Huanyang HY03D023B, 12000RPM Max Speed
tuffduck
Post by tuffduck »
Going through the settings and now the Huanyang HY03D023B VFD maxes at 12000 RPM when 14000 rpm is typed into the MDI. Does anyone know what setting(s) would cause this?
Re: Huanyang HY03D023B, 12000RPM Max Speed
your VFD needs to be calibrated to the 0-10 signal from Acorn.
viewtopic.php?f=63&t=1650
tuffduck
Post by tuffduck »
Followed the steps.
Voltage from Acorn is correct.
Tuning the VFD- we get only one speed no matter what is set 12000RPM
Here are settings we used for a 3kw air cooled spindle.
PD001 0
PD003 300
PD004 300
PD005 300
PD006 2.5
PD007 20
PD008 220
PD009 15
PD010 8
PD011 200
PD014 15
PD015 15
PD070 0
PD072 300
PD142 8.6
PD143 2
PD144 2000
PD145 2.5
PD176 1
tuffduck
Post by tuffduck »
Here is what I have.
tuffduck
Post by tuffduck »
Checked the spindle in Manual and everything works correctly. The VCP controls will allow be start and stop the spindle in auto but the plus and minus buttons do not respond.
It appears the VFD is not set up for remote control of spindle speed.
tuffduck
Post by tuffduck »
Latest Report. Checked Acorn's voltage outputs for the spindle bench test and all was correct.
report_E415F6F250EF-0205202948_2021-08-02_17-37-31.zip
(1.99 MiB) Downloaded 67 times
tuffduck
Post by tuffduck »
PD001 =1
PD002 =1
These control remote control
Are there more settings?
tuffduck
Post by tuffduck »
A few more pictures.
tuffduck wrote: Mon Aug 02, 2021 5:44 pm PD001 =1
PD002 =1
Since you haven't posted the VFD manual and I'm too lazy to hunt for it, I don't know if there are more settings.