Hi,
Don't see the answers to this in the documentation. I don't have the Acorn board available at this location, so I can't fire up the software to root around in the settings / experiment ...
Enable outputs:
When are these active, whenever the system is reset? Do they remain enabled on e-stop input (IN8) and / or the software estop on the VCP?
E-stop:
On the standard connections schematic, there is an optional e-stop contactor output on the OUT1 relay. How does this function? Does it AND together the E-stop input (IN8) and the red software button on the VCP?
VFD Reset:
How does the VFD reset output (relay board OUT6) work? Momentary out put, continuous? what software actions drive it's operation?
Thank You.
Clarification of Enable, E-stop output
Moderator: cnckeith
-
- Posts: 34
- Joined: Thu Feb 28, 2019 12:05 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: Yes
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Clarification of Enable, E-stop output
------------
Mark
Mark
-
- Posts: 2187
- Joined: Sat Nov 18, 2017 2:32 pm
- Acorn CNC Controller: Yes
- Plasma CNC Controller: No
- AcornSix CNC Controller: Yes
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: Acorn 238
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Bergland, MI, USA
- Contact:
Re: Clarification of Enable, E-stop output
I'll take a whack at these questions, but please remember that my most recent testing is with a beta version of CNC12 v14 and a version 4 IO board with the LED's. The actions may or may not be different using CNC12 v12.
Enable Outputs: On with the controller, off with ESTOP or RESET press
ESTOP Output: Comes on once the software has booted and there are no other "alarms" (limit, reset, drive or vfd fault) I use as "Master Enable" for contactors, other relays to enable servos, etc.
VFD Reset: I have not tested this because I always use a power cycle but you can easily when you are back at your machine.
Enable Outputs: On with the controller, off with ESTOP or RESET press
ESTOP Output: Comes on once the software has booted and there are no other "alarms" (limit, reset, drive or vfd fault) I use as "Master Enable" for contactors, other relays to enable servos, etc.
VFD Reset: I have not tested this because I always use a power cycle but you can easily when you are back at your machine.