After a power cycle of the acorn board, when you start up the acorn app you get the "tick" sound of the drivers being taken over by Centroid. I can move things around and have been working on getting the settings to my liking, but when I hear that same "tick" sound, it's over. DRO shows movement but all drivers will not move a motor. I'm used to that tick when they lock in from several machines, but this is the first time I have run across the tick while in use and the drivers don't unlock, but they are not controlled anymore.
Drivers, actually sound pretty good and smooth when working and auto homing sequence is doing fine with proxy switches.
I get no error messages when the tick happens, but no movement will happen until the acorn board is cycled.
Pacific Scientific 6410 drivers. 5v logic with constant 5v to step/dir+ from power supply and step/dir - hooked to the db25
The Drives ran fine on the axyz system, but it was just outdated and used a serial cable for loading files.
I used leadshine dm setup, as they use the 5v+ and are set up the same.
I have played with different feed speeds and went from 100khz to 400khz with no change.
Sometimes when no movement at all is happening on the machine I hear the "tick" and again it's over for that power cycle.
I have run the stress test and zero issues. Ping test again has zero issues.
When the tick happens, I do not loose ethernet connection to the board.
Report attached, a few pics attached, Manual for the drive attached.
Thanks
Tick and then no more movement until power cycled (Resolved)
Moderator: cnckeith
-
- Posts: 352
- Joined: Wed Jan 23, 2019 4:19 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 80F5B5B92C3A-0213236854
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Tick and then no more movement until power cycled (Resolved)
- Attachments
-
- 6410_Hardware_Manual.pdf
- (1.45 MiB) Downloaded 6 times
-
- report_80F5B5B92C3A-0213236854_2023-03-18_13-50-04.zip
- (775.92 KiB) Downloaded 8 times
Last edited by Ken Rychlik on Tue Mar 28, 2023 12:17 pm, edited 1 time in total.
Ken
-
- Posts: 352
- Joined: Wed Jan 23, 2019 4:19 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 80F5B5B92C3A-0213236854
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Re: Tick and then no more movement until power cycled
WHEN the machine runs, it sounds and feels pretty good. Here is a quick video on youtube.
Ken
-
- Posts: 7292
- Joined: Wed Mar 03, 2010 4:23 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: Yes
- CNC Control System Serial Number: none
- DC3IOB: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Contact:
Re: Tick and then no more movement until power cycled
loose connection on VDC to Acorn?
Need support? READ THIS POST first. http://centroidcncforum.com/viewtopic.php?f=60&t=1043
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
-
- Posts: 2214
- Joined: Fri May 24, 2019 8:34 am
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 7804734C6498-0401191832
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Clearwater, FL
Re: Tick and then no more movement until power cycled
I think he has an incoming main power issue Keith and I believe the drives are faulting because of overvoltage. He does not have the drive fault lines hooked up so that's why Acorn does not trigger a fault, but hopefully I've managed to get him to rethink this and wire them up. Still troubleshooting.
-
- Posts: 7292
- Joined: Wed Mar 03, 2010 4:23 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: Yes
- CNC Control System Serial Number: none
- DC3IOB: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Contact:
Re: Tick and then no more movement until power cycled
cool. i was thinking this sounded like a power issue.ShawnM wrote: ↑Wed Mar 22, 2023 6:06 pm I think he has an incoming main power issue Keith and I believe the drives are faulting because of overvoltage. He does not have the drive fault lines hooked up so that's why Acorn does not trigger a fault, but hopefully I've managed to get him to rethink this and wire them up. Still troubleshooting.
Need support? READ THIS POST first. http://centroidcncforum.com/viewtopic.php?f=60&t=1043
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
-
- Posts: 352
- Joined: Wed Jan 23, 2019 4:19 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 80F5B5B92C3A-0213236854
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Re: Tick and then no more movement until power cycled
I still don't get how all 4 drives would fault at the same time, but I am watching a fault output while running it. Dang thing won't act up when I want it to.
Question. If DRO's are moving does that mean it is sending step/dir?
Drives list 75v max and the axyz board was set up at 80v to start with. The power supply is depending on incoming voltage and I am running right at 250v ac. Shawn thinks I'm hitting the max of the drives with voltage spikes when running. It does make sense, but having all 4 fault at the exact same time every time, seems unlikely.
Loose VDC to acorn seems like it would give a com error?
Thanks
Ken
Question. If DRO's are moving does that mean it is sending step/dir?
Drives list 75v max and the axyz board was set up at 80v to start with. The power supply is depending on incoming voltage and I am running right at 250v ac. Shawn thinks I'm hitting the max of the drives with voltage spikes when running. It does make sense, but having all 4 fault at the exact same time every time, seems unlikely.
Loose VDC to acorn seems like it would give a com error?
Thanks
Ken
Ken
-
- Posts: 2179
- Joined: Sat Nov 18, 2017 2:32 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: Acorn 238
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Marquette, MI
- Contact:
Re: Tick and then no more movement until power cycled
In reality it is very likely when running a toroidal transformer, as they are linear. If designed for 230vac and 80 volt output it will output 8.9% higher voltage or 86.96 vac. Don't know what you are using, but I have seen Leadshine drives show over volt alarm at 80.1 volts.but having all 4 fault at the exact same time every time, seems unlikely.
If they are Leadshine or clones, read the blink code
-
- Posts: 2214
- Joined: Fri May 24, 2019 8:34 am
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 7804734C6498-0401191832
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Clearwater, FL
Re: Tick and then no more movement until power cycled
Gary, they are Pacific Scientific 6410 drivers and the manual states between 24 and 75 volts. He is running a toroidal transformer and at times he was reading over 80 volts on the toroidal transformer at idle. They are "old school" drives with no led's. The manual states that the drives will fault for "bus overvoltage". When decelerating multiple drives at once they can easily push the 80 volts even higher and fault.
Looking at your report Ken, you do have some ethernet communication errors as well. You said you cleared the log since then so post another current report.
Looking at your report Ken, you do have some ethernet communication errors as well. You said you cleared the log since then so post another current report.
-
- Posts: 352
- Joined: Wed Jan 23, 2019 4:19 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 80F5B5B92C3A-0213236854
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Re: Tick and then no more movement until power cycled
I was fighting windows turning back on defender stuff by itself, and I think I have that corrected. There are lots of different pages and places it can take over. Those were squared away before the "tick" issue showed itself, as I was able to manually jog the machine around. I cleared it because I wanted to know what was happening after getting the pc more reliable.
Drive ok input is hooked up and working. (I think) I ran it in series through all drives. input pin (24v) to pin 4 and pin 9 to the next pin 4 ect.. with the final pin 9 going to gd. I really have no way of knowing it will trip other than signal is passing through them as it should normally. When a fault sneaks up, I will know for sure.
I am thinking a 60 or 72v ps but would like to see for sure what is happening first. Even if I change the drives, over 80v will be excessive.
Thanks
Ken
Drive ok input is hooked up and working. (I think) I ran it in series through all drives. input pin (24v) to pin 4 and pin 9 to the next pin 4 ect.. with the final pin 9 going to gd. I really have no way of knowing it will trip other than signal is passing through them as it should normally. When a fault sneaks up, I will know for sure.
I am thinking a 60 or 72v ps but would like to see for sure what is happening first. Even if I change the drives, over 80v will be excessive.
Thanks
Ken
Ken
-
- Posts: 352
- Joined: Wed Jan 23, 2019 4:19 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 80F5B5B92C3A-0213236854
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Re: Tick and then no more movement until power cycled
Ok, the Transformer was wired Orng/blk that is for 208v. I rewired it to wht/blk (240) and it brought down the output to the drivers to 69 vdc. I need to run it through it's paces, but it looks promising. I included a pic of the transformer tag.
Thanks to all
Ken
Thanks to all
Ken