Analog Out weirdness, please help <DYN4 as spindle motor>

Post by Measurement10 »

To start, i've read all the threads regarding EMI, proper shielding, grounding, snubbers, etc.

Im using a DYN4/Servo spindle.

When i have the DYN4 analog connected to Acorn's analog (shielded and grounded via drain) i get a strange 0.19V across the terminals. This wreaks havoc on the DYN4. This voltage is not linear. If i feed it 10V i get 10.1V, 5V i get 5.19V. Its a mess. Spindle bench test passes. Tried snubbers, ferrites, no change.

Heres where things get strange. If i unplug the analog, Acorn and DYN4 terminals show 0V on a volt meter. If i plug the analog cable (same cable) into a DC power supply, 0V, voltage offset goes away. I can FULLY control the DYN4 via DC power supply with no voltage anomalies. However, if i take another acorn board and plug the same cable into it, 2nd acorn is outside of the cabinet, not even powered up, but plugged in, voltage offset is back. If i unplug this board from the wall, offset goes away.

What the heck is happening here? Im loosing my mind.


eng199
Posts: 415
Joined: Fri Jan 10, 2014 11:29 am
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: Yes
CNC Control System Serial Number: none
DC3IOB: Yes
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Howard, PA

Re: Analog Out weirdness, please help

Post by eng199 »

The ground / COM is probably slightly different between DYN4 and ACORN. ACORN analog output is not isolated. Your DC power supply probably is. Disconnect the wires between ACORN and DYN4 and measure COM to COM. If it is not the same, the ground wiring needs work.

The analog output may also oscillate, which is not obvious without viewing on an oscilloscope. Measuring using the meter's AC scale may show voltage from oscillation. The AC reading should be 0. Here is a post about analog output oscillation: viewtopic.php?p=46032#p46032


SpacedmanSpiff
Posts: 33
Joined: Mon Nov 09, 2020 6:43 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: oc1c5708fb62-01224202901
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Analog Out weirdness, please help

Post by SpacedmanSpiff »

I ended up redesigning my mill to eliminate the dmm as a spindle drive. I had issues with it faulting out after a stop command and creep after a stop command. Both were solved through plc programming changes...however I found my particular choice if servo and drive to be weak in torque and not sufficient for my application. I also was unable to get the dmm encoder to work with the acorn....never did solve that issue. I think the general consensus was try to avoid dmm as a spindle drive. As a servo I hear good things about them. All the best Sean


Gary Campbell
Posts: 2330
Joined: Sat Nov 18, 2017 2:32 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: Yes
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: Acorn 238
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Bergland, MI, USA
Contact:

Re: Analog Out weirdness, please help

Post by Gary Campbell »

Are you using the recommended 18ga twisted pair (shielded) wire?

Have you installed the often noted 0.10 mfd capacitor across the analog terminals?

Also, I do not have the confidence in DMM products that Sean has. I have been burned by them in too many instances.
GCnC Control
CNC Control & Retrofits
CNC Depot Modular ATC kits
https://www.youtube.com/user/Islaww1/videos


spikee
Posts: 76
Joined: Thu Feb 01, 2024 5:34 am
Acorn CNC Controller: No
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Contact:

Re: Analog Out weirdness, please help

Post by spikee »

This could be either the DMM analog input stage being influenced by acorn or vice versa. Snubbers, etc are not going to solve that. As this is a (slow) analog signal and not a high-frequency changing signal. Another potential issue is that both suppliers are not on the same reference . In that case you get weird offsets between them which might not be fixed and can change due to other influences.

That is one of the reason why i like full digital such as you get with ethercat implementations.


Measurement10
Posts: 79
Joined: Wed Oct 13, 2021 11:58 am
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Analog Out weirdness, please help

Post by Measurement10 »

eng199 wrote: Wed May 15, 2024 8:41 am The ground / COM is probably slightly different between DYN4 and ACORN. ACORN analog output is not isolated. Your DC power supply probably is. Disconnect the wires between ACORN and DYN4 and measure COM to COM. If it is not the same, the ground wiring needs work.

The analog output may also oscillate, which is not obvious without viewing on an oscilloscope. Measuring using the meter's AC scale may show voltage from oscillation. The AC reading should be 0. Here is a post about analog output oscillation: viewtopic.php?p=46032#p46032
As measured:

DYN4 Analog common to Acorn Analog common, 0V
Across Acorn Analog terminals, with DYN4 connected, 0.19V (spindle off)
Acorn Analog common to Acorn H9 Ground, 0.02v
Acorn Analog VOUT to Acorn H9 Common, 0.19V
AC reading for acorn analog out is 0.

These values are all with a snubber in place. Removing snubber makes no difference.
Last edited by Measurement10 on Wed May 15, 2024 1:53 pm, edited 1 time in total.


Measurement10
Posts: 79
Joined: Wed Oct 13, 2021 11:58 am
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Analog Out weirdness, please help

Post by Measurement10 »

SpacedmanSpiff wrote: Wed May 15, 2024 9:01 am I ended up redesigning my mill to eliminate the dmm as a spindle drive. I had issues with it faulting out after a stop command and creep after a stop command. Both were solved through plc programming changes...however I found my particular choice if servo and drive to be weak in torque and not sufficient for my application. I also was unable to get the dmm encoder to work with the acorn....never did solve that issue. I think the general consensus was try to avoid dmm as a spindle drive. As a servo I hear good things about them. All the best Sean
So far the motor has been good. I can use the DMM software to tune the deadzone so the motor comes to a stop. Unfortunately this wont work with non-linear offsets which is what im experiencing. I completely understand your frustration with DMM, however their product works perfectly with a cheap lab power supply, in this case its not their fault.
Last edited by Measurement10 on Wed May 15, 2024 10:29 am, edited 1 time in total.


Measurement10
Posts: 79
Joined: Wed Oct 13, 2021 11:58 am
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Analog Out weirdness, please help

Post by Measurement10 »

spikee wrote: Wed May 15, 2024 9:48 am This could be either the DMM analog input stage being influenced by acorn or vice versa. Snubbers, etc are not going to solve that. As this is a (slow) analog signal and not a high-frequency changing signal. Another potential issue is that both suppliers are not on the same reference . In that case you get weird offsets between them which might not be fixed and can change due to other influences.

That is one of the reason why i like full digital such as you get with ethercat implementations.
Could be. Doesnt look good in the case of Acorn. Centroid should be designing a product that is compatible with this sort of thing. If a cheap DC lab power supply can do better than the expensive acorn board then something is wrong.

I thought of the reference idea and tried grounding the DMM analog neg with no improvement. It seems as if the DYN4 is influencing the Acorn Analog OPAMP in some way i don't understand. Whatever it is it seems its not the best choice from a design standpoint. Ready to get flamed by Centroid employees but sorry not sorry, i shouldn't be having this problem and its going to make recommending this kit difficult.
Last edited by Measurement10 on Wed May 15, 2024 1:53 pm, edited 1 time in total.


Measurement10
Posts: 79
Joined: Wed Oct 13, 2021 11:58 am
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Analog Out weirdness, please help

Post by Measurement10 »

Gary Campbell wrote: Wed May 15, 2024 9:21 am Are you using the recommended 18ga twisted pair (shielded) wire?
Have you installed the often noted 0.10 mfd capacitor across the analog terminals?
Also, I do not have the confidence in DMM products that Sean has. I have been burned by them in too many instances.
As i mentioned i've read all the recommendations and propper practices. Shielded cables with twisted pairs, foil with drains grounded, snubbers, no difference. DMM product works well with DC power supply, problem is Acorn.


tblough
Posts: 3367
Joined: Tue Mar 22, 2016 10:03 am
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: Yes
CNC Control System Serial Number: 100505
100327
102696
103432
7804732B977B-0624192192
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Boston, MA
Contact:

Re: Analog Out weirdness, please help

Post by tblough »

After all best practices have been employed (twisted pair shielded wire, proper grounds, bypass caps, etc.), you might want to look into a signal isolator:

https://www.amazon.com/Isolator-Insulat ... B09TJTCDQ8
Cheers,

Tom
Confidence is the feeling you have before you fully understand the situation.