Probe issues

All things related to the Centroid Acorn CNC Controller

Moderator: cnckeith

Post Reply
mcbr549
Posts: 72
Joined: Thu Jul 02, 2020 5:38 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Spring, Texas
Contact:

Probe issues

Post by mcbr549 »

My probe suddenly quit working. I verified the wiring, the inputs which I did not change but White goes to 6 and red to 7. Black is connected to a com port. Both of the lights are green on inputs 6 and 7. The probe connected, the probing cycle starts but the Probe light does not come on.

Any suggestions? Report attached.
Attachments
report_0C1C571289B6-0526203333_2022-08-24_08-29-41.zip
(714.55 KiB) Downloaded 13 times
centroid467
Posts: 263
Joined: Thu Apr 14, 2022 2:46 pm
Acorn CNC Controller: No
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: No
CNC11: No
CPU10 or CPU7: No

Re: Probe issues

Post by centroid467 »

Is it a KP-3? On the KP-3 flying lead cable, white is the probe output and red is the detect output. According to your report, those are swapped.
Post Reply