Is there a system ready output on GPIO4D boards

All things related to Centroid Oak, Allin1DC, MPU11 and Legacy products

Moderator: cnckeith

Post Reply
SShep71
Posts: 8
Joined: Fri Apr 01, 2016 1:07 pm
Allin1DC CNC Controller: Yes
CNC Control System Serial Number: none
DC3IOB: No
CNC11: Yes
CPU10 or CPU7: No

Is there a system ready output on GPIO4D boards

Post by SShep71 »

The spindle amp I am using Mitsubishi MDS-A-SPJA-75RT requires a system ready signal to enable operation. Does the GPOI4D board have an output signal for "system ready" status?
tblough
Posts: 3089
Joined: Tue Mar 22, 2016 10:03 am
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: Yes
CNC Control System Serial Number: 100505
100327
102696
103432
7804732B977B-0624192192
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Boston, MA
Contact:

Re: Is there a system ready output on GPIO4D boards

Post by tblough »

NoFaultOut should be output 1; check your PLC source to verify. As the name says, Centroid enables this relay output when there are no faults present and the control is ready.

This output is part of the e-stop circuit. Depending on how the spindle input is configured, you might be able to wire the spindle in series with the e-stop circuit, or add an external contact to the e-stop relay.

There should also be a spindle enable signal on output 7. Tefer to your system schematic to see jow this is connected.
Cheers,

Tom
Confidence is the feeling you have before you fully understand the situation.
I have CDO. It's like OCD, but the letters are where they should be.
cncsnw
Posts: 3826
Joined: Wed Mar 24, 2010 5:48 pm

Re: Is there a system ready output on GPIO4D boards

Post by cncsnw »

Since you will already be using the "NoFaultOut" output to control the coil of your emergency stop contactor, it will make more sense to wire the "system ready" signal for your spindle drive through an auxiliary contact of the emergency stop contactor.

If you cannot find an additional contact on your emergency stop contactor, and you have surplus PLC outputs, you could define an additional PLC output to be a duplicate copy of NoFaultOut.