I have always used Sensorless Vector because of it's ability maintain torque at slow speeds. Night and day over V/Hz.
However, I have never used a VFD with analogue input and encoder feedback from the external controller. My gut feeling is that the Sensor-less vector algorithm inside the VFD and the external controller will cause a conflict/problem.
Am I overthinking this and it's perfectly acceptable to use with the Acorn analogue input?
Thanks in Advance!
Clay
VFD question: Will SVC cause issues if you use Acorn 0-10v?(answered)
Moderator: cnckeith
-
- Posts: 595
- Joined: Tue Sep 12, 2017 10:03 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 1030090099
- DC3IOB: Yes
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: No
- Location: Outside Winston-Salem, NC
- Contact:
VFD question: Will SVC cause issues if you use Acorn 0-10v?(answered)
Last edited by frijoli on Wed Sep 20, 2017 7:17 pm, edited 1 time in total.
Clay
near Winston-Salem, NC
unofficial ACORN fb group https://www.facebook.com/groups/897054597120437/
near Winston-Salem, NC
unofficial ACORN fb group https://www.facebook.com/groups/897054597120437/
-
- Posts: 595
- Joined: Tue Sep 12, 2017 10:03 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 1030090099
- DC3IOB: Yes
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: No
- Location: Outside Winston-Salem, NC
- Contact:
Re: VFD question: Will SVC cause issues if you use Acorn 0-10v?
Just FYI, I spoke with a drive specialist for a VFD manufacturer, and the consensus is that you should NOT run a drive in Vector mode if you have an encoder and external controller controlling the speed.
This is what I suspected, but now I am comfortable that it is correct.
Clay
This is what I suspected, but now I am comfortable that it is correct.
Clay
Clay
near Winston-Salem, NC
unofficial ACORN fb group https://www.facebook.com/groups/897054597120437/
near Winston-Salem, NC
unofficial ACORN fb group https://www.facebook.com/groups/897054597120437/
-
- Posts: 9915
- Joined: Tue Mar 28, 2017 12:01 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Location: Mesa, AZ
Re: VFD question: Will SVC cause issues if you use Acorn 0-10v?(answered)
frijoli wrote: ↑Tue Sep 19, 2017 7:07 am I have always used Sensorless Vector because of it's ability maintain torque at slow speeds. Night and day over V/Hz.
However, I have never used a VFD with analogue input and encoder feedback from the external controller. My gut feeling is that the Sensor-less vector algorithm inside the VFD and the external controller will cause a conflict/problem.
Am I overthinking this and it's perfectly acceptable to use with the Acorn analogue input?
Thanks in Advance!
Clay
Most VFDs, can be programmed sensorless vector. The 0-10vdc signal just tells the VFD at what frequency to run at. The VFD still controls the torque at lower RPM.
The spindle encoder is only there for the control to synchronize axis movement with the spindle speed for tapping and threading as well as to display accurate RPM.
The control is not maintaining spindle speed RPM by using the encoder feedback.
Perhaps Centroid staff will add to the discussion.
Marty
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
We can't "SEE" what you see...
Mesa, AZ
-
- Posts: 7
- Joined: Sat Sep 23, 2017 5:50 pm
- Acorn CNC Controller: No
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC11: No
- CPU10 or CPU7: No
Re: VFD question: Will SVC cause issues if you use Acorn 0-10v?(answered)
Yes, I believe the analog signal speed input to the VFD is just a unidirectional, open loop, "pilot" signal to tell the VFD's internal closed loop process what speed to target. No different than manually twiddling a keypad potentiometer when in Sensorless Vector Mode.
-
- Posts: 595
- Joined: Tue Sep 12, 2017 10:03 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 1030090099
- DC3IOB: Yes
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: No
- Location: Outside Winston-Salem, NC
- Contact:
Re: VFD question: Will SVC cause issues if you use Acorn 0-10v?(answered)
That's curious that they would monitor but not control the speed.(closed loop)
If that's the case then SVC is the way to go.
If that's the case then SVC is the way to go.
Clay
near Winston-Salem, NC
unofficial ACORN fb group https://www.facebook.com/groups/897054597120437/
near Winston-Salem, NC
unofficial ACORN fb group https://www.facebook.com/groups/897054597120437/
Re: VFD question: Will SVC cause issues if you use Acorn 0-10v?(answered)
Yes. It is open loop except for CSS applications on Lathes. This is typical on pretty much all non-servo spindle motor/drive system and is the reason for sensorless vector control from the VFD in the first place.
The encoder will not effect the behavior of the VFD because:
1. The encoder only comes back to the control (not the VFD).
2. The VFD will always follow the speed command from the control -it only adjusts it's output to make sure the motor is meeting the speed command of the control (not some other internal reference).
The encoder will not effect the behavior of the VFD because:
1. The encoder only comes back to the control (not the VFD).
2. The VFD will always follow the speed command from the control -it only adjusts it's output to make sure the motor is meeting the speed command of the control (not some other internal reference).
-
- Posts: 9915
- Joined: Tue Mar 28, 2017 12:01 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Location: Mesa, AZ
Re: VFD question: Will SVC cause issues if you use Acorn 0-10v?(answered)
Thanks for the clarification Scott!diycncscott wrote: ↑Mon Sep 25, 2017 7:04 am Yes. It is open loop except for CSS applications on Lathes. This is typical on pretty much all non-servo spindle motor/drive system and is the reason for sensorless vector control from the VFD in the first place.
The encoder will not effect the behavior of the VFD because:
1. The encoder only comes back to the control (not the VFD).
2. The VFD will always follow the speed command from the control -it only adjusts it's output to make sure the motor is meeting the speed command of the control (not some other internal reference).
Marty
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
We can't "SEE" what you see...
Mesa, AZ