Encoder Basics

All things related to Centroid Oak, Allin1DC, MPU11 and Legacy products

Moderator: cnckeith

Post Reply
admin
Site Admin
Posts: 3
Joined: Mon Mar 01, 2010 12:41 pm

Encoder Basics

Post by admin »

Encoders Basics

1. Encoder Type:
Centroid MPU11 based CNC hardware (Oak, Allin1DC, Acorn) requires quadrature, differential encoders which operate on 5VDC. This is the most common type of encoder. Encoders labeled "TTL type" (non differential) are unsuitable, and fortunately are quite rare.

2. Encoder Signals:
a) The following signals must be present and wired: A, /A, B, /B, Z, /Z, +5VDC and ground.
Note: The Z channel is sometimes labeled as I, C or "marker". The "/" symbol may also be
expressed as "-", "NOT" or "!" or a line over the letter, it means the signal is the complement
(opposite) of the channel specified.

b) Signal levels:
The "low" signal level must be less than 0.5 VDC and the "high" signal level must be at least 3.5 VDC.

3. Encoder Resolution:
Typical Machine tool applications (milling machines, lathes and routers) require at least 1000 line (4000 counts per rev) encoders, We recommend and sell 2000 line (8000 counts per rev) encoders. To achieve reasonable accuracy and smooth motion, the encoder/motor/ballscrew configuration must achieve a minimum resolution of 20,000 encoder counts per inch of travel (787 counts/mm). A typical knee mill which uses a 5tpi (turns per inch) ballscrew and has the motors belted at a 1:1 ratio, a 1000 line encoder just meets the minimum counts per inch at 20,000 for smooth motion, this will work however a 2000 line encoder (8000 counts per rev) would be a better choice. Older 250 and 500 line encoders will not work to satisfaction.

some examples

5 turns per inch ballscrew belted at 2:1 with the servo motor = 10 turns of the servo motor per inch of axis travel

10 turns per inch x 4000 counts per rev (1000 line) = 40,000 counts per inch

10 turns per inch x 8000 counts per rev (2000 line) = 80,000 counts per inch.

5 turns per inch ballscrew belted at 1:1 with the servo motor = 5 turns of the servo motor per inch of axis travel

5 turns per inch x 8000 counts per rev = 40,000 counts per inch of axis travel.

4. Encoder wiring MUST be shielded, twisted pair cabling.

Encoder wiring at MPU11:
DB9 Body = Cable Shield

Pin Function
1 No Connection
2 GND
3 Z\
4 A\
5 B\
6 Z
7 A
8 B
9 +5 VDC
db9m-solder side.gif
db9m-solder side.gif (1.3 KiB) Viewed 57023 times
db9m-pin side.gif
db9m-pin side.gif (1.16 KiB) Viewed 57023 times
cnckeith
Posts: 7334
Joined: Wed Mar 03, 2010 4:23 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: Yes
CNC Control System Serial Number: none
DC3IOB: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Contact:

Re: Encoder Basics

Post by cnckeith »

We sell 2000 line (8000 counts per revs) encoders that accept common sized motor encoder shafts on our website. In stock ready to ship for only $175 each.
with connectors. http://ajaxcnc.com/cnc_components.htm

2000 Line Encoder (8000ppr)
This differential encoder not only suppresses noise in the system that can be harmful to encoder signals, but also outputs a quadrature signal giving 8000 counts per revolution of the motor. This is ideal for machines already equipped with DC brush servos to enhance the speed and precision of the machine. Available in 6 mm, 1/4", 3/8", and 1/2" hollow shaft sizes
comp_encoder_large.jpg
comp_encoder_large.jpg (44.95 KiB) Viewed 56952 times
Need support? READ THIS POST first. http://centroidcncforum.com/viewtopic.php?f=60&t=1043
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
Metalstech
Posts: 8
Joined: Thu Mar 18, 2010 1:24 pm
Allin1DC CNC Controller: No
CNC Control System Serial Number: 1015090082
DC3IOB: No
CNC11: No
CPU10 or CPU7: No
Location: Lake Villa,IL

Re: Encoder Basics

Post by Metalstech »

I've got a bit of a discrepancy with the MPU11CBL.S01 file, encoder pin-out labeling and your labeling of the encoder in the basic encoder post.
According to the post, pin 4= A/ and pin 5= B/.
The drawing I mentioned shows pin 4= B/ and pin 5 =A/.
What is the correct labeling?
Thanks, Metalstech
diycncscott

Re: Encoder Basics

Post by diycncscott »

Hi Metalstech,

The pinout in the drawing above is correct. You apparently have an obsolete version of the MPU11Cable document.

Current document
MPU11_AND_CABLES.gif



I have attached the current version of the document in pdf format in the link below:
MPU11_AND_CABLES.pdf
(75.5 KiB) Downloaded 2453 times
MPU11_AND_CABLES.gif
Metalstech
Posts: 8
Joined: Thu Mar 18, 2010 1:24 pm
Allin1DC CNC Controller: No
CNC Control System Serial Number: 1015090082
DC3IOB: No
CNC11: No
CPU10 or CPU7: No
Location: Lake Villa,IL

Re: Encoder Basics

Post by Metalstech »

Fantastic job on keeping up with the Q and A! Thank you all of you guys at AJAX and those out there pitching in with the help.
Thank you,
Metalstech
diycncscott

Re: Encoder Basics

Post by diycncscott »

Hi guys,
Where page space and time permits, please post content rather than a link to a document or page outside of the AjaxCNC Support Forum. Content is easier to follow, it's searchable and provides immediate assistance to the user. Most importantly, content won't break. Links outside of the AjaxCNC Support Forum -even AjaxCNC links- will break if the document is moved or renamed. Links (with a short explanation) to other posts within the AjaxCNC Support Forum are acceptable.

FWIW We will begin posting all documents in pdf and Open Office formats. Open Office is a free office suite with the capability of opening, editing and saving in Word, Excel, Publisher, PDF, Powerpoint etc... I'll be adding post with more complete information shortly but, in the meantime, check it out at http://www.openoffice.org. I highly recommend it.
Centroid_Tech
Posts: 286
Joined: Thu Mar 18, 2010 2:24 pm

What are the wire colors of the encoder pigtail?

Post by Centroid_Tech »

Question: Somehow the encoder pigtail was damaged. What are the wire colors of the encoder pigtail?

Answer:
Pin Signal Color
1 A Blue
2 A/ Blue/Black stripes
3 B Green
4 B/ Green/Black Stripes
5 Z Violet
6 Z/ Violet/Black Stripes
7 Vcc Red
8 GND Black
9 Shield Heavier Black wire
When requesting support, please ALWAYS post a current report. Find out how to take a report from your Acorn, CNC11 or CNC10 system here: https://www.youtube.com/watch?v=Ecvg0VJp1oQ.

If your question is PLC, Macro or program related, please also post a copy of the program or macro as well.

Without the above information we may not be able to help and/or reply until the required information is posted..
naxus
Posts: 1
Joined: Mon Aug 20, 2012 1:19 pm
Allin1DC CNC Controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC11: No
CPU10 or CPU7: No

Re: Encoder Basics

Post by naxus »

this card accept encoder HEIDENHAIN "ROD420" (TTL 1250 IMP.)???
Centroid_Liviu
Posts: 431
Joined: Mon Jul 18, 2011 9:57 am
Allin1DC CNC Controller: Yes
CNC Control System Serial Number: none
DC3IOB: Yes
CNC11: Yes
CPU10 or CPU7: Yes

Re: Encoder Basics

Post by Centroid_Liviu »

Encoders labeled "TTL type" (non differential) will not work with our control. We have 2000 line (8000ppr) encoders in 6 mm, 1/4?, 3/8?, and 1/2? hollow shaft sizes available if you need to swap yours out.
When requesting support READ THIS POST first. https://www.viewtopic.php?f=60&t=1043

Please ALWAYS post a FRESH report. To make a report: https://www.youtube.com/watch?v=Ecvg0VJp1oQ.

(We pride ourselves on providing timely solid technical support but, without good information we may not be able to help and/or reply until such information is posted.)
Mountainman
Posts: 3
Joined: Mon Aug 06, 2012 9:09 pm
Allin1DC CNC Controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC11: No
CPU10 or CPU7: No

Re: Encoder Basics

Post by Mountainman »

Anybody have clear written instructions on installing encoder to SEM servo motor. Any warning out there on what I should not do or be careful of ? I have a 1991 Bridgeport V2XT. I've seen the tutorial, but I am sure a pic means one thing to one person and something else to another.
Post Reply