dec 06, 2021 7:38 pm If you set Parameter 131 appropriately (e.g. to 21, for a fourth axis labeled 'B') then you can just leave unconditional B axis commands in your homing macro.
I have the home commands in my home program now and when the 4th is not connected and enabled it displays an error after homing the other 3 axis. Does not seem to hurt anything just annoying.
Setting Parameter 131 will prevent the error message when homing in 3-axis mode, because the parameter value tells the control that B is one of your axis labels; just not of one that is currently in use.
If you home the machine in 3-axis mode, then use F6 to switch to 4-axis mode, you will be prompted to press Cycle Start to find home (again). When you press Cycle Start, it will run cncm.hom again, which will presumably home all four axes.
