Omnitec Selex Pal retrofit

Post by repauli1 »

Just starting an OmniTech router retrofit. Features include 8 tool rotary tool changer, 9 drill vblack, 10hp 24k rpm spindle, 3 hp vdrill. Vacumn holddown, toolsetter, handheld pendant with 10 pushbutton control, and MPG.
Using Centroid Oak, three ADD1616, DMM DYN4 servos 1.8KW 130mm frame size. Will document challenges as I go.
Attachments
20210103_150737.jpg
20210107_113426.jpg
20200821_082707.jpg
20210126_144224.jpg
20210123_115752.jpg
martyscncgarage
Posts: 9912
Joined: Tue Mar 28, 2017 12:01 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Mesa, AZ

Re: Omnitec Selex Pal retrofit

Post by martyscncgarage »

That will be a very interesting build....
Do keep us posted.
Thank you!
Marty
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
repauli1
Posts: 156
Joined: Thu Jul 09, 2020 9:50 pm
Acorn CNC Controller: No
Allin1DC CNC Controller: No
Oak CNC controller: Yes
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Omnitec Selex Pal retrofit

Post by repauli1 »

More pics
Attachments
20210107_113513.jpg
20210118_145245.jpg
20210103_150809.jpg
martyscncgarage
Posts: 9912
Joined: Tue Mar 28, 2017 12:01 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Mesa, AZ

Re: Omnitec Selex Pal retrofit

Post by martyscncgarage »

Two things I learned. Definitely use a Line reactor for the DYN4 drives. One large enough to handle all 4 is OK.
If you don't have a counter balance on the Z, use a regenerative resistor on the drive. I ran into this when I recently did a FADAL TRM retrofit. Both solved an alarm I was getting.
Stephen at DMM is pretty knowledgeable and helpful when it comes to this.
I assume you purchased the Oak to DMM Data cables from DMM? Worth every penny....

Best if luck in the build!
Marty
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
repauli1
Posts: 156
Joined: Thu Jul 09, 2020 9:50 pm
Acorn CNC Controller: No
Allin1DC CNC Controller: No
Oak CNC controller: Yes
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Omnitec Selex Pal retrofit

Post by repauli1 »

I will order the line reactors, I already have the 8 filters. My router has a ratcheting type pneumatic brake for Z axis, so are you saying DMM are sensitive to heavy z lifting at initial movement? Counter balance piston may be tricky to mount..humm thanks for feedback.
martyscncgarage
Posts: 9912
Joined: Tue Mar 28, 2017 12:01 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Mesa, AZ

Re: Omnitec Selex Pal retrofit

Post by martyscncgarage »

repauli1 wrote: Mon Feb 01, 2021 10:08 am I will order the line reactors, I already have the 8 filters. My router has a ratcheting type pneumatic brake for Z axis, so are you saying DMM are sensitive to heavy z lifting at initial movement? Counter balance piston may be tricky to mount..humm thanks for feedback.
ONE large line reactor is OK
You may not need the regen resistor. You can add it later if needed. The drive can always accept it.
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
cncsnw
Posts: 3763
Joined: Wed Mar 24, 2010 5:48 pm

Re: Omnitec Selex Pal retrofit

Post by cncsnw »

Before you get too far along, you might want to consider installing a larger electrical cabinet.

You want to be able to easily see and reach all your connection terminals. Having components layered on top of other components, or components on the side walls and floor overlapping components on the back panel, will make installation, service, and troubleshooting unnecessarily difficult.

If possible, you want to allow 1-1/2" or 2" between components and the wire duct that serves them. That makes terminal access easier, and makes the wire routing neater since wires do not have to leave a terminal and immediately make a sharp bend just to get to the nearest slot in the wire duct.
repauli1
Posts: 156
Joined: Thu Jul 09, 2020 9:50 pm
Acorn CNC Controller: No
Allin1DC CNC Controller: No
Oak CNC controller: Yes
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Omnitec Selex Pal retrofit

Post by repauli1 »

Thanks, I owned a ul508a panel shop/automation business for many years.. I hear your thoughts
repauli1
Posts: 156
Joined: Thu Jul 09, 2020 9:50 pm
Acorn CNC Controller: No
Allin1DC CNC Controller: No
Oak CNC controller: Yes
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Omnitec Selex Pal retrofit

Post by repauli1 »

Progress report, installed Z Axis servo today, milled, drilled, rigid tapped mounting plates for EMC/EMI filters. They do have a terminal for a neutral, and the machine does not have a neutral. Need to contact tech support and find out if it can be omitted. Anyone know?
Attachments
20210202_165126.jpg
ashesman
Posts: 395
Joined: Thu Dec 03, 2020 4:54 am
Acorn CNC Controller: No
Allin1DC CNC Controller: No
Oak CNC controller: Yes
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Omnitec Selex Pal retrofit

Post by ashesman »

Is it a neutral or earth terminal? Sometimes they provide an earth for conducting away stray current induced into the core.

If it has a pair of neutral wires in/out there should be no reason they need to be connected I wouldn't think. They should probably be insulated to ensure they cant be touched as may possibly have some voltage induced on them. A line reactor is essentially a big common mode choke. Really important that it has balanced current in it. I.e. Don't feed some part from two different line reactors. The exact current that enters the line reactor must exit through it for it to be effective.

Your install works looks really good. Looks like it will be a pretty capable and grunty machine!