VFD Voltage/RPM fluctuating
Posted: Fri Feb 05, 2021 3:02 am
Hi all,
I am bench testing my Acorn board and have been succesful for the most part.
I have completed bench/comms test - no issues.
I have completed spindle output bench test - voltage steady and within +/- 5%
I am using a Fuling (chinese) 5.5kw VFD and an Air cooled 4.5Kw spindle - Max speed 18,000rpm, Max frequency 300hz.
Report is attached.
Power supply for Acorn and VFD are on separate circuits, both with filters on the AC inlets
I currently have it wired so Acorn Output 8 is set to 'VFD Enable', this is wired to the 'Enable' pin on the VFD, which puts it in RUN mode when active.
I am then using the +/-10V control from the Acorn to control the spindle speed. This works perfectly, until I drop below about 12500rpm spindle speed/220hz on vfd/7.2V on spindle output from Acorn - The spindle speed will fluctuate up and down about 500rpm.
I'm sending a simple 'M3 Sxxxxx' in the MDI to control speed
When I put a voltmeter on the +/-10V spindle speed supply, the voltage is fluctuating with the speed change in the spindle, indicating that the VFD is just doing what It's told.
With spindle power supply disconnected, the voltage remains steady on the spindle control voltage at all speeds - indicating it may be interference from the VFD
I then tried putting a jumper across the 'Enable' pins on the VFD, and disconnected the 'VFD enable' wiring. The issue disappeared and spindle rpm & control voltage was very steady at all speeds - this narrows it down to something happening when the Output 8 relay is used to close the 'VFD Enable' pins. The speed control is exactly as one would expect
I have also tried Output 1 on the Acorn with no change
Not sure quite where to go from here, I need something to send the VFD a spindle enable to use the VFD properly, but can't/won't run it with such a speed fluctuation
I have also attached a photo of my wiring layout - I am very aware that there are no E-stops wired in, and that it's not tidy as yet.
Thank you,
Stuart
I am bench testing my Acorn board and have been succesful for the most part.
I have completed bench/comms test - no issues.
I have completed spindle output bench test - voltage steady and within +/- 5%
I am using a Fuling (chinese) 5.5kw VFD and an Air cooled 4.5Kw spindle - Max speed 18,000rpm, Max frequency 300hz.
Report is attached.
Power supply for Acorn and VFD are on separate circuits, both with filters on the AC inlets
I currently have it wired so Acorn Output 8 is set to 'VFD Enable', this is wired to the 'Enable' pin on the VFD, which puts it in RUN mode when active.
I am then using the +/-10V control from the Acorn to control the spindle speed. This works perfectly, until I drop below about 12500rpm spindle speed/220hz on vfd/7.2V on spindle output from Acorn - The spindle speed will fluctuate up and down about 500rpm.
I'm sending a simple 'M3 Sxxxxx' in the MDI to control speed
When I put a voltmeter on the +/-10V spindle speed supply, the voltage is fluctuating with the speed change in the spindle, indicating that the VFD is just doing what It's told.
With spindle power supply disconnected, the voltage remains steady on the spindle control voltage at all speeds - indicating it may be interference from the VFD
I then tried putting a jumper across the 'Enable' pins on the VFD, and disconnected the 'VFD enable' wiring. The issue disappeared and spindle rpm & control voltage was very steady at all speeds - this narrows it down to something happening when the Output 8 relay is used to close the 'VFD Enable' pins. The speed control is exactly as one would expect
I have also tried Output 1 on the Acorn with no change
Not sure quite where to go from here, I need something to send the VFD a spindle enable to use the VFD properly, but can't/won't run it with such a speed fluctuation
I have also attached a photo of my wiring layout - I am very aware that there are no E-stops wired in, and that it's not tidy as yet.
Thank you,
Stuart