EGND on acorn board?

Post by LenelyWolf »

Hi guys
I’ve got another silly question here. Does the EGND on acorn board suppose to be connected to the mains earth?
Attachments
image.jpg
martyscncgarage
Posts: 9914
Joined: Tue Mar 28, 2017 12:01 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Mesa, AZ

Re: EGND on acorn board?

Post by martyscncgarage »

LenelyWolf wrote: Sun Apr 18, 2021 7:19 am Hi guys
I’ve got another silly question here. Does the EGND on acorn board suppose to be connected to the mains earth?
Not silly question.
EGN is Earth Ground. So yes.
If you mount the Acorn on metal stand offs and those stand offs are mounted to a metal panel, that panel should be bonded to the service ground. You accomplish the same thing.

Acorn COM and Earth ground should be connected together at the Acorn Power supply.
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
LenelyWolf
Posts: 118
Joined: Sun Jan 17, 2021 3:13 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: EGND on acorn board?

Post by LenelyWolf »

martyscncgarage wrote: Sun Apr 18, 2021 9:50 am
LenelyWolf wrote: Sun Apr 18, 2021 7:19 am Hi guys
I’ve got another silly question here. Does the EGND on acorn board suppose to be connected to the mains earth?
Not silly question.
EGN is Earth Ground. So yes.
If you mount the Acorn on metal stand offs and those stand offs are mounted to a metal panel, that panel should be bonded to the service ground. You accomplish the same thing.

Acorn COM and Earth ground should be connected together at the Acorn Power supply.
Thanks for quick replay... problem is that I have plastic stand offs so I have to either make one metal stand off or run a wire to it. But that is my problem now... thanks again.. really appreciate quick support 😉
martyscncgarage
Posts: 9914
Joined: Tue Mar 28, 2017 12:01 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Mesa, AZ

Re: EGND on acorn board?

Post by martyscncgarage »

LenelyWolf wrote: Sun Apr 18, 2021 9:56 am
martyscncgarage wrote: Sun Apr 18, 2021 9:50 am
LenelyWolf wrote: Sun Apr 18, 2021 7:19 am Hi guys
I’ve got another silly question here. Does the EGND on acorn board suppose to be connected to the mains earth?
Not silly question.
EGN is Earth Ground. So yes.
If you mount the Acorn on metal stand offs and those stand offs are mounted to a metal panel, that panel should be bonded to the service ground. You accomplish the same thing.

Acorn COM and Earth ground should be connected together at the Acorn Power supply.
Thanks for quick replay... problem is that I have plastic stand offs so I have to either make one metal stand off or run a wire to it. But that is my problem now... thanks again.. really appreciate quick support 😉
Eground is actually brought to the board by its power connector. That should suffice. Or do be safe run a jumper from the power supply Acorn connector Eground terminal to the pad on the PC board.
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
tblough
Posts: 3099
Joined: Tue Mar 22, 2016 10:03 am
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: Yes
CNC Control System Serial Number: 100505
100327
102696
103432
7804732B977B-0624192192
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Boston, MA
Contact:

Re: EGND on acorn board?

Post by tblough »

In PCB design, parts that are connected by circuit traces are given "signal" names. When adding screw holes to a PCB, you can connect them to a signal or leave them unconnected. What the EGND on the screw pad refers to is that it is connected internally on the board to anything else labeled EGND. You don't need to worry about anything because the screw pads are tied electrically internally on the board to EGND - same as the ground input on the power connector which you should have connected already.
Inkedimage_LI.jpg
Cheers,

Tom
Confidence is the feeling you have before you fully understand the situation.