Hi Folks,
Here is Hyundai/Mazak 8G gang tool lathe with Acorn 12, DMM Dyn4 1.0kW motors, Siemens 360V 15hp spindle motor, and DuraPulse GS4 20hp VFD. I did all wiring with star ground coming to the ground plate. At this point no spindle encoder connected, yet.
The problem is--the spindle speed deviates and also, whenever I put M00 with 0 speed the spindle actually runs at some 95--100rpm with the 0-10v line shield not grounded. Once I ground the shield the RPM jumps to 200--205. Before I was running all VFD controls with 0-10V line in one shielded multiwire cable. Now I tried running the 0-10V in a separate shielded 2 conductor cable--no change. I tried to separate the power, logic, and analog rails--no changes. The different points of grounding--no changes.
The machine has an enormous power transformer (in separate compartment) with 3phase 220V in, giving out 3phase 360V, 3phase 220V, and 110V. Originally, I was feeding the spindle VFD with 360V, DMM with 3phase 220V, and Acorn with 110V, coming from that transformer. Thinking of reducing crosstalk I rewired the DMM to one phase 110V feeding off the wall. The same with Acorn. No any changes. Other than that everything works as it should and machine runs parts beautifully.
Do I miss something? The problem in short--when I leave the 0-10V line shield ungrounded the M00 with 0 RPM runs at 95-100RPM with some deviation, when I ground the shield it runs at 200--205RPM.
Best, M
Acorn 12 Spindle Speed Problem
Moderator: cnckeith
-
- Posts: 3095
- Joined: Tue Mar 22, 2016 10:03 am
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: Yes
- CNC Control System Serial Number: 100505
100327
102696
103432
7804732B977B-0624192192 - DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Boston, MA
- Contact:
Re: Acorn 12 Spindle Speed Problem
Ground the shield and add a 0.1 microfarad capacitor across the analog output lines from the Acorn. You will also probably need to adjust the VFD parameters as well. Search for previous discussions on VFD adjustments.
Cheers,
Tom
Confidence is the feeling you have before you fully understand the situation.
I have CDO. It's like OCD, but the letters are where they should be.
Tom
Confidence is the feeling you have before you fully understand the situation.
I have CDO. It's like OCD, but the letters are where they should be.
-
- Posts: 60
- Joined: Sun Dec 08, 2013 1:42 am
- Allin1DC CNC Controller: Yes
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC11: Yes
- CPU10 or CPU7: No
Re: Acorn 12 Spindle Speed Problem
Awesome! Thanks! It makes perfect sense and did it!
-
- Posts: 9914
- Joined: Tue Mar 28, 2017 12:01 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Location: Mesa, AZ
Re: Acorn 12 Spindle Speed Problem
Did it resolve your issue?
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
We can't "SEE" what you see...
Mesa, AZ
-
- Posts: 60
- Joined: Sun Dec 08, 2013 1:42 am
- Allin1DC CNC Controller: Yes
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC11: Yes
- CPU10 or CPU7: No
Re: Acorn 12 Spindle Speed Problem
Yes, thanks! Will try to return DMM wiring to 220v 3phase and see.
Best, M
-
- Posts: 10
- Joined: Sun Sep 29, 2019 6:31 am
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 780473492883-0621192173
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Re: Acorn 12 Spindle Speed Problem
Which bit resolved the issue? Grounding the shield or the capacitor?