**RESOLVED** Tuning Servos

All things related to Centroid Oak, Allin1DC, MPU11 and Legacy products

Moderator: cnckeith

diycncscott

Re: Tuning Servos

Post by diycncscott »

Hi Sky,

Yes, please hook the tachs back up to the drives, and configure the drives for velocity mode. This may involve one or both of the following (Please see your drive documentation for details):
1. Move the analog inputs on the drive to the velocity ref inputs
2. Set the drive(s) velocity mode in parameters


Start with the following settings for the Ajax PID values:

Kd = 0 VERY important
Ka = 0
Kv1 = 25
Kp .01
Ki = .0004

Here is a link to a velocity mode tuning document to help take you from there:

http://ajaxcnc.com/tech/bulletins/techb ... p?TBID=234

It is also available as Tech Bulletin #234 from the tech bulletin section of our site at:
http://ajaxcnc.com/tech/bulletins/


CNCguy
Posts: 28
Joined: Tue Mar 23, 2010 8:54 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC11: No
CPU10 or CPU7: No
Location: Pennsylvania

Re: Tuning Servos

Post by CNCguy »

Notice that Tech Bulletin 234 has been updated, and now emphasizes the oscilloscope tuning feature.
Oscilloscope tuning is real time and allows changing of tuning coefficients "on the fly", this makes tuning very convenient.


Locked