Hey guys,
i want to be safe but not overkill. currently ordering breakers e stop contactor etc and just want to make sure i order the correct parts..
system background Bridgeport BOSS
2 hp spindle motor using a FMX TD 400 3 HP VFD with a 10.5A output ( will be running 220 single phase input )
3 DMM Dyn4 750 watt servos ( will be running at 220 volts )
so i believe i need 3 20 amp dual pole breakers for the servos and a 15 amp double pole breaker for the spindle
and a 75 amp contactor ? is this over kill ? what do you think the system would really draw as i need to run a breaker and outlet from the electric box as well
just want to be sure i order the correct parts
thanks ! Joe
Acorn DMM Power requrement sanity check
Moderator: cnckeith
-
- Posts: 40
- Joined: Wed Aug 14, 2019 11:29 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: many
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: Yes
- Location: New Jersey
- Contact:
-
- Posts: 40
- Joined: Wed Aug 14, 2019 11:29 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: many
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: Yes
- Location: New Jersey
- Contact:
Re: Acorn DMM Power requrement sanity check
one last thing.. maybe someone can recommend a nice terminal block for the main power.. thanks !
-
- Posts: 40
- Joined: Wed Aug 14, 2019 11:29 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: many
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: Yes
- Location: New Jersey
- Contact:
Re: Acorn DMM Power requrement sanity check
looking a little closer at the DMM videos, do i need a contactor per DYN4 ? and they are showing a 20 amp circuit breaker followed by a 12 amp contactor.. so power ----- circuit breaker ------ contactor -------- DYN4
thanks in advanced
Joe
thanks in advanced
Joe
Last edited by RaptorMachine on Wed Feb 10, 2021 8:41 pm, edited 1 time in total.
-
- Posts: 3101
- Joined: Tue Mar 22, 2016 10:03 am
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: Yes
- CNC Control System Serial Number: 100505
100327
102696
103432
7804732B977B-0624192192 - DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Boston, MA
- Contact:
Re: Acorn DMM Power requrement sanity check
I would say the servo breakers are properly sized to prevent damage to the motors and drives, but you will NEVER see a combined load of 60 amps from them. A 30A main disconnect (or 45A) with a 30A main breaker should be more than enough for that system.
Cheers,
Tom
Confidence is the feeling you have before you fully understand the situation.
I have CDO. It's like OCD, but the letters are where they should be.
Tom
Confidence is the feeling you have before you fully understand the situation.
I have CDO. It's like OCD, but the letters are where they should be.
-
- Posts: 40
- Joined: Wed Aug 14, 2019 11:29 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: many
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: Yes
- Location: New Jersey
- Contact:
Re: Acorn DMM Power requrement sanity check
thanks for the reply Tom,
so a 30 amp main to a 30 amp contactor to 3 20 amp breakers for the individual servo drives ? or run separate contactors for each servo drive ?
joe
-
- Posts: 3101
- Joined: Tue Mar 22, 2016 10:03 am
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: Yes
- CNC Control System Serial Number: 100505
100327
102696
103432
7804732B977B-0624192192 - DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Boston, MA
- Contact:
Re: Acorn DMM Power requrement sanity check
I'd probably run a single contactor since you'd never want to control just a single drive.
Cheers,
Tom
Confidence is the feeling you have before you fully understand the situation.
I have CDO. It's like OCD, but the letters are where they should be.
Tom
Confidence is the feeling you have before you fully understand the situation.
I have CDO. It's like OCD, but the letters are where they should be.
-
- Posts: 9914
- Joined: Tue Mar 28, 2017 12:01 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Location: Mesa, AZ
Re: Acorn DMM Power requrement sanity check
Yes, one estop contactor for 3 750W servos is fine.
I believe individual breakers are overkill. That's your call. Did you take a look at the FADAL TRM project I did?
I used a line reactor and per DMM's suggestion, I used a regenerative resistor on the non-counterbalanced Z axis to cure a drive fault problem when the Z axis was coming down. Between the two, made me a believer in using them.
Marty
I believe individual breakers are overkill. That's your call. Did you take a look at the FADAL TRM project I did?
I used a line reactor and per DMM's suggestion, I used a regenerative resistor on the non-counterbalanced Z axis to cure a drive fault problem when the Z axis was coming down. Between the two, made me a believer in using them.
Marty