Re: Contactor Recommendations

Posted: Wed Apr 14, 2021 10:59 am
by martyscncgarage
tuffduck wrote: Tue Apr 13, 2021 8:18 pm Hi,
Power supply - 48v DC 20amps
Drives - steppers 1400oz 4.6 amps
Drivers - Gecko 201x
Are you using the contactor as an Estop Contactor?
You will want a contactor with DC voltage contact ratings. I would run both the DC- and the DC+ across a contact.
Eaton Moeller DIL or XTC series contactors are good, Schneider Telemecanique LC1DT series, etc....
20Amp contact rating would be fine.
Just remember to look at the coil voltage you intend to use. I would recommend 24VDC....

Hope that helps
Marty

Re: Contactor Recommendations

Posted: Wed Apr 14, 2021 9:49 pm
by tuffduck
I would like to use this as an estop contactor to shut down the spindle and steppers but leave acorn running, so that I can resume a program. Thanks

Re: Contactor Recommendations

Posted: Thu Apr 15, 2021 10:22 am
by martyscncgarage
tuffduck wrote: Wed Apr 14, 2021 9:49 pm I would like to use this as an estop contactor to shut down the spindle and steppers but leave acorn running, so that I can resume a program. Thanks
Look at the Acorn SYSTEM schematic in the Acorn Schematic set. It shows what you are wanting to accomplish

Re: Contactor Recommendations

Posted: Fri Apr 16, 2021 10:44 pm
by tuffduck

Re: Contactor Recommendations

Posted: Fri Apr 16, 2021 10:57 pm
by martyscncgarage
tuffduck wrote: Fri Apr 16, 2021 10:44 pm Would something like this work.

https://www.se.com/ww/en/product/LC1DT2 ... 4v-dc-low/
Yes. Same one Centroid uses and sells other than it's 24vdc

Re: Contactor Recommendations

Posted: Sat Apr 17, 2021 6:09 pm
by tuffduck
Thank you. Would you also recommend the Quencharc?

Re: Contactor Recommendations

Posted: Sat Apr 17, 2021 6:20 pm
by martyscncgarage
tuffduck wrote: Sat Apr 17, 2021 6:09 pm Thank you. Would you also recommend the Quencharc?
Always.