Re: Still struggling to get hand wheels operational.

Posted: Mon Feb 22, 2021 2:37 pm
by AcornJosh
What's the PLC have to do with handwheels. It should just be parameters. Do you see the handwheel encoder counts in the PID menu?
I think the PLC is just for the Joy stick inputs that are on the Centroid handwheels.

Re: Still struggling to get hand wheels operational.

Posted: Mon Feb 22, 2021 3:16 pm
by cncsnw
If the PLC program does not set SV_MPG_1_ENABLED, SV_MPG_2_ENABLED, SV_MPG_1_AXIS_SELECT, SV_MPG_2_AXIS_SELECT, SV_MPG_1_MULTIPLIER and SV_MPG_2_MULTIPLIER appropriately, then the handwheels will not work.

Re: Still struggling to get hand wheels operational.

Posted: Tue Feb 23, 2021 4:00 pm
by AcornJosh
That makes sense now that you mention it. Thank you.