Error in RT-200 Manual wiring diagram?
Moderator: cnckeith
-
- Posts: 3095
- Joined: Tue Mar 22, 2016 10:03 am
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: Yes
- CNC Control System Serial Number: 100505
100327
102696
103432
7804732B977B-0624192192 - DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Boston, MA
- Contact:
Error in RT-200 Manual wiring diagram?
Page 32 (DC wiring) in the RT-200 manual shows Encoder common (blk/red) connected to pin D of the Amphenol connector. The home switch green wire is also connected to pin D on the Amphenol connector. Is this correct?
Cheers,
Tom
Confidence is the feeling you have before you fully understand the situation.
I have CDO. It's like OCD, but the letters are where they should be.
Tom
Confidence is the feeling you have before you fully understand the situation.
I have CDO. It's like OCD, but the letters are where they should be.
-
- Posts: 286
- Joined: Thu Mar 18, 2010 2:24 pm
Re: Error in RT-200 Manual wiring diagram?
That is correct because the return for the power for the encoder signals should be the same as the return for the power for your inputs.
When requesting support, please ALWAYS post a current report. Find out how to take a report from your Acorn, CNC11 or CNC10 system here: https://www.youtube.com/watch?v=Ecvg0VJp1oQ.
If your question is PLC, Macro or program related, please also post a copy of the program or macro as well.
Without the above information we may not be able to help and/or reply until the required information is posted..
If your question is PLC, Macro or program related, please also post a copy of the program or macro as well.