Spindle fault remove probe from spindle
Moderator: cnckeith
-
- Posts: 73
- Joined: Thu Jan 30, 2020 9:36 am
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 0C1C57072225-0107202806
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Texas
- Contact:
Spindle fault remove probe from spindle
Upgrading from v4.82 to v5.06. v4.82 has worked fine for months. Got v5.06 running X,Y,Z and TT-1 and KC-3 probe appear to work. Spindle will not start because of subject error. Have removed probe from wizard and still same error. I'm guessing I need to change a parameter but can't find a reference. This appears to be my final hurdle. Latest Report attached. (prior to removal of probe in wizard.)
- Attachments
-
- report_0C1C57072225-0107202806_2023-12-21_17-12-02.zip
- (840.26 KiB) Downloaded 11 times
-
- report_0C1C57072225-0107202806_2023-12-21_11-36-45.zip
- (881.96 KiB) Downloaded 17 times
Last edited by DrLocke on Thu Dec 21, 2023 7:30 pm, edited 1 time in total.
-
- Posts: 93
- Joined: Thu Sep 21, 2023 9:24 am
- Acorn CNC Controller: No
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: No
- CNC11: No
- CPU10 or CPU7: No
Re: Spindle fault remove probe from spindle
Your report claims that the tool in the spindle is T10, which is the probe. Is the tool listed in the status bar in the top-right: T10H10?
Domenic
When requesting support READ THIS POST first.
Please ALWAYS post a FRESH report.
(We pride ourselves on providing timely solid technical support but, without good information we may not be able to help and/or reply until such information is posted.)
When requesting support READ THIS POST first.
Please ALWAYS post a FRESH report.
(We pride ourselves on providing timely solid technical support but, without good information we may not be able to help and/or reply until such information is posted.)
-
- Posts: 73
- Joined: Thu Jan 30, 2020 9:36 am
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 0C1C57072225-0107202806
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Texas
- Contact:
Re: Spindle fault remove probe from spindle
It was when I first attempted to start the spindle and I then changed it to tool #1 but that didn't solve the issue.
-
- Posts: 7554
- Joined: Wed Mar 03, 2010 4:23 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: Yes
- CNC Control System Serial Number: none
- DC3IOB: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Contact:
Re: Spindle fault remove probe from spindle
sounds like the probe detect signal has been inverted?
Need support? READ THIS POST first. http://centroidcncforum.com/viewtopic.php?f=60&t=1043
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
-
- Posts: 7554
- Joined: Wed Mar 03, 2010 4:23 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: Yes
- CNC Control System Serial Number: none
- DC3IOB: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Contact:
Re: Spindle fault remove probe from spindle
12-21-2023 0:25:44 9030 SPINDLE FAULT!
(4) 12-21-2023 0:25:44 9033 Reset Initiated, Press Reset to Clear
(4) 12-21-2023 9:00:30 9030 SPINDLE FAULT!
(4) 12-21-2023 9:00:30 4032 Reset Cleared
(4) 12-21-2023 9:00:32 9030 SPINDLE FAULT!
(1) 12-21-2023 9:01:01 204 Exiting CNC...Normal Exit (66)
(1) 12-21-2023 9:01:32 199 CNC Started
(1) 12-21-2023 9:01:40 CNC12 Acorn Mill v5.06
(4) 12-21-2023 9:01:40 9033 Reset Initiated, Press Reset to Clear
(4) 12-21-2023 9:01:46 4032 Reset Cleared
(1) 12-21-2023 9:02:23 407 Z+ limit (#50036) tripped
(1) 12-21-2023 9:02:26 407 Y- limit (#50035) tripped
(1) 12-21-2023 9:02:29 407 X+ limit (#50033) tripped
(1) 12-21-2023 9:17:28 204 Exiting CNC...Normal Exit (66)
(1) 12-21-2023 10:14:44 199 CNC Started
(1) 12-21-2023 10:14:51 CNC12 Acorn Mill v5.06
(4) 12-21-2023 10:14:51 9033 Reset Initiated, Press Reset to Clear
(4) 12-21-2023 10:15:00 4032 Reset Cleared
(1) 12-21-2023 10:15:17 407 Z+ limit (#50036) tripped
(1) 12-21-2023 10:15:19 407 Y- limit (#50035) tripped
(1) 12-21-2023 10:15:21 407 X+ limit (#50033) tripped
(1) 12-21-2023 10:16:45 407 Z+ limit (#50036) tripped
(1) 12-21-2023 10:37:11 8075 WARNING: TOOL TOUCH OFF TRIPPED
(1) 12-21-2023 10:37:12 9077 Tool Touch Off Cleared
(1) 12-21-2023 10:40:51 303 Paused...
(1) 12-21-2023 10:40:52 307 Operator abort: job cancelled
(4) 12-21-2023 10:40:52 8075 WARNING: TOOL TOUCH OFF TRIPPED
(4) 12-21-2023 10:40:52 9077 Tool Touch Off Cleared
(4) 12-21-2023 10:41:26 8075 WARNING: TOOL TOUCH OFF TRIPPED
(4) 12-21-2023 10:41:32 9077 Tool Touch Off Cleared
(4) 12-21-2023 10:41:47 9045 Drawbar Clamped
(4) 12-21-2023 10:43:54 9044 Drawbar Released
(1) 12-21-2023 10:44:30 407 Z+ limit (#50036) tripped
(1) 12-21-2023 10:45:22 407 Z+ limit (#50036) tripped
(1) 12-21-2023 10:45:27 407 Z+ limit (#50036) tripped
(1) 12-21-2023 10:46:38 918 Probe unable to detect surface
(4) 12-21-2023 10:47:23 9045 Drawbar Clamped
(4) 12-21-2023 11:12:28 9044 Drawbar Released
(1) 12-21-2023 11:14:40 907 X axis travel exceeded
(1) 12-21-2023 11:18:49 407 Z+ limit (#50036) tripped
(1) 12-21-2023 11:20:18 407 Z+ limit (#50036) tripped
(1) 12-21-2023 11:20:23 407 Z+ limit (#50036) tripped
(1) 12-21-2023 11:20:28 407 Z+ limit (#50036) tripped
(4) 12-21-2023 11:23:41 9045 Drawbar Clamped
(4) 12-21-2023 11:26:34 9044 Drawbar Released
(1) 12-21-2023 11:30:41 8040 WARNING: PROBE TRIPPED
(1) 12-21-2023 11:33:13 9042 Probe Cleared
(4) 12-21-2023 11:33:20 907 Z axis travel exceeded
(4) 12-21-2023 11:33:20 907 Z axis travel exceeded
(4) 12-21-2023 11:33:20 907 Z axis travel exceeded
(4) 12-21-2023 11:33:47 9045 Drawbar Clamped
(4) 12-21-2023 11:33:48 8040 WARNING: PROBE TRIPPED
(4) 12-21-2023 11:33:48 9042 Probe Cleared
(1) 12-21-2023 11:36:45 Creating report...
(4) 12-21-2023 0:25:44 9033 Reset Initiated, Press Reset to Clear
(4) 12-21-2023 9:00:30 9030 SPINDLE FAULT!
(4) 12-21-2023 9:00:30 4032 Reset Cleared
(4) 12-21-2023 9:00:32 9030 SPINDLE FAULT!
(1) 12-21-2023 9:01:01 204 Exiting CNC...Normal Exit (66)
(1) 12-21-2023 9:01:32 199 CNC Started
(1) 12-21-2023 9:01:40 CNC12 Acorn Mill v5.06
(4) 12-21-2023 9:01:40 9033 Reset Initiated, Press Reset to Clear
(4) 12-21-2023 9:01:46 4032 Reset Cleared
(1) 12-21-2023 9:02:23 407 Z+ limit (#50036) tripped
(1) 12-21-2023 9:02:26 407 Y- limit (#50035) tripped
(1) 12-21-2023 9:02:29 407 X+ limit (#50033) tripped
(1) 12-21-2023 9:17:28 204 Exiting CNC...Normal Exit (66)
(1) 12-21-2023 10:14:44 199 CNC Started
(1) 12-21-2023 10:14:51 CNC12 Acorn Mill v5.06
(4) 12-21-2023 10:14:51 9033 Reset Initiated, Press Reset to Clear
(4) 12-21-2023 10:15:00 4032 Reset Cleared
(1) 12-21-2023 10:15:17 407 Z+ limit (#50036) tripped
(1) 12-21-2023 10:15:19 407 Y- limit (#50035) tripped
(1) 12-21-2023 10:15:21 407 X+ limit (#50033) tripped
(1) 12-21-2023 10:16:45 407 Z+ limit (#50036) tripped
(1) 12-21-2023 10:37:11 8075 WARNING: TOOL TOUCH OFF TRIPPED
(1) 12-21-2023 10:37:12 9077 Tool Touch Off Cleared
(1) 12-21-2023 10:40:51 303 Paused...
(1) 12-21-2023 10:40:52 307 Operator abort: job cancelled
(4) 12-21-2023 10:40:52 8075 WARNING: TOOL TOUCH OFF TRIPPED
(4) 12-21-2023 10:40:52 9077 Tool Touch Off Cleared
(4) 12-21-2023 10:41:26 8075 WARNING: TOOL TOUCH OFF TRIPPED
(4) 12-21-2023 10:41:32 9077 Tool Touch Off Cleared
(4) 12-21-2023 10:41:47 9045 Drawbar Clamped
(4) 12-21-2023 10:43:54 9044 Drawbar Released
(1) 12-21-2023 10:44:30 407 Z+ limit (#50036) tripped
(1) 12-21-2023 10:45:22 407 Z+ limit (#50036) tripped
(1) 12-21-2023 10:45:27 407 Z+ limit (#50036) tripped
(1) 12-21-2023 10:46:38 918 Probe unable to detect surface
(4) 12-21-2023 10:47:23 9045 Drawbar Clamped
(4) 12-21-2023 11:12:28 9044 Drawbar Released
(1) 12-21-2023 11:14:40 907 X axis travel exceeded
(1) 12-21-2023 11:18:49 407 Z+ limit (#50036) tripped
(1) 12-21-2023 11:20:18 407 Z+ limit (#50036) tripped
(1) 12-21-2023 11:20:23 407 Z+ limit (#50036) tripped
(1) 12-21-2023 11:20:28 407 Z+ limit (#50036) tripped
(4) 12-21-2023 11:23:41 9045 Drawbar Clamped
(4) 12-21-2023 11:26:34 9044 Drawbar Released
(1) 12-21-2023 11:30:41 8040 WARNING: PROBE TRIPPED
(1) 12-21-2023 11:33:13 9042 Probe Cleared
(4) 12-21-2023 11:33:20 907 Z axis travel exceeded
(4) 12-21-2023 11:33:20 907 Z axis travel exceeded
(4) 12-21-2023 11:33:20 907 Z axis travel exceeded
(4) 12-21-2023 11:33:47 9045 Drawbar Clamped
(4) 12-21-2023 11:33:48 8040 WARNING: PROBE TRIPPED
(4) 12-21-2023 11:33:48 9042 Probe Cleared
(1) 12-21-2023 11:36:45 Creating report...
Need support? READ THIS POST first. http://centroidcncforum.com/viewtopic.php?f=60&t=1043
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
-
- Posts: 73
- Joined: Thu Jan 30, 2020 9:36 am
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 0C1C57072225-0107202806
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Texas
- Contact:
Re: Spindle fault remove probe from spindle
Posted a new report that shows the fault as most recent action.
Added probe back into the wizard.
Tried inverting the Probe Detect and no change, still faults when attempting to start spindle.
Added probe back into the wizard.
Tried inverting the Probe Detect and no change, still faults when attempting to start spindle.
-
- Posts: 93
- Joined: Thu Sep 21, 2023 9:24 am
- Acorn CNC Controller: No
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: No
- CNC11: No
- CPU10 or CPU7: No
Re: Spindle fault remove probe from spindle
In the wizard, what are the settings for "inhibit spindle when detect is on" for both your probe and tt?
Domenic
When requesting support READ THIS POST first.
Please ALWAYS post a FRESH report.
(We pride ourselves on providing timely solid technical support but, without good information we may not be able to help and/or reply until such information is posted.)
When requesting support READ THIS POST first.
Please ALWAYS post a FRESH report.
(We pride ourselves on providing timely solid technical support but, without good information we may not be able to help and/or reply until such information is posted.)
-
- Posts: 2291
- Joined: Thu Sep 23, 2021 3:49 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 6433DB0446C1-08115074
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Germany
Re: Spindle fault remove probe from spindle
I have both set to yes, this is no problem to run the spindle if probe detect or tripped is not on.dpascucci_support wrote: ↑Fri Dec 22, 2023 10:56 am In the wizard, what are the settings for "inhibit spindle when detect is on" for both your probe and tt?
Uwe
-
- Posts: 93
- Joined: Thu Sep 21, 2023 9:24 am
- Acorn CNC Controller: No
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: No
- CNC11: No
- CPU10 or CPU7: No
Re: Spindle fault remove probe from spindle
Right, but if the TT is set to inhibit the spindle while detect is on, it will trip the same fault "Remove probe from spindle" even though the issue lies in the TT being connected.
Domenic
When requesting support READ THIS POST first.
Please ALWAYS post a FRESH report.
(We pride ourselves on providing timely solid technical support but, without good information we may not be able to help and/or reply until such information is posted.)
When requesting support READ THIS POST first.
Please ALWAYS post a FRESH report.
(We pride ourselves on providing timely solid technical support but, without good information we may not be able to help and/or reply until such information is posted.)
-
- Posts: 73
- Joined: Thu Jan 30, 2020 9:36 am
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 0C1C57072225-0107202806
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Texas
- Contact:
Re: Spindle fault remove probe from spindle
Thank you, thank you, thank you. Changed TT to NOT inhibit and looking good!
Merry Christmas!
Merry Christmas!