M10 and M11 work via mdi. Now I want to activate M10 via Aux1 of the jog panel. I tried with parameter 188 and value 1011, without success. Now I'm thinking about programming it in the PLC. I think something is still missing.
Aux1 for 4thAxis clamp plc
- CNC Control System Serial Number: A901313
Re: Aux1 for 4thAxis clamp plc
post a fresh report.zip so we can see your setup and plc program
are you using a VCP or hard panel?
macro programming manual is here, how to interact with an output is on page 13
and vcp programming manual is here, how to run a macro directly from a button is on page 39
I have programmed aux1 in the plc, when pressing aux1 the LED changes state but the output is not activated. I can switch the output with m10 via mdi. I also swapped the worklight with the clamp as a test, and the output for the worklight was then activated with aux1.
- report_0008DC111213-0324231447_2024-01-18_16-52-38.zip
- (719.84 KiB) Downloaded 119 times
How was the issue solved?
M10 is only allowed in mdi and in the run program. In standby, Aux1 now switches an additional relay and bridges the actual clamping relay. If you now start mdi or a program, this bridging relay will be deactivated again.
OK, thanks.
I was able to find a way to allow an M-code and a VCP button control the same output....
Unfortunately this results in the M-code and VCP button working independently of each other.
That is, an output can only be turn OFF by the method that turned it ON.
Ideally the ON or OFF would happen regardless which method was used, and the button LED would always reflect the output state.
If any expert PLC programmers know how to achieve this, please share
IF M38_SV || Aux1LED_O THEN (OUT4)
IF SkinAux1_M_SV THEN (Aux1PD_PD)
IF (Aux1PD_PD ^ Aux1LED_O) THEN (Aux1LED_O)
Using your PLC definitions, not mine:
IF M38_SV ^ Aux1PD_PD THEN (M38_SV), (Aux1LED_O), (OUT4)
Excellent!
Worked a treat.
Thanks for taking the time to share.
Worked a treat.
