Re: My Sherline chucker lathe & 5400 mill with Acorn control build
Posted: Mon Sep 20, 2021 3:01 pm
THANK YOU! For the videos!
In your videos, your machine needs to home to
Z+
Y+
X+
Your X soft limit is incorrect. It should be a NEGATIVE value
In the homing and travel screen, you need to change homing direction to a +M92 for Axis 1 (X)
You probably also have the X axis moving the wrong direction and need to change in the AXIS Configuration
Under X, change DIRECTION REVERSAL TO N
Mill:
X positive, the table moves to the LEFT
X negative, the table moves to the RIGHT
Y positive, the table moves toward you, away from the column
Y negative, the table moves away from you, toward the column
Z positive, the head moves UP
Z negative, the head moves DOWN
Lathe
Z negative, carriage moves TOWARD the headstock
Z positive, the carriage moves AWAY from the headstock
X negative, the cutter moves TOWARD the spindle centerline
X positive, the cutter moves AWAY from the spindle centerline
Please review this great post on Machine tool coordinate systems:
viewtopic.php?f=63&t=3648
Tell us EXACTLY how your Estop button is wired.
Simply put. Estop NC, one wire to Acorn COM and one wire to Input 8.
Your problem as previously stated by others, is that you are tripping the ESTOP when your home switches trip. That is not supposed to happen. The Estop trip halts the control.
As was also stated. Do not mix the two machines. Get one going first then worry about the other.
You also still have MANY PC/MPU Resends. This must be corrected. You have noise that must be fixed.
From your logs:
(4) 09-19-2021 18:51:50 946 PC resending # 3067
(4) 09-19-2021 18:51:50 944 MPU requested resend # 152
(4) 09-19-2021 18:51:50 946 PC resending # 3097
(4) 09-19-2021 18:51:50 944 MPU requested resend # 153
(4) 09-19-2021 18:51:50 946 PC resending # 3119
(4) 09-19-2021 18:51:50 946 PC resending # 3128
(4) 09-19-2021 18:51:50 944 MPU requested resend # 154
(4) 09-19-2021 18:51:50 946 PC resending # 3131
(1) 09-19-2021 18:51:50 406 Emergency stop detected
(4) 09-19-2021 18:52:18 944 MPU requested resend # 155
(4) 09-19-2021 18:52:18 946 PC resending # 3134
(4) 09-19-2021 18:52:19 944 MPU requested resend # 156
(4) 09-19-2021 18:52:19 946 PC resending # 3138
(4) 09-19-2021 18:52:19 944 MPU requested resend # 157
(4) 09-19-2021 18:52:19 946 PC resending # 3142
(4) 09-19-2021 18:52:19 944 MPU requested resend # 158
(4) 09-19-2021 18:52:19 946 PC resending # 3146
(4) 09-19-2021 18:52:19 944 MPU requested resend # 159
(4) 09-19-2021 18:52:19 946 PC resending # 3149
(4) 09-19-2021 18:52:19 944 MPU requested resend # 160
(4) 09-19-2021 18:52:19 946 PC resending # 3153
(4) 09-19-2021 18:52:19 944 MPU requested resend # 161
(4) 09-19-2021 18:52:19 946 PC resending # 3158
(4) 09-19-2021 18:52:19 944 MPU requested resend # 162
(4) 09-19-2021 18:52:19 946 PC resending # 3162
(4) 09-19-2021 18:52:20 944 MPU requested resend # 163
(4) 09-19-2021 18:52:20 946 PC resending # 3165
(4) 09-19-2021 18:52:20 944 MPU requested resend # 164
(4) 09-19-2021 18:52:20 946 PC resending # 3168
(4) 09-19-2021 18:52:20 944 MPU requested resend # 165
(4) 09-19-2021 18:52:20 944 MPU requested resend # 166
(4) 09-19-2021 18:52:20 946 PC resending # 3173
(4) 09-19-2021 18:52:20 946 PC resending # 3178
(4) 09-19-2021 18:52:20 944 MPU requested resend # 167
(4) 09-19-2021 18:52:20 946 PC resending # 3182
(4) 09-19-2021 18:52:20 944 MPU requested resend # 168
(4) 09-19-2021 18:52:20 946 PC resending # 3185
(4) 09-19-2021 18:52:21 944 MPU requested resend # 169
(4) 09-19-2021 18:52:21 946 PC resending # 3188
(4) 09-19-2021 18:52:21 944 MPU requested resend # 170
(4) 09-19-2021 18:52:21 946 PC resending # 3192
(4) 09-19-2021 18:52:22 944 MPU requested resend # 171
(4) 09-19-2021 18:52:22 944 MPU requested resend # 172
(4) 09-19-2021 18:52:22 946 PC resending # 3222
(4) 09-19-2021 18:52:22 944 MPU requested resend # 173
(4) 09-19-2021 18:52:22 946 PC resending # 3249
(4) 09-19-2021 18:52:22 944 MPU requested resend # 174
(4) 09-19-2021 18:52:22 946 PC resending # 3268
(4) 09-19-2021 18:52:22 946 PC resending # 3271
(4) 09-19-2021 18:52:22 946 PC resending # 3278
(4) 09-19-2021 18:52:24 944 MPU requested resend # 175
(4) 09-19-2021 18:52:24 946 PC resending # 3280
(4) 09-19-2021 18:52:24 944 MPU requested resend # 176
(4) 09-19-2021 18:52:24 946 PC resending # 3283
(4) 09-19-2021 18:52:24 944 MPU requested resend # 177
(4) 09-19-2021 18:52:24 946 PC resending # 3284
(4) 09-19-2021 18:52:24 946 PC resending # 3287
(4) 09-19-2021 18:52:24 944 MPU requested resend # 178
(4) 09-19-2021 18:52:24 946 PC resending # 3290
(4) 09-19-2021 18:52:25 944 MPU requested resend # 179
(4) 09-19-2021 18:52:25 946 PC resending # 3293
(4) 09-19-2021 18:52:25 944 MPU requested resend # 180
(4) 09-19-2021 18:52:25 946 PC resending # 3296
(4) 09-19-2021 18:52:30 944 MPU requested resend # 181
(4) 09-19-2021 18:52:30 946 PC resending # 3299
(4) 09-19-2021 18:52:31 944 MPU requested resend # 182
(4) 09-19-2021 18:52:31 946 PC resending # 3302
(4) 09-19-2021 18:52:31 944 MPU requested resend # 183
(4) 09-19-2021 18:52:31 946 PC resending # 3306
(4) 09-19-2021 18:52:32 944 MPU requested resend # 184
(4) 09-19-2021 18:52:32 944 MPU requested resend # 185
(4) 09-19-2021 18:52:32 946 PC resending # 3350
(4) 09-19-2021 18:52:32 944 MPU requested resend # 186
(4) 09-19-2021 18:52:32 946 PC resending # 3380
(4) 09-19-2021 18:52:32 944 MPU requested resend # 187
(4) 09-19-2021 18:52:32 946 PC resending # 3409
(4) 09-19-2021 18:52:32 944 MPU requested resend # 188
(4) 09-19-2021 18:52:32 946 PC resending # 3435
(4) 09-19-2021 18:52:32 944 MPU requested resend # 189
(4) 09-19-2021 18:52:32 946 PC resending # 3455
(4) 09-19-2021 18:52:32 946 PC resending # 3466
(4) 09-19-2021 18:52:34 944 MPU requested resend # 190
(4) 09-19-2021 18:52:34 944 MPU requested resend # 191
(4) 09-19-2021 18:52:34 946 PC resending # 3469
(4) 09-19-2021 18:52:34 946 PC resending # 3473
(4) 09-19-2021 18:52:35 944 MPU requested resend # 192
(4) 09-19-2021 18:52:35 946 PC resending # 3476
(4) 09-19-2021 18:52:36 944 MPU requested resend # 193
(4) 09-19-2021 18:52:36 946 PC resending # 3478
(4) 09-19-2021 18:52:37 944 MPU requested resend # 194
(4) 09-19-2021 18:52:37 946 PC resending # 3479
(4) 09-19-2021 18:52:37 946 PC resending # 3482
(4) 09-19-2021 18:52:37 944 MPU requested resend # 195
(4) 09-19-2021 18:52:37 946 PC resending # 3485
(4) 09-19-2021 18:52:38 944 MPU requested resend # 196
(4) 09-19-2021 18:52:38 946 PC resending # 3486
(4) 09-19-2021 18:52:38 946 PC resending # 3489
(4) 09-19-2021 18:52:38 944 MPU requested resend # 197
(4) 09-19-2021 18:52:38 946 PC resending # 3492
(4) 09-19-2021 18:52:39 944 MPU requested resend # 198
(4) 09-19-2021 18:52:39 946 PC resending # 3495
(4) 09-19-2021 18:52:39 944 MPU requested resend # 199
(4) 09-19-2021 18:52:39 946 PC resending # 3498
(4) 09-19-2021 18:52:39 944 MPU requested resend # 200
(4) 09-19-2021 18:52:39 946 PC resending # 3502
(4) 09-19-2021 18:52:39 944 MPU requested resend # 201
(4) 09-19-2021 18:52:39 946 PC resending # 3505
(4) 09-19-2021 18:52:39 944 MPU requested resend # 202
(4) 09-19-2021 18:52:39 946 PC resending # 3509
(4) 09-19-2021 18:52:40 944 MPU requested resend # 203
(4) 09-19-2021 18:52:40 946 PC resending # 3510
(4) 09-19-2021 18:52:40 946 PC resending # 3512
(4) 09-19-2021 18:52:40 944 MPU requested resend # 204
(4) 09-19-2021 18:52:40 946 PC resending # 3516
(4) 09-19-2021 18:52:40 944 MPU requested resend # 205
(4) 09-19-2021 18:52:40 946 PC resending # 3520
(4) 09-19-2021 18:52:40 944 MPU requested resend # 206
(4) 09-19-2021 18:52:41 946 PC resending # 3523
(4) 09-19-2021 18:52:41 944 MPU requested resend # 207
(4) 09-19-2021 18:52:41 946 PC resending # 3526
(4) 09-19-2021 18:52:41 944 MPU requested resend # 208
(4) 09-19-2021 18:52:41 946 PC resending # 3529
(4) 09-19-2021 18:52:41 944 MPU requested resend # 209
(4) 09-19-2021 18:52:41 946 PC resending # 3534
(4) 09-19-2021 18:52:41 944 MPU requested resend # 210
(4) 09-19-2021 18:52:41 946 PC resending # 3540
(4) 09-19-2021 18:52:41 944 MPU requested resend # 211
(4) 09-19-2021 18:52:41 946 PC resending # 3544
(4) 09-19-2021 18:52:41 944 MPU requested resend # 212
(4) 09-19-2021 18:52:41 946 PC resending # 3547
(4) 09-19-2021 18:52:42 944 MPU requested resend # 213
(4) 09-19-2021 18:52:42 946 PC resending # 3548
(4) 09-19-2021 18:52:42 946 PC resending # 3550
(4) 09-19-2021 18:52:42 944 MPU requested resend # 214
(4) 09-19-2021 18:52:42 946 PC resending # 3554
(4) 09-19-2021 18:52:42 944 MPU requested resend # 215
(4) 09-19-2021 18:52:42 946 PC resending # 3555
(4) 09-19-2021 18:52:42 946 PC resending # 3557
(4) 09-19-2021 18:52:42 944 MPU requested resend # 216
(4) 09-19-2021 18:52:42 946 PC resending # 3560
(4) 09-19-2021 18:52:43 944 MPU requested resend # 217
(4) 09-19-2021 18:52:43 946 PC resending # 3564
(1) 09-19-2021 18:53:50 Creating report...
(1) 09-19-2021 18:53:58 Saved report to C:\Users\tyni\Desktop\CNC 12 Reports\report_6433DB044D1E-0623214856_2021-09-19_18-53-50.zip
(1) 09-19-2021 18:54:17 204 Exiting CNC...Normal Exit (66)
(1) 09-19-2021 18:54:33 199 CNC Started
(1) 09-19-2021 18:55:43 204 Exiting CNC...Normal Exit (66)
(1) 09-19-2021 18:56:07 199 CNC Started
(4) 09-19-2021 18:56:11 9039 Software Exited, Cycle E-Stop/Reset to Continue
(4) 09-19-2021 18:56:11 944 MPU requested resend # 15
(4) 09-19-2021 18:56:11 946 PC resending # 712
(1) 09-19-2021 18:56:14 CNC12 Acorn Mill v4.64
(4) 09-19-2021 18:56:14 9033 Reset Initiated, Press Reset to Clear
(4) 09-19-2021 18:56:20 4032 Reset Cleared
(1) 09-19-2021 18:57:29 204 Exiting CNC...Normal Exit (66)
(1) 09-19-2021 19:01:03 199 CNC Started
(1) 09-19-2021 19:01:15 102 Error initializing CPU...cannot continue.
(1) 09-19-2021 19:01:23 201 Exiting CNC due to a known error (63)
(1) 09-19-2021 19:21:25 199 CNC Started
(1) 09-19-2021 19:22:06 102 Error initializing CPU...cannot continue.
(1) 09-19-2021 19:22:08 201 Exiting CNC due to a known error (63)
(1) 09-19-2021 19:22:13 199 CNC Started
(4) 09-19-2021 19:22:17 9033 Reset Initiated, Press Reset to Clear
(4) 09-19-2021 19:22:17 944 MPU requested resend # 16
(4) 09-19-2021 19:22:17 946 PC resending # 746
(1) 09-19-2021 19:22:20 CNC12 Acorn Mill v4.64
(4) 09-19-2021 19:22:20 9039 Software Exited, Cycle E-Stop/Reset to Continue
(4) 09-19-2021 19:22:20 944 MPU requested resend # 18
(4) 09-19-2021 19:22:20 946 PC resending # 834
(4) 09-19-2021 19:22:20 9033 Reset Initiated, Press Reset to Clear
(4) 09-19-2021 19:22:26 4032 Reset Cleared
(1) 09-19-2021 19:24:18 406 Emergency stop detected
(1) 09-19-2021 19:24:19 406 Emergency stop detected
(1) 09-19-2021 19:24:20 406 Emergency stop detected
(1) 09-19-2021 19:24:23 406 Emergency stop detected
(1) 09-19-2021 19:24:24 406 Emergency stop detected
(1) 09-19-2021 19:24:25 406 Emergency stop detected
(1) 09-19-2021 19:24:26 406 Emergency stop detected
(1) 09-19-2021 19:24:43 452 Ethernet Communication Error, CNCPC to controller. See Tech Bulletin 270
(4) 09-19-2021 19:25:20 9039 Software Exited, Cycle E-Stop/Reset to Continue
(4) 09-19-2021 19:25:20 9033 Reset Initiated, Press Reset to Clear
(1) 09-19-2021 19:25:24 452 Ethernet Communication Error, CNCPC to controller. See Tech Bulletin 270
(4) 09-19-2021 19:26:48 9033 Reset Initiated, Press Reset to Clear
(4) 09-19-2021 19:26:48 9039 Software Exited, Cycle E-Stop/Reset to Continue
(4) 09-19-2021 19:26:49 944 MPU requested resend # 19
(4) 09-19-2021 19:26:49 946 PC resending # 843
(1) 09-19-2021 19:26:53 452 Ethernet Communication Error, CNCPC to controller. See Tech Bulletin 270
(4) 09-19-2021 19:27:17 9033 Reset Initiated, Press Reset to Clear
(4) 09-19-2021 19:27:19 4032 Reset Cleared
(1) 09-19-2021 19:27:29 406 Emergency stop detected
(1) 09-19-2021 19:27:30 406 Emergency stop detected
(1) 09-19-2021 19:28:00 406 Emergency stop detected
(1) 09-19-2021 19:28:01 406 Emergency stop detected
(1) 09-19-2021 19:28:15 406 Emergency stop detected
(1) 09-19-2021 19:28:20 406 Emergency stop detected
(1) 09-19-2021 19:28:23 406 Emergency stop detected
(1) 09-19-2021 19:28:49 406 Emergency stop detected
(1) 09-19-2021 19:29:34 406 Emergency stop detected
(1) 09-19-2021 19:29:42 406 Emergency stop detected
(1) 09-19-2021 19:30:44 406 Emergency stop detected
(1) 09-19-2021 19:31:09 406 Emergency stop detected
(1) 09-19-2021 19:39:16 406 Emergency stop detected
(1) 09-19-2021 19:39:16 406 Emergency stop detected
(1) 09-19-2021 19:39:17 406 Emergency stop detected
(1) 09-19-2021 19:39:17 406 Emergency stop detected
(1) 09-19-2021 19:39:17 406 Emergency stop detected
(1) 09-19-2021 19:41:18 406 Emergency stop detected
(1) 09-19-2021 19:41:43 406 Emergency stop detected
(1) 09-19-2021 19:52:49 406 Emergency stop detected
(1) 09-19-2021 22:03:44 406 Emergency stop detected
(1) 09-19-2021 22:03:44 406 Emergency stop detected
(1) 09-19-2021 22:03:46 406 Emergency stop detected
(4) 09-19-2021 22:06:27 944 MPU requested resend # 20
(4) 09-19-2021 22:06:27 946 PC resending # 846
(1) 09-19-2021 22:06:39 204 Exiting CNC...Normal Exit (66)
(1) 09-19-2021 22:07:22 199 CNC Started
(4) 09-19-2021 22:07:27 9039 Software Exited, Cycle E-Stop/Reset to Continue
(4) 09-19-2021 22:07:27 944 MPU requested resend # 19
(4) 09-19-2021 22:07:27 946 PC resending # 1021
(1) 09-19-2021 22:07:30 CNC12 Acorn Mill v4.64
(4) 09-19-2021 22:07:30 9033 Reset Initiated, Press Reset to Clear
(4) 09-19-2021 22:07:30 944 MPU requested resend # 21
(4) 09-19-2021 22:07:30 946 PC resending # 1086
(4) 09-19-2021 22:07:53 4032 Reset Cleared
(4) 09-19-2021 22:08:13 944 MPU requested resend # 22
(4) 09-19-2021 22:08:13 946 PC resending # 1090
(4) 09-19-2021 22:08:16 944 MPU requested resend # 23
(4) 09-19-2021 22:08:16 946 PC resending # 1092
(1) 09-19-2021 22:09:10 406 Emergency stop detected
(1) 09-19-2021 22:12:44 406 Emergency stop detected
(1) 09-19-2021 22:12:45 406 Emergency stop detected
(1) 09-19-2021 22:12:48 406 Emergency stop detected
(1) 09-19-2021 22:12:51 406 Emergency stop detected
(1) 09-19-2021 22:12:53 406 Emergency stop detected
(1) 09-19-2021 22:13:00 406 Emergency stop detected
(1) 09-19-2021 22:13:01 406 Emergency stop detected
(1) 09-19-2021 22:13:02 406 Emergency stop detected
(4) 09-19-2021 22:14:38 944 MPU requested resend # 24
(4) 09-19-2021 22:14:38 946 PC resending # 1095
(4) 09-19-2021 22:14:40 944 MPU requested resend # 25
(4) 09-19-2021 22:14:40 946 PC resending # 1098
(4) 09-19-2021 22:14:40 944 MPU requested resend # 26
(4) 09-19-2021 22:14:40 946 PC resending # 1101
(1) 09-19-2021 22:15:26 406 Emergency stop detected
(4) 09-19-2021 22:27:51 944 MPU requested resend # 27
(4) 09-19-2021 22:27:52 946 PC resending # 1107
(4) 09-19-2021 22:27:52 944 MPU requested resend # 28
(4) 09-19-2021 22:27:52 944 MPU requested resend # 29
(4) 09-19-2021 22:27:52 946 PC resending # 1129
(4) 09-19-2021 22:27:52 946 PC resending # 1132
(4) 09-19-2021 22:27:52 946 PC resending # 1149
(4) 09-19-2021 22:27:54 944 MPU requested resend # 30
(4) 09-19-2021 22:27:54 946 PC resending # 1173
(4) 09-19-2021 22:27:54 944 MPU requested resend # 31
(4) 09-19-2021 22:27:54 946 PC resending # 1191
(4) 09-19-2021 22:27:54 944 MPU requested resend # 32
(4) 09-19-2021 22:27:54 946 PC resending # 1213
(4) 09-19-2021 22:27:54 944 MPU requested resend # 33
(4) 09-19-2021 22:27:55 946 PC resending # 1214
(4) 09-19-2021 22:27:55 946 PC resending # 1218
(4) 09-19-2021 22:27:56 944 MPU requested resend # 34
(4) 09-19-2021 22:27:56 946 PC resending # 1225
(4) 09-19-2021 22:27:56 944 MPU requested resend # 35
(4) 09-19-2021 22:27:56 946 PC resending # 1243
(1) 09-19-2021 22:28:09 204 Exiting CNC...Normal Exit (66)
(1) 09-19-2021 22:28:41 199 CNC Started
(1) 09-19-2021 22:28:48 CNC12 Acorn Mill v4.64
(4) 09-19-2021 22:28:48 9033 Reset Initiated, Press Reset to Clear
(4) 09-19-2021 22:28:55 4032 Reset Cleared
(1) 09-19-2021 22:29:12 406 Emergency stop detected
(1) 09-19-2021 22:29:37 406 Emergency stop detected
(1) 09-19-2021 22:37:37 204 Exiting CNC...Normal Exit (66)
(1) 09-19-2021 22:37:44 199 CNC Started
(4) 09-19-2021 22:37:48 9039 Software Exited, Cycle E-Stop/Reset to Continue
(1) 09-19-2021 22:37:50 CNC12 Acorn Mill v4.64
(4) 09-19-2021 22:37:50 9033 Reset Initiated, Press Reset to Clear
(1) 09-19-2021 22:38:15 452 Ethernet Communication Error, CNCPC to controller. See Tech Bulletin 270
(1) 09-19-2021 22:38:59 204 Exiting CNC...Normal Exit (66)
(1) 09-19-2021 22:39:17 199 CNC Started
(1) 09-19-2021 22:40:23 102 Error initializing CPU...cannot continue.
(1) 09-19-2021 22:40:25 201 Exiting CNC due to a known error (63)
(1) 09-19-2021 22:41:13 199 CNC Started
(4) 09-19-2021 22:41:17 9033 Reset Initiated, Press Reset to Clear
(1) 09-19-2021 22:41:19 CNC12 Acorn Mill v4.64
(4) 09-19-2021 22:41:19 9039 Software Exited, Cycle E-Stop/Reset to Continue
(4) 09-19-2021 22:41:20 9033 Reset Initiated, Press Reset to Clear
(4) 09-19-2021 22:41:25 4032 Reset Cleared
(1) 09-19-2021 22:41:51 406 Emergency stop detected
(1) 09-19-2021 22:43:17 Creating report...
Marty
In your videos, your machine needs to home to
Z+
Y+
X+
Your X soft limit is incorrect. It should be a NEGATIVE value
In the homing and travel screen, you need to change homing direction to a +M92 for Axis 1 (X)
You probably also have the X axis moving the wrong direction and need to change in the AXIS Configuration
Under X, change DIRECTION REVERSAL TO N
Mill:
X positive, the table moves to the LEFT
X negative, the table moves to the RIGHT
Y positive, the table moves toward you, away from the column
Y negative, the table moves away from you, toward the column
Z positive, the head moves UP
Z negative, the head moves DOWN
Lathe
Z negative, carriage moves TOWARD the headstock
Z positive, the carriage moves AWAY from the headstock
X negative, the cutter moves TOWARD the spindle centerline
X positive, the cutter moves AWAY from the spindle centerline
Please review this great post on Machine tool coordinate systems:
viewtopic.php?f=63&t=3648
Tell us EXACTLY how your Estop button is wired.
Simply put. Estop NC, one wire to Acorn COM and one wire to Input 8.
Your problem as previously stated by others, is that you are tripping the ESTOP when your home switches trip. That is not supposed to happen. The Estop trip halts the control.
As was also stated. Do not mix the two machines. Get one going first then worry about the other.
You also still have MANY PC/MPU Resends. This must be corrected. You have noise that must be fixed.
From your logs:
(4) 09-19-2021 18:51:50 946 PC resending # 3067
(4) 09-19-2021 18:51:50 944 MPU requested resend # 152
(4) 09-19-2021 18:51:50 946 PC resending # 3097
(4) 09-19-2021 18:51:50 944 MPU requested resend # 153
(4) 09-19-2021 18:51:50 946 PC resending # 3119
(4) 09-19-2021 18:51:50 946 PC resending # 3128
(4) 09-19-2021 18:51:50 944 MPU requested resend # 154
(4) 09-19-2021 18:51:50 946 PC resending # 3131
(1) 09-19-2021 18:51:50 406 Emergency stop detected
(4) 09-19-2021 18:52:18 944 MPU requested resend # 155
(4) 09-19-2021 18:52:18 946 PC resending # 3134
(4) 09-19-2021 18:52:19 944 MPU requested resend # 156
(4) 09-19-2021 18:52:19 946 PC resending # 3138
(4) 09-19-2021 18:52:19 944 MPU requested resend # 157
(4) 09-19-2021 18:52:19 946 PC resending # 3142
(4) 09-19-2021 18:52:19 944 MPU requested resend # 158
(4) 09-19-2021 18:52:19 946 PC resending # 3146
(4) 09-19-2021 18:52:19 944 MPU requested resend # 159
(4) 09-19-2021 18:52:19 946 PC resending # 3149
(4) 09-19-2021 18:52:19 944 MPU requested resend # 160
(4) 09-19-2021 18:52:19 946 PC resending # 3153
(4) 09-19-2021 18:52:19 944 MPU requested resend # 161
(4) 09-19-2021 18:52:19 946 PC resending # 3158
(4) 09-19-2021 18:52:19 944 MPU requested resend # 162
(4) 09-19-2021 18:52:19 946 PC resending # 3162
(4) 09-19-2021 18:52:20 944 MPU requested resend # 163
(4) 09-19-2021 18:52:20 946 PC resending # 3165
(4) 09-19-2021 18:52:20 944 MPU requested resend # 164
(4) 09-19-2021 18:52:20 946 PC resending # 3168
(4) 09-19-2021 18:52:20 944 MPU requested resend # 165
(4) 09-19-2021 18:52:20 944 MPU requested resend # 166
(4) 09-19-2021 18:52:20 946 PC resending # 3173
(4) 09-19-2021 18:52:20 946 PC resending # 3178
(4) 09-19-2021 18:52:20 944 MPU requested resend # 167
(4) 09-19-2021 18:52:20 946 PC resending # 3182
(4) 09-19-2021 18:52:20 944 MPU requested resend # 168
(4) 09-19-2021 18:52:20 946 PC resending # 3185
(4) 09-19-2021 18:52:21 944 MPU requested resend # 169
(4) 09-19-2021 18:52:21 946 PC resending # 3188
(4) 09-19-2021 18:52:21 944 MPU requested resend # 170
(4) 09-19-2021 18:52:21 946 PC resending # 3192
(4) 09-19-2021 18:52:22 944 MPU requested resend # 171
(4) 09-19-2021 18:52:22 944 MPU requested resend # 172
(4) 09-19-2021 18:52:22 946 PC resending # 3222
(4) 09-19-2021 18:52:22 944 MPU requested resend # 173
(4) 09-19-2021 18:52:22 946 PC resending # 3249
(4) 09-19-2021 18:52:22 944 MPU requested resend # 174
(4) 09-19-2021 18:52:22 946 PC resending # 3268
(4) 09-19-2021 18:52:22 946 PC resending # 3271
(4) 09-19-2021 18:52:22 946 PC resending # 3278
(4) 09-19-2021 18:52:24 944 MPU requested resend # 175
(4) 09-19-2021 18:52:24 946 PC resending # 3280
(4) 09-19-2021 18:52:24 944 MPU requested resend # 176
(4) 09-19-2021 18:52:24 946 PC resending # 3283
(4) 09-19-2021 18:52:24 944 MPU requested resend # 177
(4) 09-19-2021 18:52:24 946 PC resending # 3284
(4) 09-19-2021 18:52:24 946 PC resending # 3287
(4) 09-19-2021 18:52:24 944 MPU requested resend # 178
(4) 09-19-2021 18:52:24 946 PC resending # 3290
(4) 09-19-2021 18:52:25 944 MPU requested resend # 179
(4) 09-19-2021 18:52:25 946 PC resending # 3293
(4) 09-19-2021 18:52:25 944 MPU requested resend # 180
(4) 09-19-2021 18:52:25 946 PC resending # 3296
(4) 09-19-2021 18:52:30 944 MPU requested resend # 181
(4) 09-19-2021 18:52:30 946 PC resending # 3299
(4) 09-19-2021 18:52:31 944 MPU requested resend # 182
(4) 09-19-2021 18:52:31 946 PC resending # 3302
(4) 09-19-2021 18:52:31 944 MPU requested resend # 183
(4) 09-19-2021 18:52:31 946 PC resending # 3306
(4) 09-19-2021 18:52:32 944 MPU requested resend # 184
(4) 09-19-2021 18:52:32 944 MPU requested resend # 185
(4) 09-19-2021 18:52:32 946 PC resending # 3350
(4) 09-19-2021 18:52:32 944 MPU requested resend # 186
(4) 09-19-2021 18:52:32 946 PC resending # 3380
(4) 09-19-2021 18:52:32 944 MPU requested resend # 187
(4) 09-19-2021 18:52:32 946 PC resending # 3409
(4) 09-19-2021 18:52:32 944 MPU requested resend # 188
(4) 09-19-2021 18:52:32 946 PC resending # 3435
(4) 09-19-2021 18:52:32 944 MPU requested resend # 189
(4) 09-19-2021 18:52:32 946 PC resending # 3455
(4) 09-19-2021 18:52:32 946 PC resending # 3466
(4) 09-19-2021 18:52:34 944 MPU requested resend # 190
(4) 09-19-2021 18:52:34 944 MPU requested resend # 191
(4) 09-19-2021 18:52:34 946 PC resending # 3469
(4) 09-19-2021 18:52:34 946 PC resending # 3473
(4) 09-19-2021 18:52:35 944 MPU requested resend # 192
(4) 09-19-2021 18:52:35 946 PC resending # 3476
(4) 09-19-2021 18:52:36 944 MPU requested resend # 193
(4) 09-19-2021 18:52:36 946 PC resending # 3478
(4) 09-19-2021 18:52:37 944 MPU requested resend # 194
(4) 09-19-2021 18:52:37 946 PC resending # 3479
(4) 09-19-2021 18:52:37 946 PC resending # 3482
(4) 09-19-2021 18:52:37 944 MPU requested resend # 195
(4) 09-19-2021 18:52:37 946 PC resending # 3485
(4) 09-19-2021 18:52:38 944 MPU requested resend # 196
(4) 09-19-2021 18:52:38 946 PC resending # 3486
(4) 09-19-2021 18:52:38 946 PC resending # 3489
(4) 09-19-2021 18:52:38 944 MPU requested resend # 197
(4) 09-19-2021 18:52:38 946 PC resending # 3492
(4) 09-19-2021 18:52:39 944 MPU requested resend # 198
(4) 09-19-2021 18:52:39 946 PC resending # 3495
(4) 09-19-2021 18:52:39 944 MPU requested resend # 199
(4) 09-19-2021 18:52:39 946 PC resending # 3498
(4) 09-19-2021 18:52:39 944 MPU requested resend # 200
(4) 09-19-2021 18:52:39 946 PC resending # 3502
(4) 09-19-2021 18:52:39 944 MPU requested resend # 201
(4) 09-19-2021 18:52:39 946 PC resending # 3505
(4) 09-19-2021 18:52:39 944 MPU requested resend # 202
(4) 09-19-2021 18:52:39 946 PC resending # 3509
(4) 09-19-2021 18:52:40 944 MPU requested resend # 203
(4) 09-19-2021 18:52:40 946 PC resending # 3510
(4) 09-19-2021 18:52:40 946 PC resending # 3512
(4) 09-19-2021 18:52:40 944 MPU requested resend # 204
(4) 09-19-2021 18:52:40 946 PC resending # 3516
(4) 09-19-2021 18:52:40 944 MPU requested resend # 205
(4) 09-19-2021 18:52:40 946 PC resending # 3520
(4) 09-19-2021 18:52:40 944 MPU requested resend # 206
(4) 09-19-2021 18:52:41 946 PC resending # 3523
(4) 09-19-2021 18:52:41 944 MPU requested resend # 207
(4) 09-19-2021 18:52:41 946 PC resending # 3526
(4) 09-19-2021 18:52:41 944 MPU requested resend # 208
(4) 09-19-2021 18:52:41 946 PC resending # 3529
(4) 09-19-2021 18:52:41 944 MPU requested resend # 209
(4) 09-19-2021 18:52:41 946 PC resending # 3534
(4) 09-19-2021 18:52:41 944 MPU requested resend # 210
(4) 09-19-2021 18:52:41 946 PC resending # 3540
(4) 09-19-2021 18:52:41 944 MPU requested resend # 211
(4) 09-19-2021 18:52:41 946 PC resending # 3544
(4) 09-19-2021 18:52:41 944 MPU requested resend # 212
(4) 09-19-2021 18:52:41 946 PC resending # 3547
(4) 09-19-2021 18:52:42 944 MPU requested resend # 213
(4) 09-19-2021 18:52:42 946 PC resending # 3548
(4) 09-19-2021 18:52:42 946 PC resending # 3550
(4) 09-19-2021 18:52:42 944 MPU requested resend # 214
(4) 09-19-2021 18:52:42 946 PC resending # 3554
(4) 09-19-2021 18:52:42 944 MPU requested resend # 215
(4) 09-19-2021 18:52:42 946 PC resending # 3555
(4) 09-19-2021 18:52:42 946 PC resending # 3557
(4) 09-19-2021 18:52:42 944 MPU requested resend # 216
(4) 09-19-2021 18:52:42 946 PC resending # 3560
(4) 09-19-2021 18:52:43 944 MPU requested resend # 217
(4) 09-19-2021 18:52:43 946 PC resending # 3564
(1) 09-19-2021 18:53:50 Creating report...
(1) 09-19-2021 18:53:58 Saved report to C:\Users\tyni\Desktop\CNC 12 Reports\report_6433DB044D1E-0623214856_2021-09-19_18-53-50.zip
(1) 09-19-2021 18:54:17 204 Exiting CNC...Normal Exit (66)
(1) 09-19-2021 18:54:33 199 CNC Started
(1) 09-19-2021 18:55:43 204 Exiting CNC...Normal Exit (66)
(1) 09-19-2021 18:56:07 199 CNC Started
(4) 09-19-2021 18:56:11 9039 Software Exited, Cycle E-Stop/Reset to Continue
(4) 09-19-2021 18:56:11 944 MPU requested resend # 15
(4) 09-19-2021 18:56:11 946 PC resending # 712
(1) 09-19-2021 18:56:14 CNC12 Acorn Mill v4.64
(4) 09-19-2021 18:56:14 9033 Reset Initiated, Press Reset to Clear
(4) 09-19-2021 18:56:20 4032 Reset Cleared
(1) 09-19-2021 18:57:29 204 Exiting CNC...Normal Exit (66)
(1) 09-19-2021 19:01:03 199 CNC Started
(1) 09-19-2021 19:01:15 102 Error initializing CPU...cannot continue.
(1) 09-19-2021 19:01:23 201 Exiting CNC due to a known error (63)
(1) 09-19-2021 19:21:25 199 CNC Started
(1) 09-19-2021 19:22:06 102 Error initializing CPU...cannot continue.
(1) 09-19-2021 19:22:08 201 Exiting CNC due to a known error (63)
(1) 09-19-2021 19:22:13 199 CNC Started
(4) 09-19-2021 19:22:17 9033 Reset Initiated, Press Reset to Clear
(4) 09-19-2021 19:22:17 944 MPU requested resend # 16
(4) 09-19-2021 19:22:17 946 PC resending # 746
(1) 09-19-2021 19:22:20 CNC12 Acorn Mill v4.64
(4) 09-19-2021 19:22:20 9039 Software Exited, Cycle E-Stop/Reset to Continue
(4) 09-19-2021 19:22:20 944 MPU requested resend # 18
(4) 09-19-2021 19:22:20 946 PC resending # 834
(4) 09-19-2021 19:22:20 9033 Reset Initiated, Press Reset to Clear
(4) 09-19-2021 19:22:26 4032 Reset Cleared
(1) 09-19-2021 19:24:18 406 Emergency stop detected
(1) 09-19-2021 19:24:19 406 Emergency stop detected
(1) 09-19-2021 19:24:20 406 Emergency stop detected
(1) 09-19-2021 19:24:23 406 Emergency stop detected
(1) 09-19-2021 19:24:24 406 Emergency stop detected
(1) 09-19-2021 19:24:25 406 Emergency stop detected
(1) 09-19-2021 19:24:26 406 Emergency stop detected
(1) 09-19-2021 19:24:43 452 Ethernet Communication Error, CNCPC to controller. See Tech Bulletin 270
(4) 09-19-2021 19:25:20 9039 Software Exited, Cycle E-Stop/Reset to Continue
(4) 09-19-2021 19:25:20 9033 Reset Initiated, Press Reset to Clear
(1) 09-19-2021 19:25:24 452 Ethernet Communication Error, CNCPC to controller. See Tech Bulletin 270
(4) 09-19-2021 19:26:48 9033 Reset Initiated, Press Reset to Clear
(4) 09-19-2021 19:26:48 9039 Software Exited, Cycle E-Stop/Reset to Continue
(4) 09-19-2021 19:26:49 944 MPU requested resend # 19
(4) 09-19-2021 19:26:49 946 PC resending # 843
(1) 09-19-2021 19:26:53 452 Ethernet Communication Error, CNCPC to controller. See Tech Bulletin 270
(4) 09-19-2021 19:27:17 9033 Reset Initiated, Press Reset to Clear
(4) 09-19-2021 19:27:19 4032 Reset Cleared
(1) 09-19-2021 19:27:29 406 Emergency stop detected
(1) 09-19-2021 19:27:30 406 Emergency stop detected
(1) 09-19-2021 19:28:00 406 Emergency stop detected
(1) 09-19-2021 19:28:01 406 Emergency stop detected
(1) 09-19-2021 19:28:15 406 Emergency stop detected
(1) 09-19-2021 19:28:20 406 Emergency stop detected
(1) 09-19-2021 19:28:23 406 Emergency stop detected
(1) 09-19-2021 19:28:49 406 Emergency stop detected
(1) 09-19-2021 19:29:34 406 Emergency stop detected
(1) 09-19-2021 19:29:42 406 Emergency stop detected
(1) 09-19-2021 19:30:44 406 Emergency stop detected
(1) 09-19-2021 19:31:09 406 Emergency stop detected
(1) 09-19-2021 19:39:16 406 Emergency stop detected
(1) 09-19-2021 19:39:16 406 Emergency stop detected
(1) 09-19-2021 19:39:17 406 Emergency stop detected
(1) 09-19-2021 19:39:17 406 Emergency stop detected
(1) 09-19-2021 19:39:17 406 Emergency stop detected
(1) 09-19-2021 19:41:18 406 Emergency stop detected
(1) 09-19-2021 19:41:43 406 Emergency stop detected
(1) 09-19-2021 19:52:49 406 Emergency stop detected
(1) 09-19-2021 22:03:44 406 Emergency stop detected
(1) 09-19-2021 22:03:44 406 Emergency stop detected
(1) 09-19-2021 22:03:46 406 Emergency stop detected
(4) 09-19-2021 22:06:27 944 MPU requested resend # 20
(4) 09-19-2021 22:06:27 946 PC resending # 846
(1) 09-19-2021 22:06:39 204 Exiting CNC...Normal Exit (66)
(1) 09-19-2021 22:07:22 199 CNC Started
(4) 09-19-2021 22:07:27 9039 Software Exited, Cycle E-Stop/Reset to Continue
(4) 09-19-2021 22:07:27 944 MPU requested resend # 19
(4) 09-19-2021 22:07:27 946 PC resending # 1021
(1) 09-19-2021 22:07:30 CNC12 Acorn Mill v4.64
(4) 09-19-2021 22:07:30 9033 Reset Initiated, Press Reset to Clear
(4) 09-19-2021 22:07:30 944 MPU requested resend # 21
(4) 09-19-2021 22:07:30 946 PC resending # 1086
(4) 09-19-2021 22:07:53 4032 Reset Cleared
(4) 09-19-2021 22:08:13 944 MPU requested resend # 22
(4) 09-19-2021 22:08:13 946 PC resending # 1090
(4) 09-19-2021 22:08:16 944 MPU requested resend # 23
(4) 09-19-2021 22:08:16 946 PC resending # 1092
(1) 09-19-2021 22:09:10 406 Emergency stop detected
(1) 09-19-2021 22:12:44 406 Emergency stop detected
(1) 09-19-2021 22:12:45 406 Emergency stop detected
(1) 09-19-2021 22:12:48 406 Emergency stop detected
(1) 09-19-2021 22:12:51 406 Emergency stop detected
(1) 09-19-2021 22:12:53 406 Emergency stop detected
(1) 09-19-2021 22:13:00 406 Emergency stop detected
(1) 09-19-2021 22:13:01 406 Emergency stop detected
(1) 09-19-2021 22:13:02 406 Emergency stop detected
(4) 09-19-2021 22:14:38 944 MPU requested resend # 24
(4) 09-19-2021 22:14:38 946 PC resending # 1095
(4) 09-19-2021 22:14:40 944 MPU requested resend # 25
(4) 09-19-2021 22:14:40 946 PC resending # 1098
(4) 09-19-2021 22:14:40 944 MPU requested resend # 26
(4) 09-19-2021 22:14:40 946 PC resending # 1101
(1) 09-19-2021 22:15:26 406 Emergency stop detected
(4) 09-19-2021 22:27:51 944 MPU requested resend # 27
(4) 09-19-2021 22:27:52 946 PC resending # 1107
(4) 09-19-2021 22:27:52 944 MPU requested resend # 28
(4) 09-19-2021 22:27:52 944 MPU requested resend # 29
(4) 09-19-2021 22:27:52 946 PC resending # 1129
(4) 09-19-2021 22:27:52 946 PC resending # 1132
(4) 09-19-2021 22:27:52 946 PC resending # 1149
(4) 09-19-2021 22:27:54 944 MPU requested resend # 30
(4) 09-19-2021 22:27:54 946 PC resending # 1173
(4) 09-19-2021 22:27:54 944 MPU requested resend # 31
(4) 09-19-2021 22:27:54 946 PC resending # 1191
(4) 09-19-2021 22:27:54 944 MPU requested resend # 32
(4) 09-19-2021 22:27:54 946 PC resending # 1213
(4) 09-19-2021 22:27:54 944 MPU requested resend # 33
(4) 09-19-2021 22:27:55 946 PC resending # 1214
(4) 09-19-2021 22:27:55 946 PC resending # 1218
(4) 09-19-2021 22:27:56 944 MPU requested resend # 34
(4) 09-19-2021 22:27:56 946 PC resending # 1225
(4) 09-19-2021 22:27:56 944 MPU requested resend # 35
(4) 09-19-2021 22:27:56 946 PC resending # 1243
(1) 09-19-2021 22:28:09 204 Exiting CNC...Normal Exit (66)
(1) 09-19-2021 22:28:41 199 CNC Started
(1) 09-19-2021 22:28:48 CNC12 Acorn Mill v4.64
(4) 09-19-2021 22:28:48 9033 Reset Initiated, Press Reset to Clear
(4) 09-19-2021 22:28:55 4032 Reset Cleared
(1) 09-19-2021 22:29:12 406 Emergency stop detected
(1) 09-19-2021 22:29:37 406 Emergency stop detected
(1) 09-19-2021 22:37:37 204 Exiting CNC...Normal Exit (66)
(1) 09-19-2021 22:37:44 199 CNC Started
(4) 09-19-2021 22:37:48 9039 Software Exited, Cycle E-Stop/Reset to Continue
(1) 09-19-2021 22:37:50 CNC12 Acorn Mill v4.64
(4) 09-19-2021 22:37:50 9033 Reset Initiated, Press Reset to Clear
(1) 09-19-2021 22:38:15 452 Ethernet Communication Error, CNCPC to controller. See Tech Bulletin 270
(1) 09-19-2021 22:38:59 204 Exiting CNC...Normal Exit (66)
(1) 09-19-2021 22:39:17 199 CNC Started
(1) 09-19-2021 22:40:23 102 Error initializing CPU...cannot continue.
(1) 09-19-2021 22:40:25 201 Exiting CNC due to a known error (63)
(1) 09-19-2021 22:41:13 199 CNC Started
(4) 09-19-2021 22:41:17 9033 Reset Initiated, Press Reset to Clear
(1) 09-19-2021 22:41:19 CNC12 Acorn Mill v4.64
(4) 09-19-2021 22:41:19 9039 Software Exited, Cycle E-Stop/Reset to Continue
(4) 09-19-2021 22:41:20 9033 Reset Initiated, Press Reset to Clear
(4) 09-19-2021 22:41:25 4032 Reset Cleared
(1) 09-19-2021 22:41:51 406 Emergency stop detected
(1) 09-19-2021 22:43:17 Creating report...