Acorn - PCB Ferrite Bead (FB6) Meltdown <cause explained>
Posted: Wed Apr 14, 2021 1:27 am
The ferrite bead (FB6) on the Acorn PCB went up in smoke and support's email response was:
"This blows when there is a voltage difference between com and ground. Try connecting a jumper between the 0V common and ground on the power supply. With the Jumper, the Acorn might function, even with the blown Ferrite bead (FB6)"
I am wanting to understand the issue some more so I either do not do further damage to the existing PCB or the potential replacement PCB.
Setup
1. This issue happened when I started to commission my touch probe (plate).
2. My spindle shaft is earthed through its chassis, so I connected Acorn common (0v) to the spindle chassis then the probe plate to input 7
3. The spindle itself is earthed to mains earth
4. All seemed to work as Acorn was responding to the touch off (Z axis)
5. About 2 min later I was trying to set X,Y axis touch off the using a second touch off plate for testing when I smelt electrical burning and powered down
You have suggested to place a link between Power Supply Common (0v) to ground (Main’s earth)
1. I would have assumed from the spindle chassis (effectively mains earth) to Acorn common is exactly the same as your suggestion?
2. There is no earth link to common described in the hook up diagram?
3. As there are multiple power supplies in the installation all commons have been tied together so you are suggesting tying them all to mains earth?
Thanks in advance.
"This blows when there is a voltage difference between com and ground. Try connecting a jumper between the 0V common and ground on the power supply. With the Jumper, the Acorn might function, even with the blown Ferrite bead (FB6)"
I am wanting to understand the issue some more so I either do not do further damage to the existing PCB or the potential replacement PCB.
Setup
1. This issue happened when I started to commission my touch probe (plate).
2. My spindle shaft is earthed through its chassis, so I connected Acorn common (0v) to the spindle chassis then the probe plate to input 7
3. The spindle itself is earthed to mains earth
4. All seemed to work as Acorn was responding to the touch off (Z axis)
5. About 2 min later I was trying to set X,Y axis touch off the using a second touch off plate for testing when I smelt electrical burning and powered down
You have suggested to place a link between Power Supply Common (0v) to ground (Main’s earth)
1. I would have assumed from the spindle chassis (effectively mains earth) to Acorn common is exactly the same as your suggestion?
2. There is no earth link to common described in the hook up diagram?
3. As there are multiple power supplies in the installation all commons have been tied together so you are suggesting tying them all to mains earth?
Thanks in advance.