(Solved) acorn PLC programming change. For dyn4 servo spindle control.
- CNC Control System Serial Number: oc1c5708fb62-01224202901
I am running a DMM dyn4 for a spindle. ACORN commands this just fine with exception of manual control. If i am over 3000 rpm and hit the Spin Stop button ACORN set analog to zero and disables VFD enable. This causes the spindle to coast to a stop and produces and over volt issue with the DYN4.
i can command M3/M4 at full RPM without difficulty. As long as the enable is on or the RPM is less than 2500 rpm the DYN4 can handle it without issue.
so I need to do one of 2 things
A. delay the VFD disable long enough to allow the spindle to stop.
B. set the RPM down sufficiently to allow DYN4 to absorb the voltage from coasting to a stop.
The VFD enable sequence is still pretty murky to me. However I think I have the set down option figgered out.
Can a PLC guru take a look and critique the code below ?
StandardSpindleStage
IF (SpindleEnableOut_M || SpinStart_M ) && !SpinStop_M
THEN SET SpindleEnableOut_M
IF !((SpindleEnableOut_M || SpinStart_M ) && !SpinStop_M) THEN RST SpindleEnableOut_M
IF SpindleEnableOut_M THEN (VFDEnable_O)
IF SpindleEnableOut_M && !SpindleDirectionOut_M && SpindleBrakeTimer THEN (SpinFWD)
IF SpindleEnableOut_M && SpindleDirectionOut_M && SpindleBrakeTimer THEN (SpinREV), (VFDDirection_O)
IF !SpindleEnableOut_M &&TwelveBitSpeed_W<2500 then (DoSpindleStop)
IF !SpindleEnableOut_M && TwelveBitSpeed_W >2500 THEN (TwelveBitSpeed_W =1000)
IF TwelveBitSpeed_W =1000 THEN set T99
IF !SpindleEnableOut_M && T99 then (DoSpindleStop)
;IF !SpindleEnableOut_M THEN (DoSpindleStop)
Thanks and All the best
Sean
Sean
Last edited by SpacedmanSpiff on Sun Nov 22, 2020 6:56 pm, edited 1 time in total.
Re: acorn PLC programming change.
While it is reasonable to assume that "DoSpindleStop" is a thing that stops the spindle, that is not the case. It is just a status flag used in some parts of the CNC12 software to indicate whether the spindle is running or not.
Actually stopping the spindle is done by the PLC, when it turns off the SpinFWD or SpinREV output relay.
Also, "TwelveBitSpeed_W" is the number sent to the 12-bit DAC to generate the 0-10V signal. It ranges from 0 to 4095, regardless of how many RPM your spindle happens to turn when the PLC sends 10V to the drive. Suppose that your maximum RPM is 8000: then 2500 RPM would require 10V * 2500/8000 = 3.125V, and "TwelveBitSpeed_W" would be 0.3125*4095 = 1280.
I would not bother trying to make it dependent on the RPM command. That is unnecessarily convoluted.
In short, instead of using coil-style outputs for SpinFwd and SpinRev, use SET commands to turn them on when the spindle should start and run. Then, when SpindleEnableOut_M turns off, start a timer, giving it a suitable setpoint (maybe 2000ms). When SpindleEnableOut_M turns on, cancel that timer. When the timer reaches its setpoint, RST SpinFwd and SpinRev.
That way, the standard speed-control logic will manage the analog output -- reducing it to zero when SpindleEnableOut_M turns off -- but the modified start/stop logic will maintain the drive enable long enough for the drive to decelerate the motor.
I am still assuming here that you would get the same fault condition if you ran:
M3 S4500
and then stopped the spindle with:
M5
I assume that, because there is no difference, in terms of PLC logic, between starting and stopping the spindle in manual mode with Spin Start and Spin Stop; and starting and stopping the spindle in auto mode with M3 and M5.
M3 S4500
M5
Ok I think I have a murky understanding of what you are attempting to teach.
Yes M5 generates the same fault. I was not ramping the RPM up in MDI high enough to set the fault on the DYN4.
I ruminated on your suggestion pretty much all day. I agree that you would be able to set a timer and etc....however what do you think of this idea ?
moving the line that resets the VFD enable out memory bit to the end of the stage. That would allow the spinforward or backwards command to accomplish the speed control and then shut the VFD enable down the next loop through......Nope. still need the timer as we are humming along at mhz....
OK, timer it is.
THEN SET SpindleEnableOut_M, SET (VFDEnable_O)
IF !((SpindleEnableOut_M || SpinStart_M ) && !SpinStop_M) THEN RST SpindleEnableOut_M, set VFDdisableTimer_T
IF !SpindleEnableOut_M && VFDdisableTimer_T THEN RST(VFDEnable_O), RST VFDdisableTimer_T, (DoSpindleStop)
thoughts and critiques welcome.
and thank you for your time and effort.
Sean
OK, timer it is.
Sean
Don't bother trying to rewrite the code that manages SpindleEnableOut_M. Just work with it after the standard logic has turned it on and off.
Does your system use the output named "VFDEnable_O" to send the run command to the drive? Or does it use the output named "SpinFWD", and perhaps also the output named "SpinREV"? Unfortunately, the code in "StandardSpindleStage" is trying to do spindle control in at least two different ways simultaneously, so it is a little convoluted.
When you use SET and RST, the target bit does not have parentheses around it.
You need to assign a preset time (number of milliseconds) to the timer.
Appending "Timer" and appending "_T" are two different ways of showing readers that a token is a timer. It is redundant to use both.
IF SpindleEnableOut_M THEN SET VFDEnable_O, RST VFDDisableTimer
IF SpindleEnableOut_M && !SpindleDirectionOut_M && SpindleBrakeTimer THEN SET SpinFWD
IF SpindleEnableOut_M && SpindleDirectionOut_M && SpindleBrakeTimer THEN SET SpinREV, SET VFDDirection_O
IF !SpindleEnableOut_M THEN (DoSpindleStop), VFDDisableTimer = 2000, SET VFDDisableTimer
IF VFDDisableTimer THEN RST VFDEnable_O, RST SpinFWD, RST SpinREV, RST VFDDirection_O
Dear Cncsnw,
Thank you much !!
All is well in my world at the moment. I am goofing with alternative code just to further my understanding so again thank you for providing that sample !
Sean
Thank you much !!
Sean
Re: (Solved) acorn PLC programming change. For dyn4 servo spindle control.
Thanks for this! This fixed my issue as well (but I'm a bit disappointed in myself that I couldn't figure out the PLC programming.)
Pete
Pete
Follow my progress on YouTube
- Plasma CNC Controller: Yes
Pete, have you tried rigid tapping yet? Have you done enough yet to test the performance of the spindle?Pete Rondeau wrote: ↑Tue Dec 08, 2020 9:28 pm Thanks for this! This fixed my issue as well (but I'm a bit disappointed in myself that I couldn't figure out the PLC programming.)
Pete
Those of you with Dyn4, was it suggested that you put a regenerative resistor on the T3 terminals of DYN4?
Excerpt from the DYN4 manual:
Hey Marty,
No, I haven't tried tapping. I still need to add a spindle encoder before I can do that.
I asked about the resistor twice. Once when I purchased the components and a second time when I was having trouble tuning it. Both times I was told it shouldn't need it. Based on my experience with other drives and the results I was getting I decided it was worth a try. I obtained one from Mouser based off of their specs rather than having the delay of customs.
Now,my Mitsubishi drives all have a parameter you can tweak if you add an external resistor so I kinda expected the same thing here but I see no option to tell the drive to make use of the resistor. It doesn't feel to me that adding the resistor has made any change whatsoever.
Pete
Pete
The resistor is for dumping energy. It is automatically activated by the drive. It is also used if the incoming voltage is higher than "normal"Pete Rondeau wrote: ↑Wed Dec 09, 2020 10:33 am Hey Marty,
Pete
The other poster said he was having Over Voltage faults when shutting down the servo from a high speed....that is why I suggested it.
DYN4 has an Encoder output that is compatible with the Acorn Encoder input. IF you belted the spindle motor to the spindle at 1:1 with a timing belt, then in "theory" it should work. I tried this on a small lathe. 750W servo. Tuning the setup was challenging. It was much easier to go the traditional route of a small 3 phase motor and VFD, along with an encoder belted to the spindle at 1:1
Many people try the DMM Dyn4/Servo solution in hopes of either saving themselves the time and trouble of fitting up a traditional encoder to the spindle correctly or a "C axis" I am interested in seeing a video of someone who successfully implemented it with a write up. I want to see the machine peck tap in a block of machinable wax....