Proper/acceptable contactor usage

Post by kb58 »

I'm building a CNC router and will use a contactor and power switches to control the 240V spindle power. 120V will be tapped off that to run the Acorn, C86, and servos.

I read that some here have wired the Estop switch into the contactor so that it removes power from the spindle and servos. I can see why (like what if a servo or spindle is on fire...). My question: might an acceptable middle ground be to wire the EStop in series with the VFD Stop Input, and count on the C86 board to shut down the servos if a fault is detected? I realize we're free to design and build our machines any way we want, but I want to pass this proposal by you guys in case I'm overlooking something important.
Previous hobby, building hard core sports cars. See http://midlana.com/ and http://kimini.com/
ShawnM
Posts: 2234
Joined: Fri May 24, 2019 8:34 am
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 7804734C6498-0401191832
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Clearwater, FL

Re: Proper/acceptable contactor usage

Post by ShawnM »

Just as you mentioned, you are free to wire the system anyway you like and are comfortable with. Use the contactor to break the COM wire on the spindle to stop it from spinning or interrupt the SPINFWD wire from the Acorn. Even without a contactor, when you hit the estop the acorn stops sending data anyway. Your spindle will stop and the drives stop, what else do you want to stop? I dont see the need to kill power to any of those devices. I have never wired a contactor to kill power to anything on a CNC machine. Oh, except when I power it down. :D

Just my 2¢

PS- if the machine is on fire I have other issues to worry about. :o
kb58
Posts: 180
Joined: Tue Jul 11, 2023 12:25 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: San Diego CA

Re: Proper/acceptable contactor usage

Post by kb58 »

I'm finding more information on this topic buried within other threads, so I'm not sure how helpful having another one here is.
Previous hobby, building hard core sports cars. See http://midlana.com/ and http://kimini.com/
cnckeith
Posts: 7334
Joined: Wed Mar 03, 2010 4:23 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: Yes
CNC Control System Serial Number: none
DC3IOB: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Contact:

Re: Proper/acceptable contactor usage

Post by cnckeith »

i would use the clearpath power hub and use estop to kill the power to servo drive and the vfd and any other powerful motor.
when i hit estop (not reset) i want everything except for the logic power (low voltage) to devices to be OFF immediately. that is definition of an emergency stop.
Need support? READ THIS POST first. http://centroidcncforum.com/viewtopic.php?f=60&t=1043
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
Gary Campbell
Posts: 2190
Joined: Sat Nov 18, 2017 2:32 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: Yes
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: Acorn 238
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Bergland, MI, USA
Contact:

Re: Proper/acceptable contactor usage

Post by Gary Campbell »

Why breakout 120vac when all of the devices you mentioned will run more efficiently on 240vac?
GCnC Control
CNC Control & Retrofits
https://www.youtube.com/user/Islaww1/videos
ShawnM
Posts: 2234
Joined: Fri May 24, 2019 8:34 am
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 7804734C6498-0401191832
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Clearwater, FL

Re: Proper/acceptable contactor usage

Post by ShawnM »

I run everything 220v also. I only break out 110 so I can mount a 4 gang outlet box on the machine for plugging other tools in and work off the table. Even your PC and monitor will run on 220.
kb58
Posts: 180
Joined: Tue Jul 11, 2023 12:25 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: San Diego CA

Re: Proper/acceptable contactor usage

Post by kb58 »

Gary Campbell wrote: Tue Sep 26, 2023 6:13 pm Why breakout 120vac when all of the devices you mentioned will run more efficiently on 240vac?
I may in fact do so. It's not like there's much power being consumed within the control box, but duly noted. I do have several 115V outlets on the box already for various items, some of which do require 115V only.
Previous hobby, building hard core sports cars. See http://midlana.com/ and http://kimini.com/
kb58
Posts: 180
Joined: Tue Jul 11, 2023 12:25 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: San Diego CA

Re: Proper/acceptable contactor usage

Post by kb58 »

cnckeith wrote: Tue Sep 26, 2023 4:56 pm i would use the clearpath power hub and use estop to kill the power to servo drive and the vfd and any other powerful motor.
when i hit estop (not reset) i want everything except for the logic power (low voltage) to devices to be OFF immediately. that is definition of an emergency stop.
The control box contains two IPC-5 power supplies, and while I do have a power hub, I figured that it can't work with two supplies, but maybe I'm wrong. Can just the one hub achieve the above, or will it require two hubs?
Previous hobby, building hard core sports cars. See http://midlana.com/ and http://kimini.com/
Gary Campbell
Posts: 2190
Joined: Sat Nov 18, 2017 2:32 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: Yes
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: Acorn 238
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Bergland, MI, USA
Contact:

Re: Proper/acceptable contactor usage

Post by Gary Campbell »

kb58 wrote: Tue Sep 26, 2023 8:34 pm
Gary Campbell wrote: Tue Sep 26, 2023 6:13 pm Why breakout 120vac when all of the devices you mentioned will run more efficiently on 240vac?
I may in fact do so. It's not like there's much power being consumed within the control box, but duly noted. I do have several 115V outlets on the box already for various items, some of which do require 115V only.
Make sure that you run all 4 wires to the controller (2 hots, neutral and ground) to the controller and load balance the 2 hot legs