Huanyang HY03D023B, 12000RPM Max Speed
Re: Huanyang HY03D023B, 12000RPM Max Speed
Hi Marty,
Setting PD005 = 180 gives the spindle one speed at 12000 rpm for all inputs on the MDI.
It does not sound like you have the VFD configured correctly. Did you move the jumper on the VFD per the notes?
Please create a sketch on how you have the VFD wired to Acorn
The jumper is on V1. Here is the diagram I used.
In your wizard you have the "spindle min speed in high range" set at 12000, why? Set it to 0.
Changed the setting to 0, no change.
Have you tested the VFD from it's front panel?
VFD works correctly from the front panel.
You can raise and lower the speed appropriately from the front panel?
You have bench tested Acorn's analog spindle speed output and it is functioning properly (Passed its test)?
These do not appear to be correct based on notes sheet I postedtuffduck wrote: ↑Mon Aug 02, 2021 2:31 pm Followed the steps.
Voltage from Acorn is correct.
Tuning the VFD- we get only one speed no matter what is set 12000RPM
Here are settings we used for a 3kw air cooled spindle.
PD001 0
PD003 300
PD004 300
PD005 300
PD006 2.5
PD007 20
PD008 220
PD009 15
PD010 8
PD011 200
PD014 15
PD015 15
PD070 0
PD072 300
PD142 8.6
PD143 2
PD144 2000
PD145 2.5
PD176 1
Did you change any of them?
I am attaching the manual I have for the HY VFD
Please revise the current settings you have. For PD001 setting of 0 only the front panel will control the VFD. Setting to 1 will use the external terminal blocks.
- inverter.pdf
- (12.12 MiB) Downloaded 80 times
The speed can be adjusted correctly from the front panel. The model I have is not in the manual. PD003,PD004,PD005 cannot be set to 60. The spindle will not turn at these settings. These are the only setting I have changed after a Factory Reset.
PD001 1
PD002 1
PD003 300
PD004 300
PD005 300
PD006 2.5
PD008 220
PD011 200
PD014 10
PD015 10
PD070 0
PD072 300
PD142 8.6
PD143 4
PD144 3000
PD1PD176 1
PD001 1
PD002 1
PD003 300
PD004 300
PD005 300
PD006 2.5
PD008 220
PD011 200
PD014 10
PD015 10
PD070 0
PD072 300
PD142 8.6
PD143 4
PD144 3000
PD1PD176 1