Retrofit My Build Looking at Switching from Mach4 to Centroid System
Moderator: cnckeith
-
- Posts: 57
- Joined: Wed Oct 16, 2024 4:15 pm
- Acorn CNC Controller: No
- Plasma CNC Controller: No
- AcornSix CNC Controller: Yes
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 0008DC111213-0116240167
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Re: Retrofit My Build Looking at Switching from Mach4 to Centroid System
I’m slowly getting everything hooked up to my AcornSIX. As I’ve probably made pretty clear electronics are not my forte and the VFD is confusing me.
This is the unit I have https://tinyurl.com/yc8fjmds
Here is a link to the manual for it https://tinyurl.com/3k5zkmr5
The next couple picture links to my album are how my MOLLEM VFD was hooked up to the ESS/MB3. The nomenclature for the MB3 is different from the Acorn and I am lost.
I am using this schematic: https://www.centroidcnc.com/dealersuppo ... 158.r3.pdf
If there is a better schematic to follow I'm all for it.
Obviously I can change any connections at the VFD. I want to hook this thing up the best way to utilize everything built into the VFD so any help would be greatly appreciated.
This is the unit I have https://tinyurl.com/yc8fjmds
Here is a link to the manual for it https://tinyurl.com/3k5zkmr5
The next couple picture links to my album are how my MOLLEM VFD was hooked up to the ESS/MB3. The nomenclature for the MB3 is different from the Acorn and I am lost.
I am using this schematic: https://www.centroidcnc.com/dealersuppo ... 158.r3.pdf
If there is a better schematic to follow I'm all for it.
Obviously I can change any connections at the VFD. I want to hook this thing up the best way to utilize everything built into the VFD so any help would be greatly appreciated.
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 529
- Joined: Thu Apr 14, 2022 2:46 pm
- Acorn CNC Controller: No
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: No
- CNC11: No
- CPU10 or CPU7: No
Re: Retrofit My Build Looking at Switching from Mach4 to Centroid System
From reading the manual, I am not sure whether or not you will need to connect +24 VDC to the VFD terminal labelled +24V. Does it supply voltage of its own? Using a multimeter set to 200VDC (or DC volts if it is autoranging), is there +24V across the VFD's +24V and COM terminals when it is powered on?
If so, then do not connect anything to +24V terminal and use the VFD's COM terminal as the connection for the VFD COMMON signals on S15158.
You'll have to check VFD parameters F4-00, F4-01, F4-02, and F4-03 to see what functions are assigned to the digital inputs (terminals labelled Sx).
I am guessing since there are only two digital signals shown from the MB3 that the VFD would be set to have S1 and S2 as FWD and REV and the enable is controlled by the level of the analog signal.
It is quite possible that they left the VFD on default input settings so S3 would then be FAULT RESET.
Regardless of the current input settings, to match our schematic S15158, you will want the VFD parameters to be:
F4-00 = 1 which then gets the signal SPIN_FORWARD
F4-01 = 2 which then gets signal SPIN_REVERSE
F4-02 = 9 which then gets signal VFD_RESET
F4-03 = 0 and it will left disconnected.
F5-02 = 38 and you should wire SpindleOk to VFD terminal TB and the corresponding GND to VFD terminal TA (labelled FAULT COM on Centroid drawing S15158). This is using the drive's relay output to act as a drive fault signal.
You may need to adjust the settings of F4-38 to get the correct input behavior. I believe it should be set to 00111 to make S1, S2, and S3 active when the circuit is closed.
For the analog signals, copy the MB3 diagram:
Acorn's ANALOG OUT to drive's AI1
Acorn\s Analog GND to drive's GND
If so, then do not connect anything to +24V terminal and use the VFD's COM terminal as the connection for the VFD COMMON signals on S15158.
You'll have to check VFD parameters F4-00, F4-01, F4-02, and F4-03 to see what functions are assigned to the digital inputs (terminals labelled Sx).
I am guessing since there are only two digital signals shown from the MB3 that the VFD would be set to have S1 and S2 as FWD and REV and the enable is controlled by the level of the analog signal.
It is quite possible that they left the VFD on default input settings so S3 would then be FAULT RESET.
Regardless of the current input settings, to match our schematic S15158, you will want the VFD parameters to be:
F4-00 = 1 which then gets the signal SPIN_FORWARD
F4-01 = 2 which then gets signal SPIN_REVERSE
F4-02 = 9 which then gets signal VFD_RESET
F4-03 = 0 and it will left disconnected.
F5-02 = 38 and you should wire SpindleOk to VFD terminal TB and the corresponding GND to VFD terminal TA (labelled FAULT COM on Centroid drawing S15158). This is using the drive's relay output to act as a drive fault signal.
You may need to adjust the settings of F4-38 to get the correct input behavior. I believe it should be set to 00111 to make S1, S2, and S3 active when the circuit is closed.
For the analog signals, copy the MB3 diagram:
Acorn's ANALOG OUT to drive's AI1
Acorn\s Analog GND to drive's GND
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 57
- Joined: Wed Oct 16, 2024 4:15 pm
- Acorn CNC Controller: No
- Plasma CNC Controller: No
- AcornSix CNC Controller: Yes
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 0008DC111213-0116240167
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Re: Retrofit My Build Looking at Switching from Mach4 to Centroid System
You rock! Sorry for the slow reply, just finished 3 12 hour shifts and haven't had a chance to get back in the shop. Hopefully I can get to this today and get this finished up!centroid467 wrote: ↑Mon Nov 04, 2024 3:00 pm From reading the manual, I am not sure whether or not you will need to connect +24 VDC to the VFD terminal labelled +24V. Does it supply voltage of its own? Using a multimeter set to 200VDC (or DC volts if it is autoranging), is there +24V across the VFD's +24V and COM terminals when it is powered on?
If so, then do not connect anything to +24V terminal and use the VFD's COM terminal as the connection for the VFD COMMON signals on S15158.
You'll have to check VFD parameters F4-00, F4-01, F4-02, and F4-03 to see what functions are assigned to the digital inputs (terminals labelled Sx).
I am guessing since there are only two digital signals shown from the MB3 that the VFD would be set to have S1 and S2 as FWD and REV and the enable is controlled by the level of the analog signal.
It is quite possible that they left the VFD on default input settings so S3 would then be FAULT RESET.
Regardless of the current input settings, to match our schematic S15158, you will want the VFD parameters to be:
F4-00 = 1 which then gets the signal SPIN_FORWARD
F4-01 = 2 which then gets signal SPIN_REVERSE
F4-02 = 9 which then gets signal VFD_RESET
F4-03 = 0 and it will left disconnected.
F5-02 = 38 and you should wire SpindleOk to VFD terminal TB and the corresponding GND to VFD terminal TA (labelled FAULT COM on Centroid drawing S15158). This is using the drive's relay output to act as a drive fault signal.
You may need to adjust the settings of F4-38 to get the correct input behavior. I believe it should be set to 00111 to make S1, S2, and S3 active when the circuit is closed.
For the analog signals, copy the MB3 diagram:
Acorn's ANALOG OUT to drive's AI1
Acorn\s Analog GND to drive's GND
1 user liked this post
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 57
- Joined: Wed Oct 16, 2024 4:15 pm
- Acorn CNC Controller: No
- Plasma CNC Controller: No
- AcornSix CNC Controller: Yes
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 0008DC111213-0116240167
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Re: Retrofit My Build Looking at Switching from Mach4 to Centroid System
Ok I have most of those connected but I realized that the analog out1 and ground for it aren’t mentioned. Would those still be the A1 and GND I had the analogs connected to on the MB3?
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 3376
- Joined: Tue Mar 22, 2016 10:03 am
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: Yes
- CNC Control System Serial Number: 100505
100327
102696
103432
7804732B977B-0624192192 - DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Boston, MA
- Contact:
Re: Retrofit My Build Looking at Switching from Mach4 to Centroid System
Analog out from the VFD will not be used. Some of the other Centroid controls have an analog input where this could be used for a spindle load meter. Unfortunately, the Acorn does not have this.
As far as A1 goes, this is more likely AI (Analog Input) and where the 0-10V output from the Acorn goes.
As far as A1 goes, this is more likely AI (Analog Input) and where the 0-10V output from the Acorn goes.
Cheers,
Tom
Confidence is the feeling you have before you fully understand the situation.
I have CDO. It's like OCD, but the letters are where they should be.
Tom
Confidence is the feeling you have before you fully understand the situation.
I have CDO. It's like OCD, but the letters are where they should be.
1 user liked this post
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 57
- Joined: Wed Oct 16, 2024 4:15 pm
- Acorn CNC Controller: No
- Plasma CNC Controller: No
- AcornSix CNC Controller: Yes
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 0008DC111213-0116240167
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Re: Retrofit My Build Looking at Switching from Mach4 to Centroid System
I probably asked that wrong but your answer was what I was looking for Thank you.tblough wrote: ↑Tue Nov 05, 2024 8:53 pm Analog out from the VFD will not be used. Some of the other Centroid controls have an analog input where this could be used for a spindle load meter. Unfortunately, the Acorn does not have this.
As far as A1 goes, this is more likely AI (Analog Input) and where the 0-10V output from the Acorn goes.
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 57
- Joined: Wed Oct 16, 2024 4:15 pm
- Acorn CNC Controller: No
- Plasma CNC Controller: No
- AcornSix CNC Controller: Yes
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 0008DC111213-0116240167
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Re: Retrofit My Build Looking at Switching from Mach4 to Centroid System
I just realized that to do this right I probably need to connect my e-stop but also to really do it right I need a contactor. The one I had when it was factory is a 3 phase I believe and even though I thought I took good pictures and notes before ripping the cabinet apart I couldn't get it connected the same again.
What contactor would work? I have a separate 24v power supply in the cabinet for powering my laser and it should have plenty of power to trigger it.
What contactor would work? I have a separate 24v power supply in the cabinet for powering my laser and it should have plenty of power to trigger it.
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 252
- Joined: Wed Jan 01, 2020 2:40 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Re: Retrofit My Build Looking at Switching from Mach4 to Centroid System
Looks like the one in your photo is a 24VDC coil 3 pole contactor. You should be able to use for single phase. https://baomain.com/products/cjx2-1810. There should be a label on the side with more information to verify it is a 24VDC coil.
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 57
- Joined: Wed Oct 16, 2024 4:15 pm
- Acorn CNC Controller: No
- Plasma CNC Controller: No
- AcornSix CNC Controller: Yes
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 0008DC111213-0116240167
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Re: Retrofit My Build Looking at Switching from Mach4 to Centroid System
Now I guess I need to figure this thing out. I gave up last time and just removed it
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 529
- Joined: Thu Apr 14, 2022 2:46 pm
- Acorn CNC Controller: No
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: No
- CNC11: No
- CPU10 or CPU7: No
Re: Retrofit My Build Looking at Switching from Mach4 to Centroid System
The terminals labelled A1 and A2 are going to be for the signal that controls the contactor. Using that website that RogDC suggested, I found this picture which should show where the coil voltage information is. I circled the location in red:
The pairs of L1-T1, L2-T2, and L3-T3 are the main contacts so those are what you would be running the main circuit power through.
1 user liked this post
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
(Note: Liking will "up vote" a post in the search results helping others find good information faster)