Gentlemen,
My automation direct GS20 has an Analog output connected to the analog input of the Allin1.
When setting it up, for lack of better knowledge, I set it to be 0-10v = 0-100% output load.
Can the allin1 use this information? If not, what is the Analog input of the Allin1 Intended for?
What should I set the Automation direct analog output to represent?
I have included a report file
Thanks, Mike
Allin1 Analog input Function?
Moderator: cnckeith
-
- Posts: 57
- Joined: Wed Jan 06, 2021 1:05 pm
- Acorn CNC Controller: No
- Allin1DC CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: console 104030 SysId 0008DC111213-1202202505
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Mims Florida
Allin1 Analog input Function?
- Attachments
-
- report_0008DC111213-1202202505_2022-09-20_22-01-05.zip
- (1.75 MiB) Downloaded 7 times
Re: Allin1 Analog input Function?
1) Set Parameter 35 = 6, to make axis #6 refer to your spindle
2) Set Parameter 313 = 0, to indicate that there is no encoder for that axis
3) Set Parameter 57 = 32, to request a PLC-driven load meter for axis #6
4) Set Parameter 990 = 10.0, to indicate that full-scale load is 10VDC
I usually configure the drive to show output current (P03.20 = 3).
2) Set Parameter 313 = 0, to indicate that there is no encoder for that axis
3) Set Parameter 57 = 32, to request a PLC-driven load meter for axis #6
4) Set Parameter 990 = 10.0, to indicate that full-scale load is 10VDC
I usually configure the drive to show output current (P03.20 = 3).