The Centroid documentation does not give specs (e.g. max amps) for the "Logic Power Supply" used by Oak. Can you please tell me the max amps so I can protect Oak with a supplementary breaker. If a breaker is unnecessary because of protections built in to the power supply, it would be good to know that too.
Thank you.
JT
Supplementary Breaker for Oak
Moderator: cnckeith
-
- Posts: 3098
- Joined: Tue Mar 22, 2016 10:03 am
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: Yes
- CNC Control System Serial Number: 100505
100327
102696
103432
7804732B977B-0624192192 - DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Boston, MA
- Contact:
Re: Supplementary Breaker for Oak
Meanwell RQ65-D is the power supply that came with mine. There is an internal fuse, but it's not user replaceable.
- Attachments
-
- MeanWell RQ-65 Power Supply.pdf
- (106.21 KiB) Downloaded 113 times
Cheers,
Tom
Confidence is the feeling you have before you fully understand the situation.
I have CDO. It's like OCD, but the letters are where they should be.
Tom
Confidence is the feeling you have before you fully understand the situation.
I have CDO. It's like OCD, but the letters are where they should be.
-
- Posts: 9914
- Joined: Tue Mar 28, 2017 12:01 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Location: Mesa, AZ
Re: Supplementary Breaker for Oak
Power up the logic supply while connected to OAK, and measure its current. Use properly sized fuse(s). It doesn't draw that much. If you use a breaker, make sure it is sized appropriately and is of the proper type. I tend to stick with commonly available AGC glass fuses. I also use standard readily available cartridge fuses on my incoming power after the rotary disconnect switch. But that's me.jtcrew wrote: ↑Mon Nov 02, 2020 10:26 am The Centroid documentation does not give specs (e.g. max amps) for the "Logic Power Supply" used by Oak. Can you please tell me the max amps so I can protect Oak with a supplementary breaker. If a breaker is unnecessary because of protections built in to the power supply, it would be good to know that too.
Thank you.
JT
I don't generally fuse the logic power supply because most of my controls are relatively small. If the control side is fused with 10A fuses, I use 16 gauge for everything downstream of the fuses. If the main fuses are 15A then I would use 14 gauge down stream of them. I use a separate set of main fuses to power the VFD.
I also tend to follow the Centroid provided schematics if the build is pretty typical.
Marty
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
We can't "SEE" what you see...
Mesa, AZ
-
- Posts: 2
- Joined: Wed Oct 28, 2020 2:21 am
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Re: Supplementary Breaker for Oak
Thank you guys for your responses! Much appreciated.
JT
JT