Re: Wiring Confirmation
Posted: Wed Jan 19, 2022 11:41 am
by tuffduck
I am using singe phase power, so it looks like some wires need to be removed, I am guessing both the green and white wires?
Re: Wiring Confirmation
Posted: Wed Jan 19, 2022 12:06 pm
by ShawnM
Absolutely, the green chassis ground or PE wire doesn't do through the contactor. All grounds from all your components need to go direct to your buss bar in the bottom center of your panel . This frees up another NO contact on your contactor, terminal 5 & 6, to use for the C86 blah blah blah.
For single phase 120 or 240 power I run the white, neutral line through the contactor. Not everyone may do this.
Re: Wiring Confirmation
Posted: Wed Jan 19, 2022 12:15 pm
by martyscncgarage
120V or 240V?
120V only the hot needs to go through the contactor
240V both hots need to go through the contactor
In either case, it frees up a contact for you to use for C86ACCP No Fault
This is why we ask you for pictures. We can not "SEE" what you "SEE"
Thank you for posting the picture
Marty
Re: Wiring Confirmation
Posted: Wed Jan 19, 2022 6:29 pm
by tuffduck
Thanks Marty!
Re: Wiring Confirmation
Posted: Wed Jan 19, 2022 7:29 pm
by tuffduck
Re: Wiring Confirmation
Posted: Wed Jan 19, 2022 7:36 pm
by martyscncgarage
Re: Wiring Confirmation
Posted: Wed Jan 19, 2022 8:08 pm
by tuffduck
Thanks