All In One bench test
- CNC Control System Serial Number: A900779
Re: All In One bench test
Never Say Die! I got into it, I'm going to finish it.
Bridgeport V2XT, All In One DC #A900779. Using existing SEM motors 112 Volt. Spindle to be controlled by Lenze AC Tech VFD mod #ESV222N02YXB. Machine is being run on 208 3Phase power.
Well it’s time for round 12. Fixed all my fault problems. Got 24Vdc at all my limits, O at lube fault, 24Vdc at my spindle fault and 24Vdc at Emergency stop. And still no power coming out of H6 #1 out to my emergency contactor. Got 24Vac coming in to H6 #1 but not out. I even checked the fuses on the board. When the program powers up you here it pull in for a second then releases. Does anyone here have a clue of what could be wrong? Is there something in the parameters that could be turned off that could be causing this? Bob L
Please post a fresh report so we can get a look at your logs. Also a screen shot of your diagnostic screen. Alt IBeagle Beagle wrote: ↑Thu Mar 04, 2021 3:23 pm Well it’s time for round 12. Fixed all my fault problems. Got 24Vdc at all my limits, O at lube fault, 24Vdc at my spindle fault and 24Vdc at Emergency stop. And still no power coming out of H6 #1 out to my emergency contactor. Got 24Vac coming in to H6 #1 but not out. I even checked the fuses on the board. When the program powers up you here it pull in for a second then releases. Does anyone here have a clue of what could be wrong? Is there something in the parameters that could be turned off that could be causing this? Bob L
Can you tell us what this means?Got 24Vdc at all my limits, O at lube fault, 24Vdc at my spindle fault and 24Vdc at Emergency stop.
When you measure voltage at a PLC input, where are you putting the other test probe?
Report. How do you do a screen shot of the diagnostic screen?
- cnc_backup_0925192286_2021-03-04_14-39-19.zip
- (371.62 KiB) Downloaded 93 times
My limits are not tripped shouldn't you have 24Vdc at H10 1 though 6? Spindle fault is NC=24Vdc at terminal10? Emergency switch NC=24Vdc at termial11. Lube fault NC=o at terminal #9.
Screen shot. Screw this cnc stuff. With the education I'm getting here I going to manufacture my own line of voting machines. As long as the party that hires me wins, I can't loss!
You didn't run a report.
Please press F7 Utilities
F7 Create report and upload that file that is created. It should be in the C:\CNCM\REPORTBACKUP directory
Your display shows a SPINDLE FAULT. With a spindle fault the Estop contactor will open. Do you have a VFD connected yet? Did you wire the correct Fault output terminals?
Invert the input with Spindle Fault as a test....
Marty, yes I have the VFD connected. I have 24Vdc at the spindle fault terminal meaning it is NC but I'll check it again. I followed the earlier directions for creating a report. I'll try again in the morning.
I don't think you have the correct terminals on the VFD connected. It should ground the input when the VFD is OK. You should have a GREEN LED on in the input on the diagnostics pageBeagle Beagle wrote: ↑Thu Mar 04, 2021 8:43 pm Marty, yes I have the VFD connected. I have 24Vdc at the spindle fault terminal meaning it is NC but I'll check it again. I followed the earlier directions for creating a report. I'll try again in the morning.
