Hello all,
I have a hitachi WJ200 VFD attached to my acorn
In essence, I have:
* Hitachi WJ200 VFD
* Motor, at 60hz is 1750RPM
* Acorn controller
* Shielded connection to VFD
VFD is setup:
* 120Hz max (via A004 and A012)
Centroid is programmed for:
* Min Speed: 80
* Max Speed: 3500
This is the problem, from centroid I get:
* Set to 1750 (50% of max speed), outputs 6.6v (on a multimeter) or 80Hz, expected output would be 5v generating 60Hz
* Set to 3500RPM (100% of max speed) outputs 10V (on a mulimeter), or 120Hz, the correct expected output
Is there some kind of curve with the spindle output that would be causing this?
MDI Spindle Voltage Incorrect
Re: MDI Spindle Voltage Incorrect
If you wish your analog voltage to be linear, set the wizard rpm minimum to zero. Then set your desired minimum speed in the VFD parameters (Htz Min)
Thanks for the reply – I set the minimum to 0 in centroid, and I get the same result.
E415F6F70BC3-0318203049
Disconnect wires from both Vout and COM analog terminals on Acorn and measure voltage on those terminals when manually commanding 1750 rpm. Does this produce 5vdc
Did you clean up wiring as we suggested in your other thread?
And PLEASE, post a new and current Report.zip
Hope this helps
Nigel
Nigel
Have you tried adding a 0.1mfd capacitor across the Acorn analog terminals?
morchips wrote: ↑Thu Feb 22, 2024 8:49 am Hello all,
In essence, I have:
* Hitachi WJ200 VFD
* Acorn controller
VFD is setup:
* Min Speed: 80
* Max Speed: 3500
disconnect the VFD from Acorn and go thru the Spindle Bench test starting on page 30