I'm using an Acorn board to run a router, commanded spindle speed via a VFD with the 0-10V analog output.
By itself, commanding the VFD to a spindle speed via its front panel-mounted pot works fine. It was then reconfigured to instead take the speed command from its analog input. Varying that input with a bench supply varies motor speed as expected.
When connected only to a voltmeter, the Acorn 0-10V analog signal appears good. Commanding 20,000 rpm outputs a stable 9.17V, and other speed commands and voltage outputs line up. The problem: When the Acorn analog output is connected to the analog input on the VFD, the signal gets severely loaded down, to 3.0-3.6V, and is very unstable, jumping around within that range. The VFD tries following the unstable command and I can hear it varying up and down in speed.
I've triple-checked everything and don't see what's wrong. The most obvious is that I miswired it, but since when I command a speed, the VFD does respond, it must be going to the right connections. Also, using a variable bench supply to command a speed works fine, which suggests that the VFD is working properly. It's only when the Acorn is connected does the signal get loaded down.
Looking in the Acorn spec sheet, it says the analog output is capable of 1ma minimum and 10ma maximum. I put a 10K resistor on the output to confirm that and it worked fine.
In the long shot chance that someone has had this issue before, this is happening with a Simphoenix E550 VFD.
Thanks
By itself, commanding the VFD to a spindle speed via its front panel-mounted pot works fine. It was then reconfigured to instead take the speed command from its analog input. Varying that input with a bench supply varies motor speed as expected.
When connected only to a voltmeter, the Acorn 0-10V analog signal appears good. Commanding 20,000 rpm outputs a stable 9.17V, and other speed commands and voltage outputs line up. The problem: When the Acorn analog output is connected to the analog input on the VFD, the signal gets severely loaded down, to 3.0-3.6V, and is very unstable, jumping around within that range. The VFD tries following the unstable command and I can hear it varying up and down in speed.
I've triple-checked everything and don't see what's wrong. The most obvious is that I miswired it, but since when I command a speed, the VFD does respond, it must be going to the right connections. Also, using a variable bench supply to command a speed works fine, which suggests that the VFD is working properly. It's only when the Acorn is connected does the signal get loaded down.
Looking in the Acorn spec sheet, it says the analog output is capable of 1ma minimum and 10ma maximum. I put a 10K resistor on the output to confirm that and it worked fine.
In the long shot chance that someone has had this issue before, this is happening with a Simphoenix E550 VFD.
Thanks
Last edited by kb58 on Tue Oct 24, 2023 6:38 pm, edited 7 times in total.
Previous hobby, building hard core sports cars. See http://midlana.com/ and http://kimini.com/
-
- Posts: 180
- Joined: Tue Jul 11, 2023 12:25 am
- Acorn CNC Controller: Yes
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: San Diego CA
Re: Well nuts, Acorn 10V spindle speed signal loading down
I tried leaving the analog connected but disconnected the FWD line. Surprise, the voltage remained stable at 9.17V, so this may be an EMI issue...
Last edited by kb58 on Tue Oct 24, 2023 6:37 pm, edited 1 time in total.
Previous hobby, building hard core sports cars. See http://midlana.com/ and http://kimini.com/
-
- Posts: 180
- Joined: Tue Jul 11, 2023 12:25 am
- Acorn CNC Controller: Yes
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: San Diego CA
Re: Well nuts, Acorn 10V spindle speed signal loading down
Sure enough, grounding the shield (only) at the control box completely solved it. I admit that I had gotten lax about EMI and it bit me. Strange symptom though, driving down the commanded signal so much. Anyway, thanks for being good listeners, and maybe this will help others.
Previous hobby, building hard core sports cars. See http://midlana.com/ and http://kimini.com/
-
- Posts: 7439
- Joined: Wed Mar 03, 2010 4:23 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: Yes
- CNC Control System Serial Number: none
- DC3IOB: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Contact:
Re: Acorn 10V analog output wonky (Resolved, and not what you thought)
thanks for reporting back.
Need support? READ THIS POST first. http://centroidcncforum.com/viewtopic.php?f=60&t=1043
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
-
- Posts: 728
- Joined: Mon Feb 19, 2018 2:52 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 38D269594F9C-0110180512
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: UK
- Contact:
Re: Acorn 10V analog output wonky (Resolved, and not what you thought)
These Chinese VFDs always seem to skip over any requirement for an EMC filter on the AC input, yet they are not magically able to avoid generating significant switching noise during operation. As a matter of good practice, VFDs should be fitted with a decent quality filter, rather than try to figure out and fix problems after they have occurred. Some of the more industrial products either include an EMC filter in the VFD or suggest the part number of a filter that might enable them to meet industrial (Class A) conducted RFI in a typical installation.
-
- Posts: 382
- Joined: Fri Jan 10, 2014 11:29 am
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: Yes
- CNC Control System Serial Number: none
- DC3IOB: Yes
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Location: Howard, PA
Re: Well nuts, Acorn 10V spindle speed signal loading down
The output was probably oscillating. A sine wave would likely display on an oscilloscope. A meter on VDC will just show the average. Once the output is out of control (continuous oscillation) it is hard to say what the DC average will be. Measuring the output on VAC and getting voltage is another way to determine something isn't right.
-
- Posts: 169
- Joined: Wed Jul 04, 2018 1:32 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC11: Yes
- CPU10 or CPU7: No
Re: Acorn 10V analog output wonky (Resolved, and not what you thought)
I had the exact same problem and it was cured by buying a piece of good quality shielded coax rather than the Radio Shack stuff I was using.
-
- Posts: 180
- Joined: Tue Jul 11, 2023 12:25 am
- Acorn CNC Controller: Yes
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: San Diego CA
Re: Acorn 10V analog output wonky (Resolved, and not what you thought)
Yeah there are a couple things I didn't mention:
1. The VFD user manual does show a filter - but they don't give any specs, making ordering one something of a gamble.
2. During testing, I wondered what would happen if the shield was initially left ungrounded, only grounding it after the spindle speed anomaly started. Interestingly, grounding the shield after the instability started didn't fix the problem. It's as if the VFD was chasing its tail, where once the EMI-induced feedback starts, it's strong enough to get through the shielding, grounded or not.
I'll look into adding an input filter as insurance.
1. The VFD user manual does show a filter - but they don't give any specs, making ordering one something of a gamble.
2. During testing, I wondered what would happen if the shield was initially left ungrounded, only grounding it after the spindle speed anomaly started. Interestingly, grounding the shield after the instability started didn't fix the problem. It's as if the VFD was chasing its tail, where once the EMI-induced feedback starts, it's strong enough to get through the shielding, grounded or not.
I'll look into adding an input filter as insurance.
Previous hobby, building hard core sports cars. See http://midlana.com/ and http://kimini.com/
-
- Posts: 1
- Joined: Mon Sep 11, 2023 10:07 am
- Acorn CNC Controller: Yes
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Re: Acorn 10V analog output wonky (Resolved, and not what you thought)
I have a Astro CNC Knee mill, induction motor whit 1750 rpm, can I used my Teco VFD to control spindle rpm that is low 0 whit gear and hi 5000 rpm
-
- Posts: 180
- Joined: Tue Jul 11, 2023 12:25 am
- Acorn CNC Controller: Yes
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: San Diego CA
Re: Acorn 10V analog output wonky (Resolved, and not what you thought)
Sounds like the makings of a separate thread!jarmachines wrote: ↑Wed Oct 25, 2023 4:19 pm I have a Astro CNC Knee mill, induction motor whit 1750 rpm, can I used my Teco VFD to control spindle rpm that is low 0 whit gear and hi 5000 rpm
Previous hobby, building hard core sports cars. See http://midlana.com/ and http://kimini.com/