My probe suddenly quit working. I verified the wiring, the inputs which I did not change but White goes to 6 and red to 7. Black is connected to a com port. Both of the lights are green on inputs 6 and 7. The probe connected, the probing cycle starts but the Probe light does not come on.
Any suggestions? Report attached.
Probe issues
Moderator: cnckeith
-
- Posts: 72
- Joined: Thu Jul 02, 2020 5:38 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Spring, Texas
- Contact:
Probe issues
- Attachments
-
- report_0C1C571289B6-0526203333_2022-08-24_08-29-41.zip
- (714.55 KiB) Downloaded 13 times
-
- Posts: 263
- Joined: Thu Apr 14, 2022 2:46 pm
- Acorn CNC Controller: No
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: No
- CNC11: No
- CPU10 or CPU7: No
Re: Probe issues
Is it a KP-3? On the KP-3 flying lead cable, white is the probe output and red is the detect output. According to your report, those are swapped.