Post by Degen »

I have recently installed the ACORN CNC on a CT054 BusyBee Mill and am using a LENZE VFD for my 3 phase motor (upgrade). Unfortunately the generic VFD wiring diagrams do not fully work beccause they do not allow the VFD to turn off the motor because LENZE has a safety circuit and funny off switch so to speak. It must recieve a signal off. Since ACORN lacks DPDT relays on there relay board I have added to relays that are driven by the ACORN generic circuit which in turn switch the LENZE VFD taking advantage of both systems (no programming changes on the ACORN side.

When I have time I will post a drawing for those interested.

Speed control through the H8 connectors works well and attached to 2 (0-10VDC Com) and 5 (0-10VDC) on the LENZE Terminal Strip.
centroidsupport
Posts: 120
Joined: Tue Sep 28, 2021 6:26 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: Yes
CNC Control System Serial Number: none
DC3IOB: Yes
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes

Re: LENZE SMV VFD

Post by centroidsupport »

You should post a link to the manual for this inverter
Need support? READ THIS POST first. http://centroidcncforum.com/viewtopic.php?f=60&t=1043
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
https://www.centroidcnc.com/centroid_di ... _gear.html
firebrick43
Posts: 21
Joined: Sat Jan 08, 2022 10:16 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: LENZE SMV VFD

Post by firebrick43 »

Ac lenze drive are very good, i love mine. My guess is you are not setting Parameter P120, 121, 122, 123 correctly which controls how the start stop direction circuit works. 13 a b and c terminals on the drive are programable how they act by the previously mentioned parameters. And you do have your relay outputs to 1, 4, 13a, and 13b on the drive right?

See pages 33 and 34 of the ac lenze drive manual.
https://inverterdrive.com/file/Lenze-AC-Tech-SMV-Manual
Degen
Posts: 7
Joined: Fri Aug 13, 2021 10:48 am
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: E415F6F9923D-0617214845
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: LENZE SMV VFD

Post by Degen »

My manual is a little different

https://download.lenze.com/TD/ESV__SMV% ... -0__EN.pdf (this is the newest one).

Setting on mine include P100, P101, P112, P121, P123, P160, P161

Mine is wired as per drawing 2.1.2 setting page 67 (or 69 on pdf viewer) more or less.

No start button.
Stop is part of the circuit.
Speed pot is I believe 2 and 5 only directly to analog speed control

The Acorn relay outputs are wired to the relays (mine) in series on the coils to drive the required outputs on the VFD. One relay for FWD, one for REV.
This issue with Lenze is that it requires a dedicated stop. Spindle reset does not do this unless Emergency stop is pressed on the Acorn, regular rest does not. So the solution is a relay (for each direction) that has 2 NO/NC contacts (vs 1 on Acorn) is required and a little fancy wiring is required to send the correct signal to the VFD.

The advantage to doing this is that no special programming is required on ACORN and No special programming is required on the VFD. Fail safe condition shuts spindle down.

You are correct that revised "my" relay outputs drive 1,4, 13A and 13 C and Acorn relay output drives my relays.

I'll create a drawing that will give the correct wiring diagram for change.