Re: Actualizacion EMCO VCM 300

Post by ashesman »

Chapter 14 of the manual lists a lot of causes for over volt and over current faults during deceleration. Have you reviewed them?

05-05 is a base motor parameter. It tells the VFD how much current the motor draws when unloaded. It should be set by auto tuning. Or manually by running the motor with no load and watching the current.

No load current is used by the slip compensation algorithm to know when it should do slip compensation or not.

I suspect that changing 05-05 has probably masked the problem rather than fixed it.

There is mention in the faults section of the manual of the stall prevention setting being lower than no load current causing faults.

Setting the base motor parameters correctly and then adjusting the other features to suit would be best.


Oscar6
Posts: 91
Joined: Thu Jun 24, 2021 1:55 pm
Acorn CNC Controller: No
Allin1DC CNC Controller: No
Oak CNC controller: Yes
CNC Control System Serial Number: A901029
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Actualizacion EMCO VCM 300

Post by Oscar6 »

ashesman wrote: Mon May 06, 2024 6:49 pm Chapter 14 of the manual lists a lot of causes for over volt and over current faults during deceleration. Have you reviewed them?

05-05 is a base motor parameter. It tells the VFD how much current the motor draws when unloaded. It should be set by auto tuning. Or manually by running the motor with no load and watching the current.

No load current is used by the slip compensation algorithm to know when it should do slip compensation or not.

I suspect that changing 05-05 has probably masked the problem rather than fixed it.

There is mention in the faults section of the manual of the stall prevention setting being lower than no load current causing faults.

Setting the base motor parameters correctly and then adjusting the other features to suit would be best.
Ok, I understand you, so what parameters do I have to configure for blocking prevention, I don't know what parameters you are referring to. Could you tell me the number of the blocking prevention parameter.


ashesman
Posts: 431
Joined: Thu Dec 03, 2020 4:54 am
Acorn CNC Controller: No
Allin1DC CNC Controller: No
Oak CNC controller: Yes
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Actualizacion EMCO VCM 300

Post by ashesman »

I think you should make sure the motor parameters are set correctly. Then start reading all the items on the page in the manual that explains the exact fault you are getting. It will list all the reasons that fault can occur.

But, if you are happy with the motors performance, then maybe it's time to move on to working on other parts of your setup.


Oscar6
Posts: 91
Joined: Thu Jun 24, 2021 1:55 pm
Acorn CNC Controller: No
Allin1DC CNC Controller: No
Oak CNC controller: Yes
CNC Control System Serial Number: A901029
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Actualizacion EMCO VCM 300

Post by Oscar6 »

Hello again, I have been looking a little through the forum about palpation probes, and it is not clear to me if I can connect a universal probe, I have obtained a Renishaw mi8 board that inverts the probe signal, but I do not know how to connect it There is a connector on the Oak board for this but the documentation only refers to centroid probes. Something could be done.
Attachments
Data sheet_ MI 8 interface unit.pdf
(86.69 KiB) Downloaded 3 times


cncsnw
Community Expert
Posts: 4458
Joined: Wed Mar 24, 2010 5:48 pm

Re: Actualizacion EMCO VCM 300

Post by cncsnw »

Yes, you can connect a probe via the MI8 interface to the Centroid control.

If you want to use the "PROBE" header on the Oak, then you would wire the B6 and B7 terminals to pins 3 and 8 of the Oak PROBE header.

If you want to use ordinary PLC inputs (e.g. any of INP13-INP16 on the Oak) then you would wire the B6 and B7 terminals to the Oak input, and to your inputs common voltage (e.g. 0VDC, if you have +24V wired to the bank common.

In either case, you will need to wire a 24VDC supply directly from your distribution terminals to MI8 terminals A5 and A6. There is no 24V supply pin on the Oak PROBE header; only 12V, which is not sufficient for the MI8.

I do not immediately see a way to automatically detect whether the probe is connected or not, separate from the N.C. trip signal.

For best protection against operator error, you want a separate normally-open input signal, wired to another input, which closes when the probe is connected. If you have such an input signal, and you set the input number in Parameter 18, then CNC12 will prevent you from trying to run a probing cycle without first connecting the probe; and your PLC program will prevent you from starting the spindle with the probe connected.

Also, if your probe-trip input is going to indicate a trip state when the probe is disconnected, then you need to either provide a probe-detect signal and set Parameter 18; or you need to leave the probe connected at all times.

If there is no way, through the MI8 interface or the probe itself, to automatically detect whether the probe is connected; but you still want the benefits of a probe-detect signal, then you can build a probe storage cradle with a normally-closed limit switch in it, so that the switch is tripped (open) when the probe is placed in storage. The control can then assume that if the probe is not in its storage cradle, then it is in the spindle.


Oscar6
Posts: 91
Joined: Thu Jun 24, 2021 1:55 pm
Acorn CNC Controller: No
Allin1DC CNC Controller: No
Oak CNC controller: Yes
CNC Control System Serial Number: A901029
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Actualizacion EMCO VCM 300

Post by Oscar6 »

cncsnw wrote: Sat Jul 13, 2024 8:19 pm Yes, you can connect a probe via the MI8 interface to the Centroid control.

If you want to use the "PROBE" header on the Oak, then you would wire the B6 and B7 terminals to pins 3 and 8 of the Oak PROBE header.

If you want to use ordinary PLC inputs (e.g. any of INP13-INP16 on the Oak) then you would wire the B6 and B7 terminals to the Oak input, and to your inputs common voltage (e.g. 0VDC, if you have +24V wired to the bank common.

In either case, you will need to wire a 24VDC supply directly from your distribution terminals to MI8 terminals A5 and A6. There is no 24V supply pin on the Oak PROBE header; only 12V, which is not sufficient for the MI8.

I do not immediately see a way to automatically detect whether the probe is connected or not, separate from the N.C. trip signal.

For best protection against operator error, you want a separate normally-open input signal, wired to another input, which closes when the probe is connected. If you have such an input signal, and you set the input number in Parameter 18, then CNC12 will prevent you from trying to run a probing cycle without first connecting the probe; and your PLC program will prevent you from starting the spindle with the probe connected.

Also, if your probe-trip input is going to indicate a trip state when the probe is disconnected, then you need to either provide a probe-detect signal and set Parameter 18; or you need to leave the probe connected at all times.

If there is no way, through the MI8 interface or the probe itself, to automatically detect whether the probe is connected; but you still want the benefits of a probe-detect signal, then you can build a probe storage cradle with a normally-closed limit switch in it, so that the switch is tripped (open) when the probe is placed in storage. The control can then assume that if the probe is not in its storage cradle, then it is in the spindle.
Thanks for the quick response, then I will connect it as you tell me to the oak probe connector, I will do the probe detection with a jumper on the same probe and when I connect the cable to use it it will already be activated, what pins of the oak probe connector do I have to bridging. I think I have to configure several parameters for it to work, in the documentation of the centroid probes it mentions something about that.


cncsnw
Community Expert
Posts: 4458
Joined: Wed Mar 24, 2010 5:48 pm

Re: Actualizacion EMCO VCM 300

Post by cncsnw »

For the probe-detect signal, connect pin 2 or 3 (the 12V COM) to pin 9 (INP771) of the Oak PROBE header.

With the probe-trip signal on pin 8 (INP769) and the probe-detect signal on pin 9 (INP771), you would set:
- Parameter 11 = 50769
- Parameter 18 = 50771
Those are the default values for those parameters.

If your probe-trip signal is normally-closed (closed/green when not tripped; open/red when tripped) then make Parameter 11 negative. I.e. set it to -50769 instead of +50769.


Oscar6
Posts: 91
Joined: Thu Jun 24, 2021 1:55 pm
Acorn CNC Controller: No
Allin1DC CNC Controller: No
Oak CNC controller: Yes
CNC Control System Serial Number: A901029
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Actualizacion EMCO VCM 300

Post by Oscar6 »

cncsnw wrote: Sun Jul 14, 2024 2:33 pm For the probe-detect signal, connect pin 2 or 3 (the 12V COM) to pin 9 (INP771) of the Oak PROBE header.

With the probe-trip signal on pin 8 (INP769) and the probe-detect signal on pin 9 (INP771), you would set:
- Parameter 11 = 50769
- Parameter 18 = 50771
Those are the default values for those parameters.

If your probe-trip signal is normally-closed (closed/green when not tripped; open/red when tripped) then make Parameter 11 negative. I.e. set it to -50769 instead of +50769.
Ok, I'll try what it tells me, the mi8 interface lets me configure normally open or normally closed, oak wants normally open and when there is a normally closed trip.


Oscar6
Posts: 91
Joined: Thu Jun 24, 2021 1:55 pm
Acorn CNC Controller: No
Allin1DC CNC Controller: No
Oak CNC controller: Yes
CNC Control System Serial Number: A901029
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Actualizacion EMCO VCM 300

Post by Oscar6 »

Hello, today I connected the probe and it works correctly, the only problem is that when I disconnect the probe cable, detection pins and open probe pins, the control gives a probe error and does not let me change the tool, To make the change I have to leave the cable connected, I don't understand if when I disconnect the cable the detection pins open there shouldn't be a problem, I don't know if I have some wrong parameter.


cncsnw
Community Expert
Posts: 4458
Joined: Wed Mar 24, 2010 5:48 pm

Re: Actualizacion EMCO VCM 300

Post by cncsnw »

What was the error number and message?


Post Reply