Wizard will not allow All-Limits - PLC compile error

Posted: Mon Feb 25, 2019 8:03 pm
by jj80909
I started working on my configuration with the the Acorn Wizard and found that if I select All-Limits for any of the 8 inputs, it will result in a PLC compile error. I am able to configure any of the 8 input to use as All-Homes.

Could this be a bug in the wizard?

Re: Wizard will not allow All-Limits - PLC compile error

Posted: Mon Feb 25, 2019 8:55 pm
by cnckeith
yes, its been covered here on the forum elsewhere,
use homeall and software travel limits, that works.
v4.14 will have the limitall fix.