Prototrak DPM
nlmarcoux
CNC Control System Serial Number: m400 serial #103306 , cnc 11-d mill v 3.16 ID 05231983
Prototrak DPM
Post by nlmarcoux »
Looking for help on Allin1DC install . The z axis #3 motor will not turn , the x an y axis work find , encoders on all 3 work . I get a sv stall error when I try to jog the z axis #3 . The fuse on z axis #3 is good , when I switch z axis motor leads from #3 on AllinDC to #2 on the the board , the axis can be joged the head of machine will move . I purchased a used AllinDC system w / 2 centroid servo motors from a machine dealer , z axis motor is new from centroid , Thanks Louis
report_0523181983_2021-07-18_10-23-17.zip
(156.22 KiB) Downloaded 80 times
polaraligned
Re: Prototrak DPM
Post by polaraligned »
Your error log shows:
1) 07-18-2021 9:15:49 412 Z axis(3) encoder differential error
(1) 07-18-2021 9:15:49 SV_STALL ERROR Reported by CNC11!!!
(4) 07-18-2021 9:15:49 2099 Message Cleared
(1) 07-18-2021 9:18:37 SV_STALL ERROR Reported by CNC11!!!
(1) 07-18-2021 10:14:17 Creating report...
(1) 07-18-2021 10:14:18 Saved report to C:\cncm\reportbackup\report_0523181983_2021-07-18_10-14-16.zip
(1) 07-18-2021 10:14:31 204 Exiting CNC...Normal Exit (66)
(1) 07-18-2021 10:17:59 199 CNC Started
(1) 07-18-2021 10:17:59 CNC11-D Mill v3.16
(4) 07-18-2021 10:18:04 2099 Message Cleared
(1) 07-18-2021 10:18:05 412 Z axis(3) encoder differential error
(1) 07-18-2021 10:18:05 SV_STALL ERROR Reported by CNC11!!!
(4) 07-18-2021 10:18:06 9039 Software Ready Fault
(1) 07-18-2021 10:18:06 SV_STALL ERROR Reported by CNC11!!!
(1) 07-18-2021 10:18:33 204 Exiting CNC...Normal Exit (66)
(1) 07-18-2021 10:22:29 199 CNC Started
(1) 07-18-2021 10:22:29 CNC11-D Mill v3.16
(4) 07-18-2021 10:22:34 9039 Software Ready Fault
(1) 07-18-2021 10:22:34 412 Z axis(3) encoder differential error
(1) 07-18-2021 10:22:34 SV_STALL ERROR Reported by CNC11!!!
(4) 07-18-2021 10:22:35 9039 Software Ready Fault
(1) 07-18-2021 10:22:35 SV_STALL ERROR Reported by CNC11!!!
(1) 07-18-2021 10:23:17 Creating report...
The Software Ready Fault indicates a problem with the PLC communicating with the CNC11 software. This is probably causing the Stall Error.
Why your other axis's work and the Z doesn't, I don't know. You indicated that this Z motor and encoder combo work fine when swapped to another axis. This would eliminate the motor/encoder for that Z axis as a source of the problem.
Your Z motor/encoder doesn't show any differential encoder errors when you swapped the axis?
I will let others who have more knowledge advise you. In the mean time, maybe try a new ethernet cable to try to clear up the Software Ready Fault.
nlmarcoux
Re: Prototrak DPM
Post by nlmarcoux »
Updated file , this started when Allin1DC was fairly new , Thanks LOUIS
msg_log.txt
2018 FILES
(29.4 KiB) Downloaded 76 times
Re: Prototrak DPM
Set Parameter 302 to a value of 3.
If you are going to exit CNC11 (F10 -> F9) or you are going to shut down the computer (F10 -> F2), make a habit of pressing Emergency Stop before you do so. When you start back up, wait until the CNC11 screen is up before you release Emergency Stop. This will eliminate any extraneous "9039 Software ready fault" messages, so you will know whether there really are communication issues.
Use the PID Configuration -> Encoder menu to view encoder connection status, and see whether any given axis encoder is showing a differential error. You can clear previously-detected errors by pressing and releasing Emergency Stop.
nlmarcoux
Re: Prototrak DPM
Post by nlmarcoux »
Set Parameter 302 to a value of 3 , Z axis can jog motor , 302 was set to zero , this error goes back to 2018 on my msg _log.text file , Thanks for your help
Re: Prototrak DPM
This control was evidently set up previously, to run just two axes.
You will also need to edit your "cncm.hom" file, to include "M92/Z" and "M26/Z" instead of "M26/@".
Re: Prototrak DPM
Follow the All in One DC Installation Manual https://www.centroidcnc.com/downloads/c ... manual.pdf
I also have a video series on All in One DC, search Martyscncgarage on YouTube, might be helpful.
Marc Leonard (cncsnw, website: www. cncsnw.com) is as sharp as they come with years of experience and helped write the PLC
So if you get stuck with something not covered in the installation guide or questions about something in the guide, continue to post here. Always post a fresh report, not pieces of it. The machine parameters and logs are in the report.
Continued luck on the project.